- Components of a 5-Way Valve Manifold
- Main Functions of a 5-Way Valve Manifold
- Step-by-Step Procedures for Bringing a DP Transmitter into Service with a 5-Way Valve Manifold
- How do I remove DPT from service?
- Step-by-Step Procedures for Removing a DP Transmitter from Service with a 5-Way Valve Manifold
- Safety Precautions for DP transmitter with 5-Way Valve Manifold
- FAQ on 5-Way Manifold Valve
- What is a 5-way manifold valve?
- What is the purpose of a manifold in a pressure transmitter?
- How does a 5-way manifold differ from a 3-way manifold?
- What is the difference between a valve and a manifold?
- What are the different types of manifold valves?
The 5-way valve manifold operates as a key element for Differential Pressure (DP) Transmitter systems. The device enables safe management of process pressure through controlled access during transmitter operation, calibration and maintenance. This guide covers the components, functions, and step-by-step procedures for bringing the transmitter into service and removing it safely.
Components of a 5-Way Valve Manifold
A 5-way valve manifold consists of five valves that allow pressure isolation, equalization, and venting:
HP Block Valve (High-Pressure Block Valve)
- Controls the process fluid entering the high-pressure (HP) side of the transmitter.
- Used to isolate the high-pressure line when needed.
LP Block Valve (Low-Pressure Block Valve)
- Controls the process fluid entering the low-pressure (LP) side of the transmitter.
- Used to isolate the low-pressure line when needed.
Equalizing Valves (Two Valves)
- Connect the HP and LP sides to equalize pressure before starting or stopping operations.
- This function safeguards the transmitter from internal damage caused by unexpected pressure changes.
Bleed Valve (One Valve)
- The manifold vents trapped pressure through this valve while releasing it into the atmospheric environment.
- Essential for safe maintenance or removal of the transmitter.
Main Functions of a 5-Way Valve Manifold
The 5-way valve manifold provides multiple essential roles for industrial processes including:
1. Isolating the DP Transmitter
- The process pressure can be isolated from the transmitter through HP and LP block valves for maintenance.
2. Equalizing Pressure
- The equalizing valves maintain equal pressure between the high pressure (HP) and low pressure (LP) sections to prepare the transmitter for operation or maintenance.
3. Venting or Bleeding Pressure
- A bleed valve provides a safe way to ventilate pressure that becomes trapped during transmitter maintenance to avoid hazardous situations.
4. Safe Calibration and Maintenance
- The manifold enables safe calibration operations without requiring a stoppage to the entire process by managing the pressure flow.
5. Preventing Damage to the Transmitter
- A sudden change in pressure can cause damage to DP transmitter components.The manifold prevents this by controlling how pressure is applied or removed.
Click here for Key Considerations for Pressure Transmitter Manifold Selection
Step-by-Step Procedures for Bringing a DP Transmitter into Service with a 5-Way Valve Manifold
The procedure prevents the transmitter from experiencing dangerous pressure spikes during its initial operation.
Step 1: Close All Valves

- Before starting the procedure check that every valve (HP block, LP block, equalizing, and bleed valves) are in the fully closed position.
Step 2: Open the Equalizing Valves

- Open both equalizing valves carefully until pressure levels become equal across the high-pressure and low-pressure areas.
- Opening the equalizing valves allows the transmitter to prevent sudden pressure increases.
Step 3: Slowly Open the HP Block Valve

- Gradually open the HP block valve to allow process pressure into the high-pressure side.
- Check for leaks in the connections and fix them before proceeding.
Step 4: Close the Equalizing Valves

- Once the HP side is stabilized, close the equalizing valves to lock the pressure difference.
Step 5: Open the LP Block Valve

- Slowly open the LP block valve to establish the normal differential pressure across the transmitter.
Step 6: Open the Main Root Valves
- Slowly open both main root valves located at the HP and LP taps until process pressure reaches the transmitter sensors.
Step 7: Verify Readings and Check for Leaks
- Check that the transmitter shows correct pressure levels in readings.
- Check all relevant connections for potential leaks as well as unexpected pressure fluctuations.
The DP Transmitter successfully entered service while maintaining proper operational function.
How do I remove DPT from service?
Step-by-Step Procedures for Removing a DP Transmitter from Service with a 5-Way Valve Manifold
This isolation procedure ensures transmitter safety by depresurising the system before maintenance or replacement work.

Step 1: Close the Main Root Valves
- Close the main root valves at both the HP and LP tapping points to stop process fluid from reaching the transmitter.
Step 2: Close the HP and LP Block Valves

- Shut off the HP block valve and LP block valve to isolate the transmitter from the system.
Step 3: Open the Equalizing Valves

- Open all equalizing valves to equalize pressure between the high pressure side and low pressure side.
- This prevents sudden pressure release.
Step 4: Open the Bleed Valve
- The process of venting trapped manifold pressure to the atmosphere can be performed by opening the bleed valve gradually.
- Perform safe venting operations at a distance from operating personnel.
Step 5: Confirm the System Is Fully Depressurized
- Verify that your system is entirely free of remaining pressure before continuing the process.
Step 6: The Transmitter is now out of Service
- The transmitter becomes safe to remove after finished ventilating all pressure.
The DP Transmitter has successfully completed its out-of-service procedures.
Safety Precautions for DP transmitter with 5-Way Valve Manifold
- Always use safety goggles, gloves, and flame-resistant clothing to protect against high-pressure leaks and chemical exposure.
- Opening equalizing valves demands that both HP block valves and LP block valves remain closed because process fluid may bypass the transmitter therefore providing inaccurate measurements and damaging the equipment.
- Thorough examinations of valves and connections must take place before starting up equipment. A leak detection solution or pressure gauge should verify that there are no leaks.
- Follow manufacturers guidelines and perform personnel training and implement both lockout/tagout LOTO procedures for every maintenance task.
- The 5-way valve manifold serves as an essential safety mechanism that enables proper operation of DP transmitters. The device maintains operational safety and measurement accuracy by regulating all necessary functions through isolation and equalization and venting.
- The correct step sequence protects transmitter components along with ensuring complete worker safety.
Refer the below link for How to Safely Zero a DP Transmitter with 3-Way Valve and 5-Way Valve Manifolds ?
FAQ on 5-Way Manifold Valve
What is a 5-way manifold valve?
Using a 5-way manifold valve technicians conduct in-place transmitter calibration procedures. The valve structure includes two block valves together with two equalizing valves and one vent valve. Indian manufacturers strongly prefer the use of 5-way manifolds instead of 3-way manifolds due to their additional functional capabilities.
What is the purpose of a manifold in a pressure transmitter?
A pressure transmitter manifold provides protection to the sensor through process separation while also enabling both calibrations and gas or liquid purging. Manifolds serve two functions as stand-alone accessories or direct placements on transmitter bodies.
How does a 5-way manifold differ from a 3-way manifold?
A 5-way manifold offers greater flexibility and control compared to a 3-way manifold, making it the preferred choice for differential pressure transmitter systems that require frequent calibration and maintenance.
Feature | 3-Way Manifold Valve | 5-Way Manifold Valve |
Number of Block Valves | 2 | 2 |
Number of Equalizing Valves | 1 | 2 |
Vent plug | Not included/ some valve included | Included |
Test plug | Not included | Included |
Primary Function | Isolates and equalizes pressure for differential pressure transmitters | Provides additional functions for venting, testing, and calibration |
Usage | Used for basic pressure equalization and isolation | Used for advanced calibration, venting, and testing |
What is the difference between a valve and a manifold?
A valve operates as a singular component which controls flow by performing opening and closing movements as well as throttling across one device. A manifold operates as a flow collection system that unites multiple paths to form a single header while using a header to divide a single flow through various branches.
What are the different types of manifold valves?
There are three basic categories of manifold valves.
- 2-Way Manifold Valves – Used in simple pressure gauge and isolation applications.
- The 3-Way Manifold Valve supports differential pressure measurement through its ability to balance pressure levels while also isolating systems.
- 5-Way Manifold Valves serve as elevated vent and testing features for performing specialized maintenance procedures and calibration tasks in differential pressure transmitters.
- A large variety of these manifold valves finds application in pressure gauge systems and impulse lines and flow recorders and switches.