Instrument Cable Gland Selector Calculator Guide

AutomationForum – Cable Gland Selector V2

Instrument Cable Gland Selector Calculator

Powered by AutomationForum.co | IEC 62444 | BS 6121 | IEC 60079
Professional cable gland selection for EPC and instrumentation work
Best Match
IP Rating
Thread
Compliance
IEC 62444

Engineering Inputs

Engineering Recommendations

Select cable details and click Calculate to receive a gland recommendation and engineering summary.

Recommendations

Best match is based on construction, environment, and cable OD.
Tip: Verify cable diameter against the manufacturer clamping range before final selection.

Engineering Report


How to Select the Right Cable Gland for Industrial Instrumentation and Electrical Installations 

In industrial instrumentation and electrical installations, a cable gland is far more than a simple cable entry accessory. It is the final mechanical, environmental, and often safety-critical interface between a cable and an enclosure. A wrong gland choice can lead to water ingress, poor strain relief, corrosion, electromagnetic interference problems, sealing failure, and in hazardous locations, serious non-compliance risks. That is why engineers need a structured and reliable way to select the right gland every time.

The Instrument Cable Gland Selector Calculator helps simplify this process by matching the gland recommendation to cable construction, environmental conditions, hazardous area zone, cable outside diameter, and material requirement. The calculator is designed for real engineering use, not just theory, and it gives a best-match recommendation, a thread size suggestion, and an IP-oriented selection summary. The uploaded calculator currently works from cable construction, environment, zone, cable OD, and material, and it generates a recommendation such as CW double compression, EMC, E2W ATEX, MICC pot seal, or hygienic stainless steel based on those conditions.

For EPC, commissioning, maintenance, and project engineers, that kind of structured selection can save time, reduce mistakes, and improve long-term reliability.

Lock down gland termination quality with this checklist: Checklist for Cable Glanding & Termination 

The Instrument Cable Gland Selector Calculator is a practical engineering aid that helps users choose a suitable gland based on the conditions of the installation. It is especially useful where the wrong gland can compromise sealing, retention, or compliance.

The calculator in the uploaded file is built around five main engineering inputs:

  • cable construction
  • environment
  • hazardous zone
  • cable outside diameter
  • gland material

It returns three key outputs:

  • Best Match
  • IP Rating
  • Thread Size

The current logic also creates a short engineering report for documentation and checking. The file shows that the calculator is intended for “professional cable gland selection for EPC and instrumentation work,” and it displays compliance with IEC 62444, BS 6121, and IEC 60079.

Choose tray sizes that pass IEC and NEC tests: Cable Tray Sizing Calculator: Complete Engineering Guide for IEC 61537 and NEC 392 Compliance

In the field, cable glands are often selected too quickly, copied from previous jobs, or chosen only by thread size. That leads to mistakes. A good selection tool forces the engineer to think about the real service conditions, not just the enclosure hole size.

How the Instrument Cable Gland Selector Calculator Works

The calculator logic is deliberately simple, which is a strength. It does not try to replace engineering judgment. Instead, it narrows the options based on the most important selection factors.

The tool accepts these cable types:

  • Unarmoured
  • SWA
  • STA
  • EMC Screened
  • MICC

Cable construction is the first decision because it determines whether the gland must grip armour, preserve screening continuity, or support mineral-insulated sealing.

The environment choices are:

  • General
  • Outdoor
  • Submersible
  • Corrosive
  • Hazardous
  • Hygienic

This drives the need for sealing, corrosion resistance, material choice, and hazardous-area compliance.

The calculator includes:

  • Safe Area
  • Zone 2
  • Zone 1
  • Zone 0
  • Zone 22
  • Zone 21

That is important because the gland must suit the enclosure location and protection concept.

Cable outside diameter is a core sizing parameter. A gland must seal the actual cable OD correctly; otherwise, the system may lose its ingress protection or retention performance.

The material setting influences corrosion resistance, chemical compatibility, mechanical strength, and hygiene suitability.

The calculator currently gives:

  • best match
  • IP rating
  • thread size
  • a short report

It uses a thread-size mapping of:

  • up to 7 mm → M12
  • up to 10 mm → M16
  • up to 13 mm → M20
  • up to 18 mm → M25
  • up to 25 mm → M32
  • up to 32 mm → M40
  • above that → M50+

It also defaults the displayed IP rating to IP68 and changes the recommendation based on cable construction and environment. For example, SWA or STA gives a CW double compression gland, hazardous environment gives E2W ATEX, EMC screened cable gives EMC-A, MICC gives MCI pot seal, and hygienic service gives SS316 Hygienic.

Stop using wrong cables in Ex zones today: What Cables to Use in Ex Zones: Complete Guide for Instrumentation & Control Engineers

Input Parameters Used by the Cable Gland Selector Calculator 
Input ParameterEngineering SignificanceIndustrial ApplicationImpact on Gland Selection
Cable constructionDetermines armour, screen, or special sealing needInstrument loops, power cables, analyzers, field devicesDecides whether single compression, double compression, EMC, or MICC gland is needed
EnvironmentDefines corrosion, moisture, washdown, or outdoor exposureOffshore, wastewater, process plants, food plantsDrives material and IP requirement
Hazardous zoneDetermines explosion protection needsZone 1, Zone 2, Zone 21, Zone 22 areasRequires certified hazardous-area gland
Cable ODEnsures proper clamping and sealingAll industrial cablesSets thread size and sealing range
MaterialControls corrosion resistance and hygiene suitabilityChemical, marine, pharmaceutical, outdoor serviceChooses brass, nickel-plated brass, SS316, aluminium, or nylon

Fix cable tray installation errors before they spread: Avoiding Mistakes in Instrumentation Cable Tray Installation: A Guide for EPC Projects

Unarmoured cables are common in control systems, light-duty instrumentation, and indoor installations. They are easier to terminate because there is no armour to bond or clamp. In many safe-area applications, a single compression gland is enough, provided the gland seals to the cable OD and the enclosure rating is suitable.

Typical uses include:

  • control panels
  • indoor junction boxes
  • PLC and DCS wiring
  • low-risk field instruments

The main concern is sealing and retention, not armour termination. For these cables, the gland must grip the outer sheath properly and maintain the required IP rating.

SWA cables are used where mechanical protection is needed. They are common in plant power distribution, outdoor routing, buried runs, and harsh industrial areas. SWA gland selection is different because the gland must do two jobs: seal the cable and terminate the armour correctly.

Typical uses include:

  • motor feeders
  • outdoor power circuits
  • pumps and skids
  • plant distribution wiring

For SWA, a CW double compression gland is often preferred because it supports armour retention and better sealing.

STA cables are less flexible than SWA and are often used where robust mechanical protection is needed in specific installations. The cable armour type influences the gland design and termination method. Incorrect gland selection can lead to poor retention or incomplete armour bonding.

Typical uses include:

STA often needs a gland type that can deal with the cable’s outer structure properly, especially where the armour layer must be securely terminated.

EMC screened cables are used in systems sensitive to electrical noise. These are extremely common in instrumentation loops, analyzers, VFD-adjacent circuits, communication lines, and precision measurement systems. The gland is important because the screen must be properly bonded to maintain electromagnetic shielding continuity.

Typical uses include:

  • analyzer houses
  • PLC and DCS signal wiring
  • speed control systems
  • instrument loops near power conductors

EMC glands are designed to preserve screen continuity and reduce interference.

MICC cables are used where fire resistance, very high temperature resistance, and long-term integrity are required. They need special sealing and termination methods because the cable construction is entirely different from polymer-insulated cables.

Typical uses include:

  • fire alarms
  • emergency systems
  • critical shutdown circuits
  • high-temperature areas

MICC glands are usually pot-seal or dedicated termination types because the cable needs a specialised sealing arrangement.

Follow this proven instrumentation cable termination method: Method Statement for Instrumentation Cable Termination

General indoor areas may not require the highest corrosion resistance, but they still need proper sealing and mechanical security. A well-sized brass or nickel-plated brass gland is often adequate.

Outdoor glands face UV, rain, dust, condensation, and temperature cycling. The gland must handle weather exposure and maintain the enclosure’s IP performance.

Submersible service is one of the most demanding conditions. The gland must be selected with careful attention to sealing, cable diameter accuracy, and immersion suitability.

Chemical plants, offshore platforms, wastewater plants, and coastal sites often need SS316 or similarly resistant materials. Corrosion resistance is not optional in these areas.

The gland must comply with the hazardous area protection concept. That means the right certification, right sealing method, and right installation practice.

In food, beverage, and pharmaceutical plants, the gland must be easy to clean, corrosion resistant, and suitable for washdown. Stainless steel is often preferred.

Build ATEX-safe cable choices with this checklist: Intrinsically Safe Cables for ATEX Zones – Complete Checklist for EPC Engineers

Hazardous Area Cable Gland Selection

Hazardous area selection is not just about the gland body. It is about the full system: zone classification, cable type, enclosure, installation method, and compliance with the area protection standard.

A safe area does not require explosive atmosphere certification, but quality sealing and retention are still important.

Zone 2 means an explosive atmosphere is not likely in normal operation and, if it occurs, it lasts only a short time. Cable glands must still be suitable for the equipment and enclosure.

Zone 1 is higher risk. Equipment and accessories must be selected with stricter control and proper certification.

Zone 0 is the highest gas-risk area, where explosive atmosphere is present continuously or for long periods. Selection and installation become highly restrictive.

Zone 22 is a dust hazardous area with lower frequency and duration of explosive dust atmosphere.

Zone 21 has a higher dust risk and requires stronger attention to sealing and certification.

The calculator’s hazardous-area selection of E2W ATEX reflects this kind of special requirement.

Eliminate cable management chaos with tray accessories: How to Fix Common Cable Management Issues using Cable Tray Accessories

Why Cable Outside Diameter Matters in Cable Gland Sizing

Cable outside diameter is one of the most important practical parameters in gland selection. If the gland is too large, the cable may not seal properly. If the gland is too small, installation may damage the sheath or prevent proper entry.

  • It determines whether the sealing insert can compress correctly.
  • It affects strain relief and cable retention.
  • It influences IP rating performance.
  • It decides the correct thread size.
  • water ingress
  • dust ingress
  • cable pullout risk
  • poor mechanical grip
  • loss of IP protection
  • accelerated seal wear
  • eventual failure during service

A good cable gland should match the OD range closely enough to seal and clamp effectively without damaging the cable.

Calculate cable tray fill fast and accurately: Cable Tray Fill Percentage Calculator

The calculator uses a practical OD-to-thread logic:

  • up to 7 mm → M12
  • up to 10 mm → M16
  • up to 13 mm → M20
  • up to 18 mm → M25
  • up to 25 mm → M32
  • up to 32 mm → M40
  • above that → M50+

Practical examples

A 6.5 mm instrument cable may suit M12.
A 9.5 mm control cable may suit M16.
A 14 mm SWA cable may move to M25 depending on gland family and clamping range.
A 22 mm industrial power cable may require M32 or M40 depending on the gland design.

The thread size should never be chosen only from the panel hole. It must align with cable OD, gland body, and enclosure entry requirement.

Catch wiring defects before startup with this procedure: Instrumentation Cable and Wiring Inspection Procedure: Essential  checklist for Project Engineers

Brass is economical, strong, and suitable for many general industrial applications. It is common where corrosion exposure is moderate.

Nickel plating enhances surface resistance and attractiveness, and provides superior resistance than plain brass in many conditions.

This is the best option for corrosive, offshore, maritime and hygienic applications. Corrosion resistance is strong and service life is lengthy.

It is light weight and can be beneficial in some industrial situations but not necessarily the best choice for highly corrosive or aggressive chemical environments.

Good for mild duty and non-metallic requirements. Often seen in general enclosures and cost-sensitive applications, but not suitable for every industrial duty.

MaterialCorrosion ResistanceMechanical StrengthCostTypical Application
BrassModerateGoodLowGeneral industrial, indoor service
Nickel Plated BrassBetter than brassGoodModerateOutdoor and mildly corrosive service
316 Stainless SteelExcellentVery goodHigherOffshore, chemical, hygienic, marine
AluminiumModerateGoodModerateLightweight industrial use
NylonGood in many non-aggressive areasLowerLowControl panels, light-duty wiring

Get a clean, complete instrument cable schedule template: Instrument Cable Schedule: Template, Example, Format and Complete Guide

Types of Cable Glands Recommended by the Calculator

A single compression gland seals the outer sheath and is commonly used for unarmoured cables in safe or general environments.

Advantages

  • simple installation
  • cost-effective
  • suitable for many standard cables

Limitations

  • not ideal for armoured terminations
  • not intended for every harsh service condition

A CW double compression gland is widely used for SWA or STA cables because it grips the armour and seals the outer sheath.

Advantages

  • excellent mechanical retention
  • strong armour termination
  • reliable for industrial power cables

Limitations

  • more installation steps
  • must be assembled correctly to achieve performance

EMC glands are used where screen continuity matters. They help maintain shielding and reduce interference.

Advantages

  • better EMC performance
  • suitable for signal integrity
  • preferred for analyzers and control systems

Limitations

  • screen termination must be done correctly
  • can be misinstalled if field practice is poor

This type is used when hazardous-area compliance matters. It is selected when the area classification and protection concept require a certified solution.

Advantages

  • supports hazardous-area compliance
  • suitable for stricter industrial duty

Limitations

  • requires careful certification checking
  • installation must follow the approved method

Used for mineral-insulated cables where termination and sealing are special.

Advantages

  • suitable for fire-rated and high-temperature service
  • specialized sealing capability

Limitations

  • not interchangeable with standard glands
  • requires special installation skill

Used where cleanability, corrosion resistance, and hygienic performance matter.

Advantages

  • excellent corrosion resistance
  • suitable for washdown and clean environments

Limitations

  • higher cost
  • may be unnecessary in simple indoor jobs

The calculator’s recommendation logic maps SWA/STA to CW double compression, hazardous service to E2W ATEX, EMC screened cable to EMC-A, MICC to MCI pot seal, and hygienic service to SS316 Hygienic.

Understand shielding mistakes that wreck signal performance: What is instrument cable shielding?

IP RatingProtection SummaryPractical Meaning in Industrial UseTypical Applications
IP54Limited dust ingress protection and protection against water splashesSuitable for basic indoor or light-duty installations where the environment is not harshIndoor panels, protected junction boxes, control rooms
IP65Dust tight and protected against low-pressure water jetsGood for outdoor and general industrial use where rain, dust, and washdown are possibleField enclosures, outdoor instruments, process skids
IP66Dust tight and protected against powerful water jetsBetter choice for more severe outdoor exposure and frequent washdown conditionsRefinery areas, wastewater plants, outdoor analyzer panels
IP67Dust tight and suitable for temporary immersionUsed where short-term water immersion may occurLow-level outdoor equipment, pit installations, occasional flooding exposure
IP68Dust tight and suitable for continuous immersion under specified conditionsHighest level among these options, but only valid under the stated manufacturer conditionsSubmersible devices, underground or immersed installations
Engineering NoteExplanation
Ingress protection importanceThe gland helps the enclosure resist dust and water entry, which protects the electrical or instrumentation system from premature failure
Selection approachIP rating should match the actual environment, not just be chosen as the highest available rating
Common use casesInstrument panels, field junction boxes, analyzers, and outdoor devices all need the IP rating to suit the cabinet design and site conditions

Find the real causes behind most industry failures: What Causes 80% of Instrument Failures in Industry? Top 10 Causes and Prevention Methods

StandardWhat It CoversWhy It Matters for Cable Gland SelectionPractical Impact
IEC 62444Requirements and test methods for cable glands, including classification, sealing performance, cable retention, environmental resistance, and documentationIt is central to proper gland selection because it defines how glands should perform and be verifiedInfluences product qualification, engineering specification, procurement, and commissioning checks
BS 6121Longstanding reference for cable gland practice and performance expectations in industrial applicationsHelps guide traditional industrial gland selection and installation practiceUseful for standardization and historical engineering reference
IEC 60079Hazardous area electrical equipment and installation practicesEssential for glands used in Zone 0, Zone 1, Zone 2, Zone 21, and Zone 22 areasDrives certification, installation method, and compliance for explosive atmospheres
IEC 60529Ingress protection coding such as IP65, IP66, IP67, and IP68Defines the protection level against dust and water entryUsed to specify the correct sealing performance for the environment
Compliance NoteExplanation
Design influenceThese standards affect gland design, sealing, retention, corrosion resistance, and hazardous-area suitability
Procurement influenceThey help define what must be purchased and what certificates or test data may be required
Installation influenceThey affect how the gland is installed, tightened, sealed, and inspected in the field
Commissioning influenceThey support final verification that the installed gland meets the intended application requirements

Use this SIS checklist to avoid compliance gaps: Advanced Safety Instrumented System (SIS) Inspection Checklist for IEC 61511 Compliance

Practical Cable Gland Selection Examples

For an outdoor pressure or temperature transmitter, choose a gland that matches the cable OD, resists UV and moisture, and maintains the required IP rating. If the location is corrosive, move to nickel-plated brass or SS316.

In Zone 1 or Zone 2 service, the gland must be certified for the application and installed exactly as required by the area protection standard. Correct certification is as important as the thread size.

Use EMC glands for screened cables to preserve shielding and reduce noise. This is crucial for analytical precision and consistent communication.

A sanitary gland made from 316 stainless steel is frequently the preferred option due of its cleanability and corrosion resistance.

Offshore locations usually justify SS316, robust sealing, and careful attention to cable clamping and corrosion resistance.

Ace EPC instrumentation interviews with sharper answers: Instrumentation Designer Interview Questions and Answers for EPC Projects

  1. Cable OD testing before thread size selection
  2. General-purpose gland in a hazardous environment
  3. Ignoring kind of cable armour
  4. Selecting the wrong material for corrosion service
  5. Omission of EMC screening requirements
  6. Size of gland mixed with size of enclosure entry
  7. Installation without confirming manufacturer clamping range
  8. Washdown or immersion exposure underestimated
  9. Reusing a damaged seal or insert.
  10. Not checking final torque and retention

Pick the right grounding method for stability: Single Point vs Multiple Point Grounding in Instrumentation Systems: Complete Guide for Engineers

  • Water Ingress Problems: Normally caused by incorrect OD choice, loose tightness, damaged seals or low IP rating.
  • Incorrect Cable Clamping:  Due to improper gland family, wrong insert size or bad installation procedure.
  • Corrosion Failures: Often due to poor choice of material, especially in offshore or chemical conditions.
  • Hazardous Area Non-Compliance: Typically caused by faulty certification, wrong gland type or insufficient installation documents.
  • Improper Armour Termination: Common with SWA or STA when the gland is not correctly designed or installed.
  • EMC Grounding Issues: Generally caused by bad screen bonding or inappropriate placement of EMC glands.
  • Seal Degradation: Can be accelerated by temperature, chemicals, UV exposure, or repeated rework.
  • Mechanical Loosening: Often results from vibration, thermal cycling, or under-tightening during installation.

Cut noise fast with a practical grounding calculator: Shield Grounding Noise Calculator for Instrumentation: A Practical Engineer Guide

  1. Verify cable OD from the actual cable datasheet.
  2. Match gland family to cable construction.
  3. Confirm hazardous-area certification before procurement.
  4. Select material based on the true environment.
  5. Do not assume a gland from a previous job is suitable.
  6. Check IP rating against the actual enclosure exposure.
  7. Use EMC glands for screened instrumentation where required.
  8. Confirm armour termination method for SWA and STA.
  9. Inspect each gland for seal damage before installation.
  10. Tighten to manufacturer guidance, not guesswork.
  11. Keep thread compatibility consistent with the panel.
  12. SS316 is used for corrosive or sanitary service.
  13. Do not mix dissimilar metals in a location where corrosion may occur.
  14. Have several extra seals and inserts for service.
  15. After a vibration-prone start-up, inspect the final installation.
  16. Document gland type, material and certification.
  17. Separate signal and power cable gland practices.
  18. Verify hazardous-area labels after installation.
  19. Train technicians on correct termination methods.
  20. Make gland selection part of the project QA checklist.

Spot signal drift early during live running checks: Noise and Signal Stability Observation for Running Inspection in Instrumentation and Control Systems

ItemVerificationStatus
Cable typeConfirm unarmoured, SWA, STA, EMC, or MICC
Cable ODMatch actual diameter range
EnvironmentGeneral, outdoor, corrosive, submersible, hygienic
Hazardous areaSafe, Zone 0, Zone 1, Zone 2, Zone 21, Zone 22
MaterialBrass, nickel plated brass, SS316, aluminium, nylon
Thread sizeM12 to M50+ as applicable
IP ratingConfirm enclosure and gland suitability
Armour terminationVerify if required
EMC continuityConfirm if screened cable needs it
CertificationCheck IEC 60079 / hazardous-area suitability
Installation torqueFollow manufacturer guidance
Seal conditionNo damage or deformation
DocumentationRecord gland type and serial data if needed

Verify 4 to 20 mA loops without doubt: Live Signal Verification 4 to 20 mA Loop Standard Operating Procedure (SOP)

A cable gland is used to securely terminate and seal a cable where it enters an electrical enclosure or equipment. It guards against dust, infiltration of water, mechanical stress and environmental damage yet preserving installation safety.

The size of the cable gland is based on the outside diameter of the cable and not just on the conductor size. Depending on the overall diameter and insulation thickness a 2.5 mm cable may require an M12, M16 or M20 gland.

There are several types of cable glands including single compression, double compression, EMC, hazardous area, and hygienic cable glands. The kind is correct depending on the cable construction, environment and application requirements.

Three cable glands are usually used: single compression, double compression and EMC cable glands. These varieties of glands fulfill most of the industrial cable termination requirements for instrumentation and electrical systems.

The selection of cable glands is important as the gland is the last protective barrier between the enclosure and the cable. It has a direct impact on sealing performance, mechanical retention, corrosion resistance and hazardous area compliance.

No various cable constructions require different gland designs to provide the required sealing and termination. Installation requirements for unarmoured, SWA, STA, EMC screened and MICC cables.

Cable OD is relevant as the gland seal is intended to squeeze around the outside diameter of the cable. Incorrect OD selection can lead to poor sealing, poor grip and loss of ingress protection.

Where additional mechanical retention and armour termination is required a double compression gland shall be employed. It is often used with SWA and STA cables in severe industrial applications.

An EMC gland gives electrical continuity between the cable screen and the cabinet. This is intended to minimize electromagnetic interference and enhance signal integrity in sensitive instrumentation systems.

The SS316 cable glands provide a strong resistance to corrosion, chemicals and harsh process conditions. They are often found in chemical plants, offshore applications and hygiene applications where durability is a must.

If the wrong size of thread is used, the result may be difficult or impossible assembly, poor sealing and diminished mechanical strength. It could also cause the gland to not sit properly in the enclosure entry.

Not necessarily. Because the best IP rating relies upon the real operation environment. IP68 is good for immersion protection, although IP65 may be enough for many industrial and outdoor applications.

No, hazardous area cable glands need to be matched to the certified zone classification, the type of cable and the equipment protection technique. Safety can be compromised and regulatory standards violated by using the improper gland.

One of the most typical mistakes is selecting a gland without considering the cable construction, outer diameter and environmental conditions. This commonly leads to seal failures and premature equipment difficulties.

Nylon cable glands are used in light-duty, non-corrosive and non-hazardous situations where metal glands are not needed. They are often utilized for indoor panels and general purpose enclosures.

Offshore environments are harsh on equipment due to salt spray, dampness and aggressive corrosion conditions. The corrosion resistance of SS316 cable glands provides long-term reliability for various applications.

No, a cable gland cannot make up for a wrong cable choice. The gland chosen must be appropriate to the kind and application of the cable to ensure correct performance and compliance.

Yes, you need cable glands that are easy to clean and are corrosion resistant for sanitary use. Hygienic stainless steel glands are utilized in pharmaceutical, food and beverage operations.

Yes, the selection of cable glands shall be incorporated in engineering specifications, procurement papers and quality assurance procedures. Making the right choice of glands makes a project more consistent, safer and easier to install.

Cable Glands may be modest in size but have a huge responsibility in industrial instrumentation & electrical systems. They protect enclosures from dust and moisture, hold cables securely, preserve EMC integrity, terminate armour where required, and support hazardous-area compliance. In many cases, the gland is the difference between a reliable field installation and a recurring maintenance problem.

The Instrument Cable Gland Selector Calculator is useful because it turns a complex selection problem into a practical engineering workflow. By checking cable construction, environment, zone, cable OD, and material, it helps engineers choose a gland that fits the real application instead of relying on assumptions. The current calculator structure reflects that approach by providing a best-match recommendation, an IP rating indication, a thread-size suggestion, and an engineering report for documentation.

For EPC teams, commissioning engineers, maintenance planners, and instrumentation professionals, that means better decisions, cleaner installations, stronger compliance, and more reliable systems over the life of the plant. Proper cable gland selection is not a minor detail. It is a core part of industrial reliability.


Read More