What are the Characteristics of trip Curves of the MCB?

Trip Curve of MCB:

The Trip Curve is a graphical representation of the circuit protection devices. Fuse, MCB’s, MCCB’s, supplementary protectors, motor protection circuit breakers, overload relays, electronic fuses, and air circuit breakers are all examples of circuit protection devices.

The multiples of the current going through the miniature circuit breaker are represented on the horizontal X-axis. On a logarithmic scale, the Y-axis displays the miniature circuit breaker tripping time.

Typical Characteristic Curve of MCB

The characteristic curve indicates the correlation between the current and the tripping time.

MCB have:

  • Type B characteristic curves 
  • Type C characteristic curves 
  • Type D characteristic curves 
  • Type K characteristic curves 
  • Type Z characteristic curves 

They’re listed below:

The classification of Type B, C, or D is based on the breakdown current rating at which electromagnetic operation occurs to give short-term protection against short circuits. The trip curve is a graph defined between the outgoing current and the tripping time (amp-sec Curve) to provide proper equipment protection and performance and avoiding unwanted tripping.

Type B characteristic curves:

3 to 5 times in the magnetic trip for use in household operations when maximum sensitivity is required and there is little equipment that requires significant start up current. When loads are resistive and there is no in-rush current, B curve MCBs should be used.

TYPE B MCB CURVE
TYPE B MCB CURVE

Type C characteristic curves:

For commercial and industrial applications, Type C devices are the standard. These devices are designed to trip when the current is 5-10 times the rated current i.e., 50-100A for a 10A electrical device. When loads have a negligible amount of in-rush current on initiation, C curve MCBs should be used. Small transformer load is the ideal application.

TYPE C MCB CURVE

Type D characteristic curves:

The Type D devices have more limited uses, generally in industrial use where high inrush currents can be expected large battery charging systems, winding motors, power transformers, X-ray devices, and certain discharge lighting sources .

Type D devices are intended to trip 10-20 times per second i.e., 100-200A / 20A electrical device. Normal connection ratings refer to the amount of time a cable can be used continuously under certain installation conditions. Of course, cables can high currents for a limited time without damage.

TYPE D MCB CURVE

   

Type K characteristic curves:

The K curve MCB is designed for motor applications where ampere rises quickly and rapidly during “start-up.” Curves can go through the transitory inrush of current and minimise nuisance tripping while providing circuit protection. In less than 0.01 seconds, the magnetic element of the K curve interrupts a short circuit at 10 times of the rated current. At 10 times the rated current, the K curve tripping bandwidth will vary from 0.01 second.

TYPE K MCB CURVE

Type Z characteristic curves:

When the current flowing through an MCB with type Z trip characteristics exceeds 2 to 3 times the rated current, it trips instantly. These MCBs are extremely sensitive to short circuits and are used to protect extremely sensitive electronics devices like semiconductors devices. Low short circuit trip settings are required for Z type MCB.

TYPE Z MCB CURVE

Some Useful Questions:

1.What is ideal trip curve?

The ideal curve is the desired curve for the bimetallic strip because of its nature and since the exact tripping point cannot be pointed out in the ideal MCB.

2. Which MCB curve is ideal for use at houses?

Circuits with equipment that does not create surge current, such as lighting and distribution circuits are protected by ‘B’ Curve MCBs. They are the appropriate choice for home applications and household appliances that mostly use resistive load.

3. Why Low short circuit trip settings are required for Z type MCB ?

Since Z curve MCBs are highly sensitive, they will trip when the current exceeds the rated load by two to three times. They’re employed on more delicate instruments that are sensitive to short circuits.

4.What is in-rush current?

When a power source or electrical equipment is turned on, it draws a high input current. The high input currents necessary to charge the capacitors, inductors, and transformers, it is termed as in-rush current. The switch–on surge, or input surge current, is other term for the in-rush current. These currents can be up to 20 times high than steady state current.

5.Does the MCB trip when the voltage is high?

Overvoltage can cause the MCB to trip. When the system voltage is higher, the load provided by the MCB demands more current, which may be greater than the MCB’s rating. The MCB’s built-in protection is current operated, and it will trip if it detects a current greater than its rating.

Rabert T

As an electrical engineer with 5 years of experience, I focus on transformer and circuit breaker reliability in 110/33-11kV and 33/11kV substations. I am a professional electrical engineer with experience in transformer service and maintenance. I understand electrical principles and have expertise troubleshooting, repairing, and maintaining transformers, circuit breakers, and testing them. Tweet me @Rabert_infohe

Related Articles

Back to top button

Adblock Detected

We Noticed You're Using an Ad Blocker Hi there! We understand that ads can be annoying, but they help support our website and allow us to continue providing you with high-quality content. Please consider whitelisting our site or disabling your ad blocker while you visit. Your support means a lot to us! Thank you for understanding!