Troubleshooting of a transmitter

Introduction

In this session we are gonna discuss about troubleshooting of a transmitter.we are gonna look into some common problems and their solutions .

What are the troubleshooting when Transmitter milliamp reading is zero

  • Verify power is applied to signal terminals
  • Check power wires for reversed polarity
  • Verify terminal voltage is 10.5 to 42.4 V dc
  • Check for open diode across test terminal

Transmitter Not Communicating with HART Communicator

  • Verify the output is between 4 and 20 mA or saturation levels
  • Verify clean DC Power to transmitter (Max AC noise 0.2 volts peak to peak)
  • Check loop resistance, 250 Ω minimum (PS voltage -transmitter voltage/loop current)
  • Check if unit is addressed properly

 Milliamp reading is low or high Verify applied pressure

  • Verify applied pressure
  • Verify 4 and 20 mA range points
  • Verify output is not in alarm condition
  • Verify if 4 – 20 mA output trim is required

Transmitter will not respond to changes in applied pressure

  • Check impulse piping or manifold for blockage
  • Verify applied pressure is between the 4 and 20 mA set points
  • Verify output is not in alarm condition
  • Verify transmitter is not in Loop Test mode

Digital Pressure Variable reading is low or high

  • Check test equipment (verify accuracy)
  • Check impulse piping for blockage or low fill in wet leg
  • Verify transmitter is calibrated properly
  • Verify pressure calculations for application

Digital Pressure Variable reading is erratic

  • Check application for faulty equipment in pressure line
  • Verify transmitter is not reacting directly to equipment turning on/off
  • Verify damping is set properly for application

Milliamp reading is erratic

  • Verify power source to transmitter has adequate voltage and current
  • Check for external electrical interference
  • Verify transmitter is properly grounded
  • Verify shield for twisted pair is only grounded at one end

 

How to Remove a transmitter from Service ?

• Follow all plant safety rules and procedures.
• Isolate and vent the process from the transmitter before removing the transmitter from service.
• Remove all electrical leads and conduit.
• Detach the process flange by removing the four flange bolts and two alignment screws that secure it.
• Do not scratch, puncture, or depress the isolating diaphragms.
• Clean isolating diaphragms with a soft rag and a mild cleaning solution, and rinse with clear water.
• Whenever you remove the process flange or flange adapters, visually inspect the Teflon o-rings. Replace the o-rings if they show any signs of damage, such as nicks or cuts. Undamaged o-rings may be reused.

 

Also read 

Calibration procedure of DPT transmitter

How to calibrate RTD transmitter

How to calibrate a Pressure gauge.

Related Articles

Leave a Reply

Back to top button

Adblock Detected

We Noticed You're Using an Ad Blocker Hi there! We understand that ads can be annoying, but they help support our website and allow us to continue providing you with high-quality content. Please consider whitelisting our site or disabling your ad blocker while you visit. Your support means a lot to us! Thank you for understanding!