Pressure Switch Calibration Procedure: Step by Step Guide

Pressure switch calibration verifies that a pressure switch changes its electrical contact state at the required pressure and resets at the specified pressure. In process industries, pressure switches are used for alarms, equipment interlocks, pump protection, compressor protection, and selected shutdown functions.

A typical calibration uses a suitable pressure source, a calibrated pressure reference, and a multimeter to monitor contact operation. The technician records the pressure at which the switch operates during increasing pressure and the pressure at which it resets during decreasing pressure. The difference between these values is the switching differential, commonly called deadband.

This guide explains the equipment required, safety precautions, calibration setup, rising and falling pressure tests, set point adjustment, deadband and repeatability calculations, troubleshooting, and calibration report preparation.

EquipmentPurpose
Hand pressure pump or suitable pressure controllerApplies controlled increasing and decreasing pressure
Calibrated pressure gauge or digital pressure calibratorProvides the reference pressure reading
Digital multimeterMonitors contact continuity and changeover
Suitable pressure fittings and tubingConnects the pressure source safely to the switch
Manufacturer datasheetProvides set point, reset point, allowable differential, range, and pressure limits
Calibration reportRecords as found and as left readings and the final result

 

The device contains a micro switch, connected to a mechanical lever and set pressure spring. The contacts get actuated when process pressure reaches the set pressure of the spring. In this session calibration of pressure switch is covered.

  • It can be used for alarming or interlocking purposes, on actuation.
  • It can be used for high / high-high or low /low-low actuation of pressure in the process. The set range can be adjusted within the switch range.
  • The sensing element may be a Diaphragm or a piston

Calibration Procedure of the Pressure Switch

Isolate the Pressure Switch and Review Its Settings

Identify the instrument tag, switch type, pressure range, required trip point, reset point or differential, contact configuration, and process connection. Obtain authorization before testing any switch associated with an alarm, interlock, or shutdown function.

Connect the Pressure Source and Contact Monitor

Safely isolate and depressurize the switch. Connect the pressure source and calibrated reference to the correct port. Connect the multimeter to the designated common and NO or NC terminals according to the wiring diagram.

Verify the Initial Contact State

With the switch at its specified initial pressure condition, check the contact state using the multimeter. Record the state of the relevant contacts and verify that it matches the switch wiring diagram and expected operating logic.

Measure the Rising Pressure Trip Point

Increase pressure gradually while monitoring the contacts. When the contact state changes, record the reference pressure as the rising trip point. Approach the switching point slowly enough to avoid overshooting it.

Measure the Falling Pressure Reset Point

Reduce pressure gradually and record the pressure at which the contacts return to their reset state. Do not exceed the maximum allowable pressure simply to perform this test. Follow the manufacturer’s procedure and specified test limits.

Pressure Switch Calibration

Calculate Deadband and Check Repeatability

Calculate the difference between the rising trip point and falling reset point. Repeat the test under consistent conditions and compare the readings with the manufacturer’s specifications and approved acceptance criteria.

Adjust the Pressure Switch if Required

If the as found results do not meet the specified requirements, inspect the setup and switch condition before adjustment. Adjust the set point or differential only when the switch design permits it, following the manufacturer’s instructions. Repeat the tests after adjustment.

Restore the Switch and Complete the Calibration Report

Safely remove the test pressure, reconnect the process connection and electrical wiring, check for leaks, restore authorized bypasses, and confirm normal operation. Record as found and as left readings, acceptance criteria, adjustments, and the final result.

Test cycleRising trip pressureFalling reset pressureDeadband
18.00 bar7.20 bar0.80 bar
28.05 bar7.25 bar0.80 bar
38.00 bar7.20 bar0.80 bar
ProblemPossible causeRecommended action
Switch does not change stateIncorrect terminals, damaged contacts, insufficient pressure, or faulty mechanismVerify the wiring diagram, contact continuity, pressure source, and switch condition
Trip pressure is too highIncorrect setting, wrong pressure reference, or mechanical driftVerify the reference equipment and configured set point before adjusting
Reset pressure is inconsistentUnstable pressure source, friction, or switch mechanism wearApply pressure slowly and repeat the test under consistent conditions
Deadband is greater than specifiedIncorrect differential setting, wear, or damaged mechanismCheck the manufacturer’s adjustment method and permitted differential
Trip point changes between testsPressure overshoot, inadequate stabilization, or mechanical instabilityImprove pressure control and repeat the test
NO and NC states appear reversedIncorrect terminal identification or misunderstanding of the normal stateCheck the terminal diagram and confirm the specified initial pressure condition
Switch fails after reinstallationIncorrect wiring, leakage, incorrect installation, or process connection issueVerify wiring, connection integrity, and operation under the approved return to service procedure
  • Isolate the switch from process pressure and verify that stored pressure has been safely released.
  • Confirm the test pressure source, gauge, fittings, tubing, and adapters are rated for the intended pressure.
  • Use suitable protective measures when testing high pressure, hydraulic, toxic, corrosive, or flammable process services.
  • Do not disconnect or test energized electrical contacts unless the approved procedure and hazardous area requirements permit it.
  • For switches used in safety instrumented functions or critical trips, obtain authorization and apply the approved bypass, impairment, and restoration procedure.
  • Confirm the correct contact state and process response before returning the switch to service.
Report fieldInformation to record
Instrument identificationTag number, location, manufacturer, model, and serial number
Switch configurationRising or falling trip, NO and NC terminal identification
Required settingsSpecified trip point, reset point, and allowable deadband
Reference equipmentPressure calibrator identification, range, and calibration due date
As found resultsInitial trip point, reset point, deadband, and contact state
Adjustment detailsAdjustment performed, if any, and reason
As left resultsFinal trip point, reset point, deadband, and contact state
Acceptance criteriaRequired limits and source of the limits
Final statusPass or fail, technician, date, and remarks

Pressure switch calibration verifies that the switch operates and resets at the specified pressures. It also checks contact operation and switching differential.

Trip pressure is the pressure at which the switch changes state in the specified direction. Reset pressure is where the switch returns to its previous state.

For a rising pressure trip and falling pressure reset, subtract the reset pressure from the trip pressure. Compare the result with the manufacturer’s specified differential.

Typical equipment includes a suitable pressure source, calibrated pressure reference, digital multimeter, compatible fittings, and the manufacturer’s datasheet.

Use a pressure source and reference suitable for the low pressure range. Increase and decrease pressure slowly while recording the contact changeover points.

Repeatability indicates how consistently the switch operates under the same test conditions. Poor repeatability may indicate instability, mechanical wear, or problems with the test setup.

No. Record the as found results first and compare them with the specified acceptance criteria. Adjust the switch only when required and permitted by the manufacturer.

Record the instrument tag, specified settings, reference equipment, trip and reset pressures, deadband, as found and as left results, acceptance criteria, and final status.