Calibration

How-to do Control Valve Calibration?

 

Required Material:

1) Data sheet
2) Hart Communicator

Step wise Procedure:

*Ask panel man to put the controller in manual mode for control loop
*Isolate the Control valve from the process.
WARNING – The Isolation of control valve from the process shall be done by field operator. Careful step shall be done to ensure no upset to the operation.
*Hook up HART Communicator and verify some parameters by refer to data sheet such as Tag Number, OP and etc.
*Select auto find stop (wait some minute)
*If full open is more than 100% select open adjustment and put new number as per calculation
*Make an auto calibration ( wait some minute)
*Verify the linearity by increasing and decreasing the travel (0%,25%,50%,75%,100%,75%,50%,25% and 0%of range)
*After completion of the job ask panel operator to put loops back in normal mode
*Fill the calibration form and file it for future reference.
Example calculation:
A: Max travel from stem   70mm
B: Scale plate   50mm
New open adjustment should be (50/70) X 100 = 71.48%

Related Articles

Leave a Reply

Back to top button

Adblock Detected

We Noticed You're Using an Ad Blocker Hi there! We understand that ads can be annoying, but they help support our website and allow us to continue providing you with high-quality content. Please consider whitelisting our site or disabling your ad blocker while you visit. Your support means a lot to us! Thank you for understanding!