Table of Contents
- Simulating a 4-20mA signal in an analog input loop using a loop calibrator is a fundamental task for commissioning and troubleshooting instrumentation in a process plant.
- This procedure ensures that the analog input loop and associated transmitter are functioning correctly, providing accurate and reliable data to the control system.
Step 1. Safety Precautions
Before commencing the simulation, it is crucial to adhere to the following safety precautions:
- Personal Protective Equipment (PPE): Wear appropriate PPE, including safety glasses, gloves, and protective clothing.
- Isolation: Ensure the loop is isolated from the control system to avoid false alarms and potential system disturbances.
- Lockout/Tagout (LOTO): Follow the LOTO procedure to ensure the loop is de-energized and safe to work on.
- Verify Instrumentation: Confirm that all instruments are correctly installed and calibrated.
- Environmental Considerations: Be aware of the environmental conditions, such as explosive atmospheres, and take necessary precautions.
Step 2. Required Tools and Equipment
- Loop Calibrator (capable of sourcing and measuring 4-20mA signals)
- Multimeter
- Standard tools
- Documentation (P&IDs, instrument loop diagrams, datasheets, and calibration certificates)
- Personal Protective Equipment (PPE)

Step 3. Preparation for Loop Checking
Review Documentation
- Verify the loop diagrams, P&IDs, and datasheets to understand the configuration and specifications of the analog input loop and transmitter.
- This step ensures that you have a clear understanding of the system layout and can identify the correct points for testing and connection.
Inform Control Room
- Notify the control room and relevant personnel about the upcoming simulation test.
- Ensure they acknowledge and understand the test to avoid unnecessary alarms.
- Communication is key to avoid false alarms and confusion during the simulation.
Isolate the Loop
- Use the LOTO procedure to isolate the loop from the control system. Ensure that the loop is de-energized and tagged out.
- This ensures safety and prevents any unintended interactions with the control system during the test.
Visual Inspection
- Conduct a visual inspection of the loop components, including wiring, connectors, and the transmitter, to identify any visible defects or damage.
- Identifying and addressing any physical issues before testing can save time and prevent potential hazards.
Step 4. Connect the Loop Calibrator

Identify Test Points
- Identify the test points where the loop calibrator will be connected. Typically, these are at the transmitter’s terminals or a designated test junction box.
- Knowing the exact points for connection ensures a smooth setup.
Disconnect the Transmitter
- Disconnect the transmitter from the loop if necessary.
- This prevents interference with the calibration signal and ensures accurate simulation.
- Isolating the transmitter can help in getting a clear and accurate calibration signal.
Connect the Calibrator
- Connect the loop calibrator to the analog input loop. Ensure proper polarity and secure connections to avoid loose connections that could affect the simulation.
- Proper connections are crucial for accurate signal simulation and measurement.
Step 4. Simulate the 4-20mA Signal
Power On the Calibrator
- Turn on the loop calibrator and set it to source mode.
- Ensure the calibrator is configured correctly to simulate a 4-20mA signal.
- Correct configuration of the calibrator is essential for an accurate simulation.
Zero Signal (4mA)
- Set the calibrator to output 4mA.
- Verify that the analog input module and control system register the correct signal.
- Record the readings from the control system, ensuring they match the expected 4mA signal.
- This initial step confirms that the zero-point is correctly calibrated.
Mid-Range Signal (12mA)
- Set the calibrator to output 12mA.
- Verify that the analog input module and control system register the correct signal.
- Record the readings from the control system, ensuring they match the expected 12mA signal.
- This mid-range check helps verify linearity.
Click here for 4-20mA to PV scaling calculator
Full-Scale Signal (20mA)
- Set the calibrator to output 20mA.
- Verify that the analog input module and control system register the correct signal.
- Record the readings from the control system, ensuring they match the expected 20mA signal.
- This ensures the full-scale end of the range is correct.
Note: Allow the system to stabilize after setting each mA value before taking readings. This ensures that transient effects do not affect the measurement.
Intermediate Signals
- Optionally, simulate additional intermediate signals (e.g., 8mA, 16mA) to verify linearity and response of the loop.
- Record the readings from the control system for these intermediate signals.
- Intermediate checks can provide a more detailed view of the system’s linearity and performance.
Signal Drift
- Observe the signal for any drift over time. Record the readings at intervals to check for stability.
- This can help in identifying potential issues with the transmitter or calibrator.
Alarm Checks
- Verify that the control system alarms are functioning correctly based on the simulated signals. This includes high, low, and failure alarms.
HART Communicator (if applicable)
- If the transmitter is HART-enabled, use a HART communicator to verify and document the transmitter’s digital signal in parallel with the analog signal. This provides an additional way of validation of simulation process.
Step 5. Troubleshooting (if necessary)
Check Connections
- If the readings do not match the expected values, check all connections to ensure they are secure and correct. Loose or incorrect connections are a common source of errors.
- Use a multimeter to measure the loop current directly at different points to ensure signal integrity. Compare these readings with the control system readings.
- Check the loop’s load resistors. Incorrect resistor values can affect the current signal and thus the readings on the control system.
Click here for How to do the 4-20mA Wiring?
Verify Loop Calibrator
- Verify that the loop calibrator is functioning correctly by testing it on a known good loop or using a multimeter.
- Ensuring the calibrator itself is not faulty can save time in troubleshooting.
Inspect Wiring and Voltage
- Inspect the wiring for continuity, shorts, or grounding issues that could affect the signal. Wiring issues are often the cause of signal problems.
- Verify the power supply to the loop. An unstable or incorrect power supply can cause erratic signal behavior.
- Inspect for ground loops in the wiring, which can introduce noise and affect signal accuracy.
Consult Documentation
- Refer to the transmitter’s datasheet and the control system’s manual for troubleshooting guidelines and specifications.
- Manufacturer documentation can provide specific troubleshooting tips and specifications.
- If the issue persists, consult with colleagues or seek assistance from the manufacturer’s technical support.
- Collaboration can often provide new insights or solutions to complex problems.
Click here for How to do troubleshooting of a 4-20mA loop?
Step 6. Restore the Loop
Reconnect the Transmitter:
- After successful simulation, disconnect the loop calibrator and reconnect the transmitter to the loop.
- Ensure all connections are secure and correct.
Remove LOTO:
- Remove the lockout/tagout devices following the LOTO procedure and re-energize the loop.
- Properly restoring power and removing safety locks is crucial.
Inform Control Room:
- Notify the control room and relevant personnel that the simulation test is complete and the loop is back in service.
- Communication ensures everyone is aware that the loop is back in normal operation.
Verify Normal Operation:
- Verify that the analog input loop and transmitter are operating normally and providing accurate data to the control system.
- A final check confirms the system is functioning correctly post-simulation.
Record Results:
- Document the results of the simulation test, including any observations and deviations.
- Ensure the documentation is signed and dated for future reference. Proper documentation ensures a record of the test for future reference and audits.
Frequently Asked Questions
How to calibrate a 4 to 20 mA loop?
- To calibrate a 4-20 mA loop, connect a loop calibrator, isolate the transmitter, set the calibrator to source mode, and adjust to output 4 mA, 12 mA, and 20 mA, verifying readings at each point.
How do you measure a 4-20 mA current loop?
- To measure a 4-20 mA current loop, connect a multimeter in series with the loop, ensuring proper polarity.
- The multimeter will display the current flowing through the loop, allowing verification of the signal.
What is the difference between 4-20 mA source and simulate?
- “Source” mode actively supplies the 4-20 mA signal, powering the loop.
- “Simulate” mode mimics the signal without providing power, requiring an external power supply for the loop.
What is a mA loop calibrator?
- An mA loop calibrator is a device used to source, measure, and simulate 4-20 mA signals.
- It is essential for calibrating, testing, and troubleshooting analog input loops in instrumentation systems.
Click here for Why not use 0-20mA & 0-15psi instead of 4-20mA & 3-15psi?