Calibration

How to Calibrate Thermocouple Transmitter

Introduction

A thermocouple is a sensor used to convert temperature into an electric signal. It consists of 2 dissimilar metals joined together to form junctions. In this session we are going to discuss about Thermocouple transmitter calibration

Working principle  

Seebeck effect: the emf produced in the thermocouple is proportional to the temperature difference between 2 junctions (hot &cold)

How to Calibrate Thermocouple Transmitter

Different types of thermocouples

J type, k type, T type, E type, R type, S type

Thermocouples

Equipments required for calibration

24 vdc supply, multimeter, transmitter, mill volt source(725 process calibrator)

Equipments required for calibration

Procedure for calibrating thermocouple transmitter.

Procedure for calibrating thermocouple transmitter

  • Connect the circuit as shown in fig
  • Put multimeter into ma.
  • Let us look at this calibration procedure through an example
Example:

LRV=0 degree Celsius   and URV=200 degree Celsius

So 5 point calibration values be like this

4ma-0 degree Celsius

8ma-50 degree Celsius

12ma-100 degree Celsius

16ma- 150 degree Celsius

20ma- 200 degree Celsius

So right now we know the corresponding values of temp to ma

  • In process calibrator select thermocouple option.
  • And give different values of temperature in process calibrator and check the ma in multimeter and by adjusting zero and span potentiometer in the transmitter correct the ma values.
  • Repeat this procedure.

To know about Thermocouple basics and types of thermocouple.

Related Articles

Leave a Reply

Back to top button

Adblock Detected

We Noticed You're Using an Ad Blocker Hi there! We understand that ads can be annoying, but they help support our website and allow us to continue providing you with high-quality content. Please consider whitelisting our site or disabling your ad blocker while you visit. Your support means a lot to us! Thank you for understanding!