Critical Flaw in Rockwell ControlLogix CVE-2024-6242 – Trusted Slot Bypass Vulnerability

In July 2024, a serious security flaw was found in Rockwell Automation ControlLogix 1756 devices. These devices are used in many industries, including oil and gas, chemical processing, water treatment, power generation, and advanced manufacturing. This vulnerability, known as CVE-2024-6242, has a CVSS v3.1 score of 8.4, which means it is a serious problem.

The issue makes the Trusted Slot function, which is a key security element in Rockwell chassis environments, less effective. Attackers can transmit illegal commands to the CPU through a trusted module by taking advantage of a flaw in Common Industrial Protocol (CIP) routing. This allows them get around slot-level constraints.

Claroty’s Team82 found this vulnerability, and CISA later validated it. It has big effects on the cybersecurity of industrial control systems (ICS). The following article discusses the technical details, how the Rockwell ControlLogix CVE-2024-6242 vulnerability can be used, how to fix it, and what we learned from it.

The ControlLogix 1756 chassis is the main part of Rockwell’s modular PLC platform. The backplane connects all the modules in each chassis, which can be of different sorts.

These are the brains of the system; they run process control, structured text, and ladder logic commands. The automation system can’t do its main jobs without them.

These connect directly to sensors and actuators in the field. Digital and analog I/O cards deal with signals from real-world processes, which makes them very important for connecting the control system to plant equipment.

Some examples are 1756-EN2T, EN2TR, EN3TR, EN4TR, and EN2TP. These cards connect the chassis to Ethernet/IP networks, which lets you monitor, set up, and talk to SCADA or DCS systems from a distance.

Critical Flaw in Rockwell ControlLogix CVE-2024-6242 - Trusted Slot Bypass Vulnerability - What is the Trusted Slot Feature?

Rockwell included the Trusted Slot functionality to lower the risk of illegal communications inside the chassis. The reasoning is simple:

Administrators can mark certain chassis slots as “trusted.” These are usually the slots that carry network interface modules that engineers use to upload or download logic.

When targeting the CPU, every command that comes from an untrusted slot is turned down. This stops bad or rogue cards from giving sensitive commands like forcing I/O, uploading new logic, or overwriting projects.

Know why 24VDC powers industrial PLCs: Why is 24 Volts Mostly used in Industrial PLC Systems?

This technique, on the other hand, enforces a security boundary at the chassis level. This gives operators assurance that only verified modules can send high-privilege commands to the CPU.

This process should, in theory, create significant separation. But the Rockwell ControlLogix CVE-2024-6242 vulnerability shows a big hole in how this validation is done.

Understand hot standby PLC system benefits: Hot Standby in PLC Systems: Architecture, Working, and Benefits

The Vulnerability - CVE-2024-6242 Explained - Critical Flaw in Rockwell ControlLogix CVE-2024-6242 - Trusted Slot Bypass Vulnerability

Claroty’s Team82 found out that the Trusted Slot protection doesn’t adequately check the pathways of CIP (Common Industrial Protocol) messages.

  • CIP allows requests move between different modules and slots by using path-based communication.
  • When everything is working normally, an engineer’s workstation sends a packet to the CPU through a network card. The trail tells you what each “hop” across the chassis is.
  • But this flexibility also makes it possible to hide the real source of a request by routing it in a roundabout way.
CIP Routing Weakness in Rockwell PLCs = Critical Flaw in Rockwell ControlLogix CVE-2024-6242 - Trusted Slot Bypass Vulnerability
  • When the CPU processes a CIP packet, it merely checks the last hop in the chain.
  • The CPU thinks the request is safe if that last hop is in a trusted slot.
  • The CPU doesn’t check to see if the request came from an untrusted slot before going via the trusted one.

Explore PLC hardware modules, types, and functions: PLC Hardware: Modules,Types, Functions, and Applications

  • An attacker who connects through an untrusted module can make a malicious CIP request that goes through a trusted slot before it gets to the CPU.
  • The CPU accepts the request without question since it just checks the last trusted slot.
  • This means that even a module that isn’t trusted can get higher privileges by taking advantage of routing logic.

Practical Impact

  • Attackers can download logic, rewrite project files, modify configuration settings, and add bad ladder logic.
  • The PLC might stop, change, or harm industrial operations, which could cause downtime, safety issues, or lost productivity.

The Common Industrial Protocol (CIP) makes it possible to route Rockwell systems in great detail.

  • Each chassis slot has its own number that is different from all the others.
  • Forward Open Requests explain communication by showing how messages move across the network and chassis.
  • For example:
    • A legitimate path might be Engineering Workstation → EN2T (Trusted Slot) → CPU.
    • An exploit path could be Attacker → Untrusted Slot → EN2T (Trusted Slot) → CPU.

The CPU carries out the malicious request even though it came from an untrusted source since it only checks that the last step goes through the EN2T (trusted slot).

This design flaw makes the Trusted Slot functionality useless against smart attackers who know how CIP routing works.

Comprehensive guide to top PLC software: Top 22 PLC programming software available in market?

Claroty Team82 produced an intrusion detection signature to help defenders.

  • The Snort rule finds CIP Forward Open Requests that have more than one backplane hop.
  • In real operations, most traffic goes straight from a trusted card to the CPU without being redirected.
  • Multiple hops, especially requests that go from one module to another before reaching the CPU, are rare and hence suspicious.
  • When security personnel find it, they can look into it and stop the bad traffic before it causes damage.

This way of finding problems gives businesses a temporary shield until they can fix or replace devices that are at risk.

Explore the leading global DCS manufacturers: Top 10 DCS manufacturing companies

A real-world attack that takes use of the Rockwell ControlLogix CVE-2024-6242 vulnerability could go like this:

  • The attacker gets access via breaking into a remote engineering workstation or by using a poorly segmented OT/IT network.
  • Once they’re inside, they can use regular CIP discovery techniques to look for ControlLogix chassis modules.
  • The attacker makes a CIP packet that first goes via a trusted slot (like EN2T) before getting to the CPU. They do this by knowing how the slots are set up.
  • This makes the request look real.
  • The CPU checks and carries out the request because the last hop is from a trusted slot.
  • The system doesn’t know where the untrusted source came from.
  • The attacker can download any ladder logic they want to mess with process flows.
  • They might change configuration files to hide that they are there.
  • In the worst instances, they could stop all operations, which would make things less safe and less available.

This example shows how a mistake in a protocol might make a hardware-enforced security feature useless, which could put vital infrastructure at risk.

Master NO vs NC contact logic writing: Understanding NO vs NC Contacts is key for Logic Writing in PLC Programming

Rockwell has acknowledged that a number of product lines are compromised. Some of them need firmware updates, while others need to have their hardware completely replaced.

ProductFirst Affected FirmwareFixed FirmwareNotes
ControlLogix 5580 (1756-L8z)V28V32.016, V33.015, V34.014, V35.011+Update required
GuardLogix 5580 (1756-L8zS)V31V32.016, V33.015, V34.014, V35.011+Update required
1756-EN4TRV2V5.001+Update required
1756-EN2T (Series A/B/C)V5.007 / V5.027No fix – must upgrade to Series DHardware replacement
1756-EN2F (Series A/B)Same as aboveNo fix – upgrade to Series CHardware replacement
1756-EN2TR (Series A/B)Same as aboveNo fix – upgrade to Series CHardware replacement
1756-EN3TR (Series A)Same as aboveNo fix – upgrade to Series BHardware replacement
1756-EN2T (Series D)V10.006V12.001+Update required
1756-EN2F (Series C)V10.009V12.001+Update required
1756-EN2TR (Series C)V10.007V12.001+Update required
1756-EN3TR (Series B)V10.007V12.001+Update required
1756-EN2TP (Series A)V10.020V12.001+Update required

This table highlights a major challenge: Older hardware series (A/B) can’t be patched and have to be replaced, which costs a lot of money and time for operators.

Best free PLC programming tools revealed: Top 6 free PLC Programming software

CISA and Rockwell suggest a number of ways to protect enterprises who can’t quickly patch or replace their equipment:

  • When the CPU’s physical mode switch is set to RUN, it stops project downloads, which lowers the chance of malicious logic insertion.
  • This stops reprogramming, but it doesn’t stop all bad CIP commands, thus it should be used with other defenses.
  • It is very important to properly separate OT and IT networks.
  • Firewalls should only let CIP communications go through approved engineering workstations and management systems.
  • When accessing a system from the outside, you should use secure techniques like VPNs with multiple factors of authentication.
  • Claroty’s Snort rule and other tools let you see suspicious CIP routing attempts.
  • Organizations can add IDS alerts to a Security Information and Event Management (SIEM) platform to keep an eye on everything in one place.
  • You need to get new Series C or D hardware that supports patched firmware to replace the older Series A/B modules.
  • To prevent being exposed for a long time, businesses should consider this in their asset lifecycle planning.

Adopt Security Best Practices

  • Follow Rockwell’s System Security Design Guidelines, which stress least-privilege access, secure remote connections, and constant monitoring.
  • Check Rockwell advisories often and quickly install firmware upgrades as they come out.

The Rockwell CVE-2024-6242 problem teaches us a few essential things:

  • Hardware Trust Alone Is Not Enough: If the communication protocol doesn’t have strong validation, even chassis-level slot enforcement can be gotten around.
  • Collaboration between vendors and researchers is very important: The relationship between Claroty, Rockwell, and CISA made it possible to quickly release detection signatures, vendor alerts, and other information.
  • We need secure-by-design protocols: To eliminate path spoofing, future versions of CIP and other ICS protocols should include cryptographic source validation.
  • Defense-in-Depth is Not Up for Discussion: Operators must expect that any one control could fail. The only long-term solution is to use numerous detection and preventive methods.
  • It’s important to plan for the whole life cycle: Security should be a top priority in managing the lifecycle of assets, not something that comes up later when problems arise.

Reduce downtime with proactive PLC I/O care: Proactive Maintenance Strategies for PLC I/O Modules: Reduce Downtime & Improve Reliability

This vulnerability is extremely problematic in today’s operational contexts, when IT and OT networks are coming together more and more.

  • Remote Engineering Access: Cloud-based SCADA or vendor maintenance sessions make more entry points possible.
  • Integrators from Other Companies: Contractors often connect laptops or temporary modules, which makes it easy for an untrusted slot to be added without anybody knowing.
  • IoT and Edge Devices: Devices on the Internet of Things (IoT) and the Edge As plants start using IIoT sensors and edge gateways, more devices are on the same network as core PLCs. This makes it more likely that attackers will go sideways.

Step-by-step voltage drop calculation in PLC wiring: How to Calculate and Minimize Voltage Drop in PLC Wiring?

The Rockwell ControlLogix CVE-2024-6242 vulnerability shows that protocol design issues can make even trusted hardware-based defenses less effective. Attackers can use CIP routing to get beyond Trusted Slot enforcement and directly attack the CPU, putting important industrial systems at risk of sabotage, disruption, or manipulation.

To protect themselves from this, businesses must:

  • Fix or replace weak modules right away
  • Use IDS rules to find bad CIP traffic.
  • Limit access to important PLCs on the network
  • Use a defense-in-depth strategy that includes firmware updates, monitoring, and splitting up the architecture.

This story shows that industrial automation needs more than one layer of protection to stay safe. No one feature, not even a hardware-level protection like Trusted Slot, can guarantee safety. To keep modern industrial networks safe, you need to always be on the lookout, manage their lifecycles, and find threats before they happen.

Find out the top PLC brands worldwide: Top 15 PLC brands

CVE-2024-6242 is the main issue at the heart of the dispute. It is a serious weakness in Rockwell ControlLogix 1756 PLCs. Attackers can get around the Trusted Slot feature and send commands that aren’t allowed, which puts electricity, oil and gas, and manufacturing industries at danger.

Rockwell’s key customers are in the oil and gas, energy, water treatment, automotive, pharmaceuticals, and advanced manufacturing industries. A lot of Fortune 500 firms use its ControlLogix PLCs and FactoryTalk software.

It is a security setting at the chassis level that marks certain slots as trusted. Only modules that fit in these slots, which are usually network cards, can send critical orders to the CPU.

Learn scaling of analog values in automation: Scaling Analog Values in Industrial Automation (PLC)

Rockwell is mostly a product-based company that sells PLCs, drives, and automation software. It is a hybrid supplier because it also offers services including system integration, lifecycle support, and cybersecurity.

The problem is that the CPU only checks the last step in CIP routing. Attackers can get around constraints and get privileged access by sending requests through a trusted slot.

A problem like this is called a vulnerability. Attackers can take advantage of things like weak protocols, old firmware, or bad network segmentation.

The Trusted Slot feature is a Rockwell security feature that makes sure that only modules in approved slots can talk to the CPU at a high privilege level.