Common Reasons for RTD Failures and How to Prevent Them

Table of Contents

Resistance Temperature Detectors (RTDs) are widely used in process sector due to their superior accuracy, repeatability and long term stability. RTDs find use in many applications such as refinery heaters, pharmaceutical reactors, power plant boilers, food processing lines, and water treatment facilities. Whatever the application, the RTD is a vital part in ensuring safe and efficient process temperatures.

RTDs are built for harsh industrial conditions, yet they can, and do, fail. Plant engineers often meet unexpected temperature variations, sporadic readings or full sensor failures that result in wasteful shutdowns, product quality difficulties and maintenance expenditures. The sensor itself is often not the real problem. This is usually caused by incorrect installation, broken wiring, entry of moisture, vibration or inadequate maintenance methods.

A good understanding of common RTD failure causes can assist maintenance personal detect problems immediately, increase measurement reliability, save down time and extend the life of the sensor. In this post we will present the most frequent reasons of failure, realistic troubleshooting procedures and proven preventive strategies from real industry experience.

Think You Master Sensor Selection? Prove Your Engineering Skills: Quiz on RTD and Thermocouple Selection for Instrumentation Design Engineers

What Is an RTD and How Does It Work?

A Resistance Temperature Detector (RTD) is a temperature sensor based on the change of electrical resistance of a metallic sensing element. 

Platinum is the preferred material because its resistance changes in a highly predictable manner over a wide temperature range.

The most widely used industrial sensor is the PT100, which has a resistance of 100 ohms at zero degrees Celsius. PT1000 sensors are also common where higher signal sensitivity is required.

Industrial RTDs are generally available in three wiring configurations.

The simplest arrangement where lead wire resistance directly affects measurement accuracy. It is normally used only for short cable runs.

Never Misconfigure Temperature Transmitters During Critical Plant Commissioning: How to Calibrate RTD transmitter?

The most common industrial configuration. It compensates for lead resistance and provides accurate measurements for PLC, DCS, and temperature transmitters.

Used for laboratory measurements and critical industrial applications requiring the highest possible accuracy by eliminating lead wire resistance errors.

RTDs are widely installed in reactors, heat exchangers, steam systems, storage tanks, boilers, furnaces, pipelines, compressors, and HVAC systems because of their excellent accuracy and long operating life.

The Hidden Installation Rule Every Process Engineer Should Understand: Why RTD Temperature Sensors are Installed Downstream of Orifice Plates?

Despite their reputation for reliability, RTDs operate in some of the harshest industrial environments. Extreme temperatures, vibration, chemicals, moisture, pressure, and mechanical handling gradually affect sensor performance.

From field experience, manufacturing defects account for only a small percentage of failures. Most problems develop after installation because of poor cable practices, damaged thermowells, incorrect sensor selection, improper maintenance, or harsh process conditions. Understanding these failure processes might help engineers avoid sudden shutdown and increase the dependability of the measurement in the long term.

Only Experienced Engineers Can Score High on This Challenge: RTD (Resistance Temperature Detector) Advanced Quiz

Common RTD FailureLikely CauseImpactRecommended Solution
Open circuitBroken sensing element or cableNo temperature readingReplace sensor and inspect wiring
Short circuitMoisture or damaged insulationIncorrect low temperature readingRepair wiring and eliminate moisture
Calibration driftAging or overheatingReduced measurement accuracyRecalibrate or replace RTD
Moisture ingressFailed cable gland or junction box sealUnstable readingsImprove sealing and replace damaged components
Mechanical damageMishandling or excessive forceSensor failureInstall carefully and protect during maintenance
Cable damageAbrasion or crushingIntermittent signalReplace damaged cable and improve routing
Common Reasons for RTD Failures

One of the most frequent reasons for RTD failure is still mechanical damage. Sensors are routinely bent, dropped, struck with tools or shoved into thermowells during installation.

During plant outages, maintenance personnel often pull numerous temperature sensors for inspection. RTDs can be dropped on hard surfaces, walked on, or otherwise destroyed during transport in busy turnaround schedules.

Symptoms

  • Readings intermittently
  • Total sensor failure 
  • Alarms open circuit
  • Fluctuating resistance values

Diagnosis

Check the sensor sheath for dents, bends, cracks or impact marks. Compare the sensor’s resistance to conventional RTD values.

Prevention

RTDs should always be treated with care, stored with protective covers, and never forced into a thermowell that may have debris or corrosion.

Replace Failed Temperature Sensors Safely Without Costly Shutdown Mistakes: Faulty Thermocouple Replacement Procedure in Process Area: Complete Step-by-Step Field Guide for Instrumentation Engineers

Constant vibration from compressors, pumps, turbines, cooling fans, and large motors can slowly damage the sensing element or internal connections.

Long insertion lengths without proper mechanical support are particularly susceptible to vibration caused fatigue.

Refinery engineers might see temperature values that only change when a nearby compressor is running. Upon inspection, the RTD sheath may look intact with the interior sensing element having shattered from extended vibration.

Symptoms

  • (occasional) temperature changes
  • Different ways of reading
  • Alarms open circuit from time to time

Diagnosis

Compare sensor performance during equipment operation vs. shutdown. Examine the thermowell for wear due to vibration or for fatigue cracks.

Prevention

Select vibration resistant RTDs, use properly designed thermowells, and avoid unnecessarily long insertion lengths.

Stop Cable Selection Mistakes That Cause Unreliable Temperature Readings: Thermocouple Wire vs. Thermocouple Extension Wire: The Complete Guide for Instrumentation Engineers

Every RTD has a maximum operating temperature specified by the manufacturer. Continuous exposure beyond this limit gradually changes the characteristics of the platinum sensing element.

Overheated RTDs commonly develop calibration drift before complete failure occurs. Process temperature above the specified limits can cause damage to the sensor and often results in unnecessary transmitter replacement by maintenance personnel.

Symptoms

  • The temperature readings start to move slowly.
  • Calibration mistakes increase
  • The quality difficulties of product arise

Diagnosis

Compare calibration findings to prior maintenance records and review process temperature history.

Prevention

Always select an RTD with the correct temperature rating and with enough safety factor for the process.

The Critical Compensation Principle Every Instrument Engineer Must Understand: Why Thermocouple Reference Junction Compensation(CJC) is Essential for Accurate Temperature Measurement ?

The sensing element, mineral insulation and protective sheath, expand and contract with repeated heating and cooling.

During normal operation of power plants, batch reactors, sterilizers and food processing systems, RTDs are often subjected to rapid temperature changes.

Internal welds will eventually deteriorate with repeated temperature cycling, increasing the chance of open circuit failures.

Symptoms

  • Gradual calibration shift
  • Intermittent measurement errors
  • Reduced repeatability

Diagnosis

Check the operating history to see if the process is subject to frequent heating and cooling cycles.

Prevention

Select RTDs specifically developed for cyclic service and limit temperature shock during plant start-up.

One of the most neglected reasons for RTD failure in industrial operations is moisture ingress to junction boxes, cable glands or terminal heads.

Damaged cable glands allow water to enter the terminal compartments during the monsoon seasons or equipment washdowns. Moisture reduces insulation resistance, creates leakage currents, and leads to unstable measurements or total sensor failure.

Outdoor RTDs commonly fail in water treatment plants because cable entrances are not securely sealed after commissioning.

Symptoms

  • Variable temperature indicator
  • Sudden shifts in reading
  • Intermittent alarms of communication
  • Low insulating resistance.

Diagnosis

Examine junction boxes for dampness, corrosion, or the presence of water. Test for moisture contamination by doing insulation resistance testing.

Prevention

Use good quality cable glands and check seals regularly. Use weatherproof junction boxes and replace damaged gaskets before moisture can reach the sensing element.

Many Resistance Temperature Detector problems start at the terminal block and not in the sensor itself. Loose screws , corroded terminals , faulty three wire connections and inadequate crimping add resistance to the circuit and give unreliable temperature measurements .

Wiring errors are particularly prevalent during commissioning when several RTDs are terminated simultaneously in large marshalling panels.

Symptoms

  • temperature values are randomly varied
  • Measurement variations with movement of cable
  • Unexpected high resistance values

Diagnosis

Verify wiring against loop drawings, tighten all terminals and verify continuity from the RTD to the control system.

Prevention

Use proper ferrules, proper three wire connection method, correct torque terminals and examine connections after every preventive maintenance shutdown.

Find Hidden Temperature Sensor Faults Before They Stop Production: Check List: How to Troubleshoot a Thermocouple?

RTD extension cables are often run through cable trays that are exposed to heat, chemicals, vibration and mechanical stress. Over time the insulation may fracture, deteriorate or become crushed so that conductors short or open.

Symptoms

Variations in signal, intermittent readings or loss of signal.

Diagnosis

Check cable over entire length and test for continuity and insulation resistance.

Prevention

Use adequate industrial extension cables, shield them with conduit when required and minimize severe bends or crushing of the cable.

Usually a broken sensing element or a damaged lead wire causes an open circuit. If moisture or damaged insulation permits conductors to contact, a short-circuit can develop.

Symptoms

The transmitter will generally be driven to its maximum or fault value (open circuit). A short circuit usually means an abnormally low temperature.

Diagnosis

Measure the resistance of the RTD with a multimeter and compare to standard PT100 resistance values.

Prevention

Chemical fumes, corrosive liquids and aggressive cleaning agents can attack the sheath, terminal head and cable connections. Corrosion of the sensing element quickly reduces the reliability of the measurement.

Proper sheath material selection is essential in chemical plants and offshore installations.

Even platinum RTDs gradually change characteristics after years of continuous service. Long exposure to increased temperatures speeds up aging and induces measurement drift.

Routine calibration can detect drift before it affects product quality or process control.

Measurement inaccuracy arises from using standard copper wire instead of the proper RTD extension cable, particularly with long cable runs.

The conductor size and the wiring layout are matched to provide an accurate measurement of resistance across the loop.

Avoid Startup Failures With This Essential Field Verification Guide: RTD Commissioning Checklist

common Symptoms of a Failing RTD
Observed SymptomPossible Cause
No temperature readingOpen circuit or broken lead
Constant low readingShort circuit or moisture
Fluctuating indicationLoose connection, vibration, or cable damage
Slow responseIncorrect insertion depth or damaged thermowell
Reading differs from referenceCalibration drift or aging
Intermittent alarmsMoisture ingress or poor termination


Discover Proven Techniques That Reveal Hidden Sensor Problems Quickly: RTD Testing Methods

Step by Step RTD Troubleshooting Procedure

A systematic technique can pinpoint the real defect without unnecessarily changing good components..

  1. Check alarms and process history to see when the problem originated.
  2. Visually inspect the sensor, cable, junction box and thermowell.
  3. Look for loose terminals, corrosion, damaged cable glands and moisture
  4. Measure the RTD resistance using a calibrated multimeter and compare with conventional PT100 values.
  5. Check continuity of wiring from sensor to transmitter or control system.
  6. Test for insulation resistance if you suspect moisture contamination.
  7. Compare the RTD reading against a calibrated reference thermometer or dry block calibrator.
  8. Check thermowell for vibration damage, process deposits or corrosion.
  9. Only replace the sensor after wiring, transmitter and installation have been checked and found satisfactory.
  10. Document results to enable future maintenance and reliability improvement.

Prevent Costly Measurement Errors Before They Impact Plant Operations: RTD Tolerance Calculation 

Preventive maintenance remains the best approach to improving RTD reliability.

Preventive Maintenance ActivityRecommended FrequencyExpected Benefit
Visual inspectionMonthlyEarly fault detection
Cable and terminal inspectionEvery six monthsReliable electrical connections
Calibration verificationAnnually or as requiredMaintains measurement accuracy
Thermowell inspectionDuring shutdownPrevents vibration and corrosion failures
Moisture seal inspectionQuarterlyReduces water ingress
Documentation reviewAfter maintenanceImproves troubleshooting efficiency
Best Practices to Prevent RTD Failures


Additional recommendations include:

  • Select the proper RTD for process temperature/pressure.
  • Use correct rated thermowells.
  • Route cables away from power cables. 
  • Seal cable glands properly.
  • Sensors shall be protected during shutdown activities.
  • Store spare RTD’s in a clean, dry area.
  • Check three wire connections before activating the loop.
  • Maintain full records of calibration and maintenance.

Make the Right Temperature Sensor Choice Every Single Time: Choosing Between Thermocouples and RTDs: A Practical Guide for Temperature Sensing

Root Cause Analysis
A chemical processing plant experienced erratic reactor temperature readings which resulted in unneeded control valve activity. The temperature transmitter was first suspected, but was proven to be calibrated appropriately.

Further inspection revealed that water had entered the RTD terminal head after a heavy rainfall. Ingress of moisture had been caused by a broken cable gland, resulting in reduced insulation resistance and intermittent measurement inaccuracies.
Corrective Actions Taken
The maintenance team rebuilt the cable gland, fitted a new RTD, increased weather sealing and modified the inspection checklist. Immediately the temperature of the reactor normalized, no process disruptions were reproduced and further failures were avoided.

Avoid Calibration Mistakes That Can Damage Process Reliability: 8 Steps RTD Calibration Procedure

common reasons for RTD failures, troubleshooting methods, preventive maintenance tips

Common Reasons for RTD: What to Know Failures allow engineers to quickly troubleshoot temperature measurement problems and avoid costly production downtime. Defective sensors are not the cause of most sensor failures, which are usually due to poor installation, vibration, dampness, wiring difficulties, aging or incorrect usage.

Best practices including routine inspection, proper installation practices, periodic calibration and systematic RTD troubleshooting greatly improve measurement reliability and extend sensor life. A disciplined preventive maintenance program not only avoids unexpected breakdowns, but also provides accurate process control, higher product quality and safer plant operation.
The Smart Wiring Upgrade Every Maintenance Engineer Should Know: Converting 2-Wire and 3-Wire RTDs into 4-Wire RTDs

RTD failure is commonly caused by vibration, moisture ingress, cable damage, loose connections, excessive temperature, corrosion, and sensor aging. RTD reliability is compromised by improper installation and/or incorrect thermowell selection.

The three most common causes of sensor failure are mechanical damage, electrical connection problems, and environmental exposure such as moisture, heat, or corrosion. These kinds of problems might cause false readings or total sensor failure.

Visually inspect the RTD and wiring for any physical damage. Measure the sensor resistance and check the cable continuity. Compare the readings to a calibrated reference . Replace the RTD if out of specification .

Calculate Sensor Performance Like an Experienced Instrumentation Professional: RTD Temperature Coefficient Calculation

Thermocouples can fail owing to oxidation, corrosion, vibration, high temperature, thermal cycling, insulation breakdown, or mechanical damage. Also, the thermocouple junctions can age and become contaminated , which can lead to measurement errors .

The most common thermocouple failure is an open circuit resulting from a broken sensor junction or damaged lead wire. Generally, this is the result of long-term vibration, metal fatigue, or repeated thermal cycling.

Inspect the thermocouple for obvious damage, loose connections, or corrosion and then test for continuity and output voltage using a multimeter. Check the reading against a known temperature reference or calibrated device to verify its correctness.

Vibration, moisture ingress, cable damage, excessive temperature, aging, poor installation or loose electrical connections are the usual causes of RTD failure, not manufacturing defects.

Measure its resistance with a calibrated multimeter and check the value against the standard resistance table, for the specific RTD type, at the measured temperature.

Long-term exposure to high temperatures, repetitive thermal cycling and natural aging eventually modify the characteristics of the platinum element and the precision of measurements is thus decreased.

Yes.  Internal connections may fatigue or the sensing device can fracture from continuous vibration especially in the case of extended thermowells or unsupported sensors.

RTDs in industrial plants are usually calibrated once a year . Critical applications may require more frequent calibration depending on the operating conditions and quality requirements .

Yes.  Moisture in junction boxes, cable glands or terminal heads leads to a decrease in insulation resistance and usually results in unstable or incorrect temperature measurements.

A typical PT100 measures around 100 ohms at 0 degrees Celsius. As per the RTD standard, the resistance increases predictably with increasing temperature.

Signal transmission is interrupted by cable failure from damaged insulation or broken conductors, and sensor failure happens within the RTD sensing element and changes the resistance characteristics of the RTD.