Intrinsic Safety Barrier Selection Procedure for Instrumentation Engineers

Selecting the correct intrinsic safety barrier is an important part of hazardous area instrumentation design. A barrier is not selected simply because the signal is 4 to 20 mA or because the device carries an intrinsic safety approval.

The complete circuit must be evaluated, including the hazardous area classification, field instrument, barrier, cable, control system, grounding arrangement, entity parameters, voltage drop and applicable certification.

An intrinsic safety barrier limits the electrical energy available to a hazardous area circuit by controlling voltage, current and power under normal operation and specified fault conditions. Zener barriers and galvanic isolators are common approaches, but their installation and electrical characteristics are different.

An intrinsic safety barrier is an interface installed between equipment in a safe area and an intrinsically safe field circuit in a hazardous area.

Its purpose is to prevent sufficient electrical energy from reaching the hazardous area to cause ignition under the conditions covered by the applicable intrinsic safety assessment.

The barrier works together with the field instrument and connecting cable. Therefore, the barrier should never be evaluated as an isolated component.

Types of Intrinsic Safety Barriers

A zener barrier normally uses zener diodes, resistors and a fuse to limit voltage and current. Excess energy is diverted through the grounding arrangement.

Because the circuit contains resistance, a voltage drop must be considered during loop design. A zener barrier also requires the grounding arrangement specified by its certification and installation documentation.

Compare IS And Explosion Proof Protection Before Equipment Selection: Difference Between Intrinsically Safe and Explosion-Proof

A galvanic isolator provides electrical isolation between the safe side and hazardous side while also providing the required energy limitation.

Many galvanic isolators require an external power supply and can also provide signal conditioning. Their isolation can simplify grounding arrangements, but the specific product certification and installation requirements must still be checked.

Calculate Earth Fault Current Before Your IS Loop Fails: IS Barrier Earth Fault Current Calculator | Intrinsic Safety Loop Design Tool

Intrinsic Safety Barrier Selection Procedure
  • Start with the hazardous area classification and project requirements.
  • Check the applicable zone, gas or dust classification, gas group, temperature class, equipment protection requirements and required certification.
  • The field instrument and associated apparatus must have compatible certification for the intended installation. Never select a barrier only from a general zone description.

Check Every IS Installation Detail Before Energizing Instruments: Installation Checklist for Intrinsically Safe Instrument (Apparatus)

Determine exactly what signal the barrier must handle.

Typical applications include:

  1. 4 to 20 mA transmitter
  2. Two wire transmitter
  3. HART transmitter
  4. Discrete input
  5. Discrete output
  6. Solenoid valve
  7. RTD
  8. Thermocouple
  9. Pulse signal
  10. Frequency signal

A barrier designed for one signal function should not automatically be assumed suitable for another signal function.

Trace PLC Input Failures Before They Disrupt Plant Operations: Top Causes of PLC Input Signal Failure in Plants

Entity parameters are among the most important checks in IS barrier selection.

For the field instrument, verify:

  • Ui
  • Ii
  • Pi
  • Ci
  • Li

For the barrier, verify:

  • Uo
  • Io
  • Po
  • Co
  • Lo

The basic engineering comparison is:

  • Uo must be less than or equal to Ui
  • Io must be less than or equal to Ii
  • Po must be less than or equal to Pi
  • The available barrier capacitance must accommodate the instrument and cable capacitance.
  • Co must be greater than or equal to Ci plus cable capacitance
  • The available barrier inductance must accommodate the instrument and cable inductance.
  • Lo must be greater than or equal to Li plus cable inductance

These relationships are commonly used for entity concept verification, but the final acceptance must always follow the certified equipment documentation and applicable installation requirements.

Cable characteristics can affect the intrinsic safety assessment, particularly on long instrumentation runs.

For example, consider a 500 metre cable with:

  • Cable capacitance = 80 pF per metre
  • Cable inductance = 0.8 microhenry per metre

Cable capacitance is:

500 × 80 pF = 40 nF

Cable inductance is:

500 × 0.8 microhenry = 400 microhenry

If the transmitter has Ci of 5 nF and Li of 100 microhenry, the barrier must provide sufficient Co and Lo for the combined values.

Required capacitance:

5 nF + 40 nF = 45 nF

Required inductance:

100 microhenry + 400 microhenry = 500 microhenry

This demonstrates why cable data should be checked before final barrier selection.

Understand 2oo3 Voting Before Designing Critical Protection Logic: 2oo3 Voting Logic Explained: How it Works, Why it is Used 

Certification compatibility alone does not guarantee correct operation.

Check:

  1. Signal type
  2. Operating voltage
  3. Current range
  4. Barrier input and output characteristics
  5. Loop resistance
  6. Voltage drop
  7. Transmitter minimum operating voltage
  8. DCS or PLC input resistance
  9. HART communication requirements

A barrier can satisfy the intrinsic safety entity requirements and still cause an operational problem if its voltage drop is too high or its signal characteristics are unsuitable.

HART applications require particular attention to signal transmission through the selected barrier. The manufacturer documentation should confirm HART compatibility for the complete circuit.

Select Intrinsically Safe Cables Without Risking EPC Compliance: Intrinsically Safe Cables for ATEX Zones – Complete Checklist for EPC Engineers

Calculate Intrinsic Safety Loop Voltage

For a two wire transmitter, verify that sufficient voltage remains at the transmitter under maximum loop current.

Consider a simple illustrative circuit:

  • Power supply = 24 VDC
  • Barrier voltage drop = 2.5 V
  • Cable resistance = 200 ohms
  • DCS input resistance = 250 ohms
  • Maximum current = 20 mA

Cable voltage drop:

0.020 × 200 = 4 V

DCS input voltage drop:

0.020 × 250 = 5 V

Voltage remaining for the transmitter:

24 minus 2.5 minus 4 minus 5 = 12.5 V

The calculated 12.5 V gives a tiny operational margin for a transmitter that needs minimum 12 V at 20 mA.

The actual transmitter requirement must come from its manufacturer documentation. This calculation should be performed during engineering rather than discovered during commissioning.

Calculate PFDavg Correctly Before Confirming Your Required SIL: SIF PFDavg / SIL Verification – Complete Guide + Online Calculator (IEC 61508 / 61511)

  • Grounding is an important distinction between barrier architectures.
  • A zener barrier uses a grounding path as part of its energy limiting arrangement. The required grounding system must therefore meet the barrier certification and installation requirements.
  • A galvanic isolator uses electrical isolation between circuits and generally does not depend on a dedicated IS grounding path in the same way as a grounded zener barrier.
  • Instrument earth, IS earth and safety earth should not be treated as interchangeable terms. The project grounding philosophy and manufacturer installation instructions must be followed.

Identify Cable Differences Before Connecting Hazardous Area Instruments: Difference Between Intrinsically Safe (IS) and Non-IS Cables

Before approving the barrier, verify:

  1. ATEX certification where applicable
  2. IECEx certification where applicable
  3. Certificate number
  4. Protection concept
  5. Entity parameters
  6. Gas group
  7. Temperature class
  8. Installation requirements
  9. Manufacturer instructions
  10. Control drawing
  11. System certification
  12. Hazardous area documentation
  13. Project specifications

A barrier should never be selected only from its product name or signal description. The complete certified loop must be evaluated.

Master Ex Protection Levels Before Selecting Hazardous Area Equipment: Intrinsic Safety Protection Systems: Understanding Ex ia, Ex ib, and Ex ic

Intrinsic Safety Entity Parameters for Barrier Selection

Consider a two wire 4 to 20 mA pressure transmitter installed in a hazardous area and connected to a DCS in a safe area.

Illustrative transmitter parameters:

Ui = 30 V

Ii = 100 mA

Pi = 0.70 W

Ci = 5 nF

Li = 100 microhenry

Illustrative barrier parameters:

Uo = 28 V

Io = 93 mA

Po = 0.65 W

Co = 83 nF

Lo = 2 mH

Cable parameters:

Cable capacitance = 40 nF

Cable inductance = 400 microhenry

The entity checks are:

28 V is less than 30 V

93 mA is less than 100 mA

0.65 W is less than 0.70 W

Understand Explosion Proof Protection Before Choosing Hazardous Area Equipment: Exploring Explosion-Proof: Safety in Hazardous Environment

Intrinsic Safety Entity Parameter Calculation Example

Available capacitance after transmitter capacitance:

83 nF minus 5 nF = 78 nF

The cable requires 40 nF, so the capacitance requirement is satisfied in this illustrative example.

Available inductance after transmitter inductance:

2 mH minus 0.1 mH = 1.9 mH

The cable requires 0.4 mH, so the inductance requirement is also satisfied.

Zener Barrier and Galvanic Isolator Comparison
ParameterZener barrierGalvanic isolator
Basic arrangementPassive energy limiting circuitIsolated active interface
IsolationNo galvanic isolationProvides galvanic isolation
GroundingGrounding arrangement is essentialDedicated IS earth generally not required
PowerNormally passiveCommonly requires external power
Voltage dropMust be consideredDepends on the specific module
Signal handlingDepends on barrier designDepends on isolator design
MaintenanceFuse and grounding checks may applyPower and module health checks may apply
Selection focusEntity values and groundingEntity values, isolation and power

GlobalSpec identifies zener barriers as passive devices and galvanic isolators as isolated interfaces, with both available for intrinsic safety applications.

Test Your Intrinsic Safety Knowledge With Real Plant Scenarios: Advanced Quiz on Intrinsic Safety Instrumentation Circuits in Oil & Gas Process Industries

  • Selecting Only by 4 to 20 mA: A matching signal range does not prove intrinsic safety compatibility. Always verify entity parameters.
  • Ignoring Cable Capacitance: Long cables can consume a significant portion of the permitted capacitance.
  • Ignoring Cable Inductance: Cable inductance must be included when verifying the complete intrinsic safety circuit.
  • Ignoring Voltage Drop: A barrier can introduce sufficient voltage drop to prevent a two wire transmitter from operating correctly.
  • Incorrect Grounding: Wrong grounding can impact on the intended operation of a grounded barrier.
  • Ignoring HART Compatibility: Standard analog barriers may not have the signal characteristics required for reliable HART connection.
  • Ignoring Certification: Zone, gas group, temperature class and protection requirements must be verified against the actual certification.
  • Not Checking the Complete Loop: The transmitter, barrier, cable and DCS or PLC interface must be evaluated together.

Discover The Engineering Reasons Behind Intrinsic Safety Selection: Why Choose Intrinsic Safety (IS) for Hazardous Area Instrumentation?

  • Barrier selection should be coordinated with the complete instrumentation design.
  • Review the instrument index, I O list, instrument datasheet, hazardous area drawing, cable schedule, junction box design, marshalling arrangement and DCS or PLC I O requirements.
  • For SIS, ESD and fire and gas applications, additional project requirements may apply. The selected interface should therefore be consistent with the safety system design, approved architecture and applicable project documentation.
  • During commissioning, the same information becomes important for loop checking and troubleshooting. A barrier that was selected correctly on paper can still produce field problems if wiring, grounding, termination or configuration differs from the approved design.

Understand Intrinsic Safety Before Designing Hazardous Area Circuits: What is Intrinsic Safety? Definition, Working Principle, Standards and Applications

ProblemFirst checkEngineering verification
Low 4 to 20 mA signalMeasure loop voltageVerify barrier drop and loop resistance
Transmitter does not powerMeasure transmitter terminal voltageCompare with minimum operating voltage
Intermittent signalCheck terminals and groundingInspect cable integrity and barrier condition
HART communication failureCheck communicator connectionVerify barrier HART compatibility
Incorrect loop currentMeasure current at suitable pointsCheck loop resistance and barrier characteristics
Signal loss after installationCheck barrier wiringVerify terminal assignment and certification
Unexpected voltage dropMeasure each sectionCalculate complete loop voltage
Ground faultCheck grounding arrangementVerify project grounding philosophy
Barrier channel failureCheck channel statusFollow manufacturer diagnostic procedure

See Why Engineers Rely On Intrinsic Safety Protection: Why select Intrinsic safety?

Before approving an IS barrier selection, verify:

  1. Hazardous area classification
  2. Applicable certification
  3. Signal type
  4. Ui and Uo
  5. Ii and Io
  6. Pi and Po
  7. Ci and Co
  8. Li and Lo
  9. Cable capacitance
  10. Cable inductance
  11. Loop resistance
  12. Voltage drop
  13. Transmitter minimum voltage
  14. Grounding requirements
  15. Isolation requirements
  16. HART compatibility
  17. Gas group
  18. Temperature class
  19. Manufacturer instructions
  20. Complete loop verification

Build Stronger Process Safety Through A Clear Shutdown Philosophy: Shutdown Philosophy: Engineering Documentation for Process Safety and Emergency Shutdown Systems

An intrinsic safety barrier limits voltage, current, and electrical energy entering a hazardous area circuit.
It helps protect intrinsically safe instruments by keeping the available energy below ignition levels.

Select an IS Barrier by evaluating the hazardous area, kind of signal, certification, entity specifications and cable characteristics.

Also check voltage loss, grounding, HART compatibility and the whole instrument loop.

Verify SIL Performance Before Finalizing Safety Instrumented Functions: SIL Verification Report (Safety Integrity Level Verification Report)

Zener barriers use components like zener diodes to limit the amount of electrical energy and require the grounding configuration specified.

A galvanic isolator offers electrical isolation between the safe area circuits and the hazardous area circuits.

Ui, Ii, and Pi define the maximum voltage, current, and power accepted by the field instrument.
Uo, Io, and Po define the maximum voltage, current, and power supplied by the associated apparatus.

Yes, an intrinsic safety barrier can be used with a HART transmitter when the barrier supports HART communication.
The complete transmitter, barrier, cable, and control system loop must also meet the required compatibility checks.

Design Reliable FISCO Networks Without Missing Critical IS Requirements: Fieldbus Intrinsically Safe Concept (FISCO) Model for Foundation Fieldbus H1 and Profibus PA

Common types are zener barriers and galvanic isolators for certain intrinsically safe instrumentation applications.

Selection is based on the type of signal, isolation, grounding, parameters of the entity, certification and project requirements.

Intrinsic safety installations are commonly designed with reference to the IEC 60079 series and applicable ATEX or IECEx requirements.
The specific requirements will be determined by the equipment certification, hazardous area categorization and project specifications.

An intrinsically safe circuit shall limit electrical energy and satisfy applicable certification and entity parameter requirements.

Intrinsic safety devices are certified equipment designed to operate in hazardous areas while limiting available ignition energy.
Examples include intrinsically safe transmitters, switches, sensors, barriers, isolators, and associated apparatus.

An IS barrier is an intrinsic safety barrier installed between safe area equipment and an intrinsically safe hazardous area circuit.
It limits electrical energy while providing the required interface between field instrumentation and control systems.

A zener barrier used between a safe area DCS and a hazardous area 4 to 20 mA transmitter is a common example.
A galvanic isolator certified for intrinsic safety is another widely used barrier interface.

Intrinsic barriers are interfaces designed to restrict electrical energy in instrumentation circuits connected to hazardous areas.
They help maintain intrinsic safety by controlling voltage, current, and power under specified operating and fault conditions.

Understand SIS SIF And SIL Before Designing Safety Systems: What is SIS, SIF and SIL? An In-Depth Guide to Functional Safety

Intrinsic safety barrier selection is a complete engineering verification rather than a simple component selection exercise. The correct barrier must satisfy hazardous area requirements, certification, entity parameters, cable characteristics, voltage requirements, signal compatibility, grounding requirements and control system interfaces.

For instrumentation engineers, the most important practice is to verify the complete loop from the DCS or PLC through the barrier and cable to the hazardous area instrument. This approach reduces commissioning problems and provides a clear technical basis for hazardous area instrumentation design.