- Why it’s important to measure the Boiler drum level precisely
- Types of Boiler Level Transmitters
- Example Setup – DP Type Level Measurement
- Differential Pressure Calculations
- Role of Steam Density (Ds) in Boiler Drum level Measurement
- Level Transmitter Calibration Range
- Why it is important to have accurate level transmitters
- Maintenance and Best Practices on Boiler Drum Level transmitters
- How does a drum level transmitter work?
- What is the DP transmitter of a boiler?
- What is the level control of the boiler drum?
- How to measure boiler water level?
- What is boiler drum pressure?
- Why 3 elements instead of 2 elements in boiler?
- What is the normal water level in a boiler?
Why it’s important to measure the Boiler drum level precisely
When using steam boiler systems, especially in high-pressure industrial settings, it’s not just important to know how much water is in the steam drum; it’s crucial.
If the water level is too low:
- Boiler tubes may get too hot because they are exposed to steam instead of being submerged in water.
- This can lead to dry-firing, which can cause the boiler tubes to distort, shatter, or collapse completely.
If the water level is too high:
- Wet steam can bring water drops into superheaters, turbines, or other industrial equipment.
- This lowers thermal efficiency and can wear down and erode equipment downstream.
So, it is important to keep an eye on the level all the time with trustworthy Level Transmitters (LTs). These transmitters send real-time data to a DCS (Distributed Control System) or PLC (Programmable Logic Controller) to keep the feedwater control and operation safe.
Master Drum Level Control Now: Boiler Drum level control
Types of Boiler Level Transmitters
There are three common types of level transmitters used in industrial boilers:
The Differential Pressure (DP) Level Transmitter is the main topic of this article. It is the most common method used in steam drum applications since it is simple, reliable, and easy to add to control systems.
Explore All Boiler Types Here: Types of boilers, Fire tube, water tube and combination
Example Setup – DP Type Level Measurement

Refer to the image above. It illustrates a classic DP transmitter configuration for boiler steam drum level measurement using a wet reference leg
System Parameters:
- Drum Height (H) = 2.0 meters
- Water Density (Dw) = 960 kg/m³
- Steam Density (Ds) = 5.0 kg/m³
- Reference Leg (Condensate) Density (D₀) = 995 kg/m³
Installation Configuration
- The bottom of the steam drum, where the water gathers, is where the High Pressure (HP) side of the transmitter connects to it.
- A vertical line filled with condensate (called the reference leg) connects the Low Pressure (LP) side to the top of the drum. This line drains into a condensate pot.
This setup ensures:
- HP side measures pressure based on the real water level in the drum.
- LP side perceives a steady hydrostatic pressure because of a column of condensate with a known density.
Click here for Closed tank level measurement – Wet Leg System – Transmitter installed in non-zero based remote mount application
Differential Pressure Calculations
Let’s find the differential pressure (ΔP) for two different water levels: 100% full and 20% full.
At 100% Water Level (H = 2.0 m):
- HP Side Pressure (P_HP)
PHP=H×Dw×g=2.0×960×9.81=18,835.2 Pa
- LP Side Pressure (P_LP)
PLP=H×D0×g=2.0×995×9.81=19,549.8 Pa
- Differential Pressure (ΔP)
ΔP=PHP−PLP=18,835.2−19,549.8=−714.6 Pa
At 20% Water Level (H = 0.4 m)
- HP Side Pressure (P_HP)
PHP=0.4×960×9.81=3,767.04 Pa
- LP Side Pressure (P_LP) remains the same:
PLP=19,549.8 Pa
- Differential Pressure (ΔP)
ΔP=3,767.04−19,549.8=−15,782.76 Pa
As the water level goes down, HP pressure goes down while LP pressure stays the same. This makes ΔP more negative.
Refer the below link for the DP calculator for Closed tank level measurement – Wet Leg system – Transmitter installed in zero based direct mount application
Role of Steam Density (Ds) in Boiler Drum level Measurement
Because of the wet reference leg, steam density doesn’t have much of an effect in this arrangement.
Why?
- Steam has a fairly low density (Ds = 5.0 kg/m³) compared to water, hence the steam column doesn’t put much pressure on the water.
- If you employed a dry reference leg (filled with steam) instead of a condensate-filled leg, any variations in the temperature or pressure of the steam would have a big effect on the LP side pressure, which would make the level measurements wrong.
- The wet leg stays stable because it uses condensate with a known density (995 kg/m³) to keep the pressure on the LP side steady.
This gets rid of mistakes that happen when the density of the steam changes.
Click here for Unloaded Steam Cost calculator
Level Transmitter Calibration Range
To connect the transmitter’s 4–20 mA signal to the real level range:
- Lower Range Value (LRV) = –15.78 kPa = 4 mA = 0% level
- Upper Range Value (URV) = –0.71 kPa = 20 mA = 100% level
This is a reverse-acting configuration:
- As the water level goes down, the HP pressure goes down, and the ΔP gets more negative. (As water level drops → HP pressure drops → ΔP becomes more negative)
- So, a lower level means a smaller differential pressure, and vice versa..
What’s a Deaerator? Find Out: Deaerator- What are deaerators?, working, construction.
Why it is important to have accurate level transmitters
Choosing and setting up level transmitters in steam drums correctly is important for:
- Safe Operation: Stops the boiler from tripping and the tube from overheating when the level is low.
- Efficient Steam Generation: Keeps the right amount of water in the system to get the best steam purity and heat transfer.
- Stable Feedwater Control: Lets you use DCS or PLC to control PID based on the water level in real time.
- Minimized Errors Due to Steam Fluctuations: Less Mistakes Because of variations in steam density, a wet leg cancels out changes in pressure.
Unlock Maximum Boiler Performance: How to increase Boiler efficiency?
Maintenance and Best Practices on Boiler Drum Level transmitters
- Check the condensate pot every now and again to make sure it isn’t too full or blocked.
- Check the transmitter zero during shutdowns when both sides are at the same pressure.
- To keep the temperature of the condensate stable, insulate the reference and impulse lines.
- For accurate measurement, always utilize density-corrected calibration.
How does a drum level transmitter work?
To find out how high the water is in a boiler drum, a drum level transmitter, which is usually a differential pressure transmitter, monitors the difference in hydrostatic pressure between two points on the drum.
- The bottom of the drum, where water collects, is connected to the High-Pressure (HP) side.
- The Low-Pressure (LP) side connects to the top of the drum through a reference leg that is full of condensate.
This setup makes use of the fact that water and steam have different densities. Because the boiler works under saturation conditions, the densities of both water and steam change with temperature and pressure. The transmitter turns the difference in pressure into an electrical signal that shows the level of water.
What is the DP transmitter of a boiler?
A Boiler Differential Pressure (DP) Transmitter is a specific instrument for measuring pressure in boiler systems.
- Detecting the pressure difference between the water leg (HP) and the reference leg (LP) to find the drum level.
- Flow rate through orifice plates in the steam or feedwater lines.
These transmitters are built to last and can handle the extreme pressures and temperatures seen in power plants and industrial steam systems, which can be hundreds of psi and above 300°C.
What is the level control of the boiler drum?
Drum Level Control is important for:
- Preventing dry-out: Stops boiler tubes from getting too hot and breaking.
- Avoiding carryover: stops water from getting into steam heads or turbines.
- Keeping things stable: makes sure that steam is always made.
Critical Interlocks You Must Know: Steam Turbine Interlocks and Associated Protection Systems
Common ways to control:
- Single-element control: Only uses the drum level as feedback. This works well when the load changes slowly.
- Two-element control: Uses both the drum level and the steam flow. This is preferable for small changes.
- Three-element control uses the level of the drum, the flow of steam, and the flow of feedwater. It works best for changes in high demand.
How to measure boiler water level?
Differential Pressure Cells are the most common way to do things in current systems:
- One side is under pressure from the column of hot water in the boiler (HP).
- The other side is open to a reference leg (LP) that is full of condensate.
Some of the technologies utilized for internal sensing in the transmitter are:
- Capacitive sensing
- Strain gauges
- Inductive ways
These methods find diaphragm deflection and turn it into a level signal, either analog or digital, that works with control systems like DCS/PLC.
What is boiler drum pressure?
The term “boiler drum pressure” refers to the pressure inside the steam drum. This pressure can range from 150 psi to more than 2000 psi, depending on the construction of the boiler.
- The steam drum is composed of high-carbon steel so it can handle very high temperatures and pressures, which can be over 350°F (175°C).
- This pressure is very important for figuring out the saturation temperature, which in turn tells us the density of steam and water.
We always check the drum pressure to make sure:
- Safe operation
- Consistent steam quality
- Correct level compensation in DP transmitters
Why 3 elements instead of 2 elements in boiler?
Three-element control provides superior drum level management, especially under rapid load changes:
- 1st element: Drum water level (primary process variable)
- 2nd element: Steam flow (load indicator)
- 3rd element: Feedwater flow (corrective action)
This setup:
- Anticipates changes in steam demand.
- Adjusts feedwater proactively.
- Minimizes shrink/swell effects in drum level.
In contrast:
- Two-element control omits feedwater flow, leading to delayed responses.
- Single-element control is prone to oscillations under load changes.
What is the normal water level in a boiler?
The Normal Operating Water Level (NOWL) is typically:
- At the midpoint of the boiler’s sight glass
- Verified using two independent indicators:
- Sight glass
- Electronic level transmitter or magnetic gauge
Maintaining NOWL ensures:
- Steam purity (no water carryover)
- Safe margin from low- or high-level trip points
- Balanced heat transfer in boiler tubes
Operators monitor the NOWL visually and via automation systems.