Relay vs Contactor: Differences, Working Principle, Wiring Diagram, Applications and Selection Guide

A relay is an electrically operated switching device used to control electrical circuits through a separate control signal. In industrial automation, relays are commonly installed inside PLC panels, motor control panels and instrument control systems.

An electromagnetic relay consists of a coil, magnetic core, armature, spring and electrical contacts. When the coil receives its rated voltage, it generates a magnetic field that moves the armature and changes the contact positions.

Relays are particularly useful for PLC signal isolation, interlocking, alarm circuits and switching small electrical loads.

How Does an Electromagnetic Relay Work Step by Step?

The operation of an electromagnetic relay involves four basic steps.

  1. The control voltage is applied across coil terminals A1 and A2.
  2. The energized coil produces a magnetic field.
  3. The magnetic force attracts the armature.
  4. The normally open contact closes and the normally closed contact opens.

When the coil supply is removed, the spring returns the armature to its original position.

Stop Valve Failures From Disrupting Automatic Process Control: Step-by-Step Procedure to Troubleshooting Solenoid Valves in PLC Digital Output Loops

Electromagnetic relay: Uses a coil and mechanical contacts to switch electrical circuits.

Auxiliary relay: Provides additional contacts for control logic, alarms and electrical interlocking.

Interposing relay: Provides electrical isolation and interfaces between PLC outputs and external equipment.

Time delay relay: Changes contact status after a predefined time interval.

Solid state relay: Uses semiconductor components instead of mechanical contacts. It provides electronic switching without mechanical contact movement.

Master Contact Logic Before Writing Your Next Program: Understanding NO vs NC Contacts is key for Logic Writing in PLC Programming

An electrical contactor is an electromechanical switching device designed to control higher power electrical loads, particularly three phase motors, industrial heaters and other power equipment.

Unlike a conventional control relay, a contactor has a more robust contact arrangement and an arc management system suitable for its specified switching duty.

Contactors are widely used in pump starters, conveyor systems, compressors, cooling tower fans and industrial motor control panels.

When the contactor coil receives its rated control voltage, the magnetic field attracts the moving armature towards the fixed magnetic core.

This movement closes the main power contacts, allowing electrical power to flow towards the connected load.

When the coil is de energized, the return spring separates the contacts and interrupts the electrical supply. During switching, an electrical arc can develop between the contacts. The arc chamber helps extinguish this arc.

What Are the Main Parts of an Electrical Contactor?
  1. Coil: Produces the magnetic field required for operation.
  2. Magnetic core: Provides the magnetic path.
  3. Armature: Moves when the coil is energized.
  4. Main contacts: Carry the electrical load current.
  5. Arc chamber: Controls and extinguishes switching arcs.
  6. Auxiliary contacts: Support feedback, interlocking and control circuits.

Catch Panel Component Problems Before They Cause Downtime: Running Inspection Checklist of PLC Components in Control Panels

Relay vs Contactor: 13 Major Differences Every Electrical Engineer Should Know

Although both devices use electromagnetic operation in their electromechanical versions, their construction and intended applications are different.

ComparisonRelayContactor
Main purposeControl circuit switchingPower load switching
Current capacityGenerally lowerDesigned for higher load currents
Voltage ratingDepends on contact designDesigned for specified power circuits
Contact arrangementNO and NC contactsMain and auxiliary contacts
ConstructionCompactMore robust
Arc managementDepends on relay designDedicated arc management arrangement
Switching frequencyDepends on device ratingDesigned for specified switching duty
Coil voltageAC or DCAC or DC
Load applicationSignals and smaller loadsMotors and power equipment
MountingPCB or DIN railPanel or DIN rail, depending on model
ProtectionRequires suitable circuit protectionRequires separate coordinated protection
MaintenanceContact inspection where applicableContact and mechanical inspection
Installation spaceGenerally smallerGenerally larger
CostGenerally lowerGenerally higher

Actual current and voltage ratings depend on the manufacturer, device model, load type and switching category. A relay should not automatically be considered unsuitable for every power application, nor should a contactor be selected based on current rating alone.

The main wiring difference is that relays are commonly used in control circuits, whereas contactors provide switching in power circuits.

A1 and A2 are commonly identified as the coil terminals.

For a typical 24 V DC relay:

  1. Connect the positive control supply to A1 through the control output.
  2. Connect A2 to the DC negative terminal.
  3. Identify the required normally open or normally closed contact terminals.
  4. Connect the external control circuit through the selected contacts.

Always check the relay wiring diagram because contact numbering and coil arrangements can vary.

For DC coils, verify polarity when a suppression diode is fitted.

Build Safer Mixing Sequences Without Risky Control Gaps: Step-by-Step PLC Ladder Logic for Automatic Liquid Mixing Process with Interlocks

A standard three pole contactor has six main power terminals.

TerminalFunction
L1Incoming phase 1
L2Incoming phase 2
L3Incoming phase 3
T1Outgoing phase 1
T2Outgoing phase 2
T3Outgoing phase 3

The three phase supply connects to L1, L2 and L3. The outgoing connections from T1, T2 and T3 feed the motor circuit, normally through an appropriately selected overload protection arrangement.

Fix Hidden Interlock Problems Before They Stop Production: PLC Permissive Logic Troubleshooting Procedure for Instrumentation Engineers

Auxiliary contacts are important for industrial control and monitoring.

13 and 14: Commonly represent a normally open auxiliary contact.

21 and 22: Commonly represent a normally closed auxiliary contact.

What Is the Difference Between Relay Wiring and Contactor Wiring?

These contacts are used for PLC feedback, electrical interlocking and seal in circuits.

For example, a normally open auxiliary contact can provide feedback to a PLC digital input when the contactor operates. However, this confirms the auxiliary contact position and does not independently prove that the motor is rotating.

Restore Lost Rack Communication Before Production Gets Interrupted: PLC Troubleshooting Remote IO Rack Communication Failure Complete Troubleshooting Guide for Industrial Automation Engineers

How to Connect a Contactor to a PLC Digital Output Module

PLC systems commonly operate relays and contactors through digital output modules.

A PLC output energizes an interposing relay or contactor coil according to the control logic. The associated auxiliary contact can then provide status feedback to a PLC digital input.

Before connecting a coil directly to a PLC output, verify:

  1. Output voltage compatibility.
  2. Continuous output current rating.
  3. Coil inrush current.
  4. Inductive load switching capability.
  5. Output module sourcing or sinking arrangement.
  6. Required coil suppression.

A PLC relay output uses mechanical contacts and can switch compatible AC or DC loads within its specified ratings.

A PLC transistor output uses semiconductor switching and is generally intended for DC loads. It is commonly used for faster switching applications.

An interposing relay is useful when the PLC output cannot directly handle the contactor coil load or when additional electrical isolation is required.

Find Out Why Commands Never Reach Field Equipment: PLC Input ON but Output Not Energizing: Complete Troubleshooting Guide

Industrial applicationRecommended deviceEngineering purpose
PLC output isolationInterposing relayIsolates control interfaces
Solenoid valve controlRelay or direct PLC outputDepends on coil rating
Pump motor controlContactorSwitches motor power
Conveyor motor controlContactorControls motor starting
Compressor controlContactorSwitches motor supply
Cooling tower fanContactorControls fan motor
Industrial heaterContactorSwitches heating loads
Forward and reverse controlTwo contactorsProvides motor direction control
Panel interlockingAuxiliary relay or contactor contactsPrevents conflicting operations
Alarm annunciationRelayOperates external indication circuits

The final selection must consider the electrical characteristics of the load and the required switching frequency.

Prevent Dangerous Trips With Better Alarm Documentation Practices: PLC Alarm and Trip Documentation Procedure – EPC PLC Automation Engineer Guide

Selecting a switching device requires more than checking its current rating.

Consider the following engineering factors:

  1. Rated operating voltage and current.
  2. AC or DC load characteristics.
  3. Motor starting current.
  4. Coil voltage and power consumption.
  5. Switching frequency and electrical endurance.
  6. Ambient temperature and enclosure conditions.
  7. Short circuit protection and coordination.
  8. Required auxiliary contacts.
  9. PLC output compatibility.
  10. Manufacturer selection tables and datasheets.

IEC 60947 utilization categories help engineers select contactors according to the type of load and switching duty.

AC 1: Used for non inductive or slightly inductive AC loads, such as resistance heating.

AC 3: Used for squirrel cage motor starting and switching off motors during normal running.

AC 4: Used for demanding motor operations such as plugging, inching and frequent reversing.

A contactor suitable for an AC 1 resistive load may not be suitable for the same current in an AC 3 motor application.

Before selecting a contactor for an industrial motor, engineers need to determine the motor’s full load current. This helps identify a suitable contactor based on its rated operational current and applicable utilization category.

Consider a three phase induction motor with the following assumed specifications.

ParameterValue
Motor power5.5 kW
Supply voltage415 V
Power factor0.85
Motor efficiency90% or 0.90

Step 1: Apply the three phase motor current formula

Motor current is calculated using the following formula:

Motor Current (A) = Motor Power (W) / (1.732 × Supply Voltage × Power Factor × Efficiency)

Step 2: Substitute the given values

Convert the motor power from kilowatts to watts:

5.5 × 1000 = 5500 W

Now substitute the values into the formula:

Motor Current = 5500 / (1.732 × 415 × 0.85 × 0.90)

Step 3: Calculate the motor current

Motor Current = 5500 / 548.9

Motor Current = 10.02 A

Calculated motor current = 10.02 A

This means the estimated full load current of the motor is approximately 10.02 A under the assumed operating conditions.

Engineering consideration: Use this calculated value as an initial reference when selecting the contactor. The final selection must be based on the actual motor nameplate current, AC 3 utilization category, starting conditions and manufacturer’s contactor selection tables. A suitable overload relay and short circuit protective device must also be selected separately.

Avoid Costly Logic Errors With Smarter Data Handling: PLC Data Types Every Automation Engineer Must Know to Avoid Costly Programming Errors

PLC Output Current and Contactor Coil Power Calculation

When a PLC controls a contactor, engineers must verify whether the PLC output channel can safely operate the contactor coil. The coil current and power consumption are important selection parameters.

Consider a contactor with an assumed 24 V DC coil and an operating current of 150 mA.

ParameterValue
Contactor coil voltage24 V DC
Coil operating current150 mA
Current in amperes0.15 A

Step 1: Convert coil current into amperes

Coil current = 150 / 1000

Coil current = 0.15 A

Step 2: Apply the electrical power formula

The DC coil power consumption is calculated using:

Power (W) = Supply Voltage (V) × Coil Current (A)

Step 3: Substitute the given values

Power = 24 × 0.15

Step 4: Calculate the coil power

Power = 3.6 W

Calculated contactor coil power = 3.6 W

This means the contactor coil consumes approximately 3.6 W under the assumed operating conditions.

Engineering consideration: Before connecting the contactor coil directly to a PLC transistor output, verify the output module’s rated voltage, continuous current capacity, switching capability and inductive load compatibility. Also check the contactor manufacturer’s pickup current and holding current because the initial coil current may differ from its steady operating current.

If the PLC output cannot safely handle the coil load, use a suitable interposing relay or an external driver. Provide appropriate coil suppression to protect the PLC output from inductive switching transients. For DC coils fitted with suppression diodes, observe the specified polarity.

Discover Why Industrial Controls Depend On Stable Voltage: Why is 24 Volts Mostly used in Industrial PLC Systems?

ProblemPossible causeRecommended inspection
Relay not energizingMissing supply or damaged coilMeasure coil voltage and resistance
Contactor not picking upIncorrect coil voltageVerify A1 and A2 supply
Contactor chatteringVoltage fluctuation or mechanical problemCheck control supply and armature
Main contacts overheatingLoose terminals or excessive loadInspect connections and load current
Welded contactsExcessive switching dutyCheck load category and contact rating
PLC output failureCoil inrush or inductive voltage spikeCheck output rating and suppression
Incorrect coil operationWrong AC or DC coilVerify nameplate
Auxiliary feedback failureDamaged contact or wiringPerform continuity testing
Overload relay trippingMotor overload or incorrect settingCheck motor current and overload setting
Electrical noiseUnsuppressed inductive coilInstall suitable suppression

Troubleshooting should always begin with electrical isolation and verification of the actual circuit conditions.

Eliminate Wiring Losses Before They Trigger Unstable Signals: How to Calculate and Minimize Voltage Drop in PLC Wiring?

Before commissioning, verify the following:

  1. Confirm coil voltage against the control circuit drawing.
  2. Check terminal identification and wiring connections.
  3. Tighten terminals according to manufacturer specifications.
  4. Use suitable wire ferrules and cable identification.
  5. Separate power and control wiring appropriately.
  6. Install suitable coil suppression.
  7. Verify overload relay settings against motor nameplate requirements.
  8. Test electrical and mechanical interlocking.
  9. Verify PLC output operation and auxiliary feedback.
  10. Complete functional testing before handing over the equipment.

For maintenance or wiring changes, isolate the supply, apply the required lockout and tagout procedure, and verify absence of voltage using an appropriate tester.

Wire PLC Inputs Correctly And Avoid Costly Mistakes: Sinking and Sourcing: Which Connection is Best for Your PLC?

A relay is mainly used for control circuits, signal switching and smaller electrical loads, while a contactor is designed for switching higher power loads such as industrial motors. The correct choice depends on the load current, switching duty and manufacturer’s ratings.

Yes, a contactor can perform many switching functions handled by a relay, provided its coil and contact arrangements are suitable for the application. However, using a contactor for a small control signal may increase panel space and cost unnecessarily.

Recover Failed Measurement Channels Without Unnecessary Plant Disruption: Replacing a Faulty Analog Input Card in a PLC Rack in Continuous Process Industries: Step by Step Procedure

A contactor can be controlled by a PLC when its coil voltage and electrical requirements match the PLC output capabilities. For smaller control signals and isolation requirements, an interposing relay is often a more practical choice.

Common industrial relay types include electromagnetic relays, solid state relays, time delay relays and latching relays. Each type serves different switching and control requirements in industrial automation.

Prevent Unexpected Controller Downtime With Essential Battery Care: Step-by-Step PLC Battery Replacement and Maintenance Procedure

A contactor is an electrically operated switching device used to control power circuits, particularly motors, heaters and industrial equipment. Its robust contacts and arc management arrangement make it suitable for applications involving higher switching loads.

A1 and A2 are the coil terminals where the specified AC or DC control voltage is connected to operate the device. Always check the manufacturer’s wiring diagram, particularly when using DC coils with polarity sensitive suppression diodes.

Avoid Miswiring Problems That Can Damage Control Inputs: Understanding Wet Contacts in PLC Wiring

Contactors are available with both AC and DC coils, depending on the control supply requirements. Their main contacts can also be designed for AC or DC switching, but the applicable voltage and current ratings must always be verified.

L1, L2 and L3 are the incoming three phase power terminals, while T1, T2 and T3 provide the outgoing connections to the load. These terminals are commonly used in industrial motor control circuits.

Expand Control Coverage Without Complicating Your PLC Architecture: Understanding Remote I/O in PLC Control Systems

No, a contactor only switches the motor power supply and does not independently protect the motor against overload. A properly selected overload relay and short circuit protective device are required for motor protection.

AC 1 is intended mainly for resistive or slightly inductive loads, such as industrial heating elements. AC 3 is intended for squirrel cage motor starting and switching off motors during normal running conditions.

Control Motor Sequences Precisely With Smarter Timing Logic: Understanding ON Delay and OFF Delay Timers in PLC Programming

Relays and contactors perform important switching functions in industrial automation, but they are designed for different electrical applications.

Relays are suitable for control signals, PLC interfaces, alarms and interlocking circuits. Contactors are preferred for switching motors and other power loads where appropriate switching capacity and arc management are required.


Read More