Engineering Units to PLC Raw Counts Conversion Calculator

- Purpose and use of the Engineering Units to PLC Raw Counts Calculator
- How to use the Engineering Units to PLC Raw Counts conversion Calculator?
- Example: Calculating Raw Value using a 16-Bit PLC
- Frequently Asked Questions (FAQ) on Raw Value and Engineering Units in PLC Systems
- What is a raw value (or native value) in PLC?
- What are engineering units in PLC?
- What is meant by engineering units?
- What is raw count in a PLC?
- How is scaling performed in a PLC?
- Why are raw values and engineering units important?
An Engineering Units to Raw Counts Calculator is a useful tool that allows the conversion of the physical measurements made using the engineering units such as temperature, pressure, or flow rate into figures that are in raw count form that PLC or any other digital control system can process. Such raw counts are expressed in the form of sensor data without having gone through any further arithmetic calculation; the outcome usually falls within a certain range set by the resolution of the PLC.
Click here for Calculator/Instrumentationtool for Raw Counts value to Engineering Units
Purpose and use of the Engineering Units to PLC Raw Counts Calculator
This calculator is essential in industrial automation and process control systems, where:
- DCS, PLCs, or microcontrollers frequently call for raw count early values to perform calculation or interact with another system.
- Sensors give sensible units of measurement (°C, PSI etc.). All these have to be converted back to raw count form for correct system interfacing.”
- This calculator is employed by engineers for purposes of approximating raw counts useful in testing and calibrating equipment.
- Closes values properly for the specified ranges of sensors and controllers.
- Enables the linking of devices that have apparently dissimilar data types or scales.
Click here for Collection of PLC Digital Signal Calculators for Industrial Automation
How to use the Engineering Units to PLC Raw Counts conversion Calculator?
Inputs Needed
- Min Scaled Value: Minimum value of the engineering unit range.
- Max Scaled Value: Maximum value of the engineering unit range.
- Min Raw Value: Minimum raw count (e.g., 0 for most systems or specific values for certain sensors).
- Max Raw Value: Maximum raw count (e.g., 65,535 for 16-bit, 4,294,967,295 for 32-bit PLCs).
- Scaled Value: The engineering unit value to be converted into raw counts.
Steps for conversion Calculation
- Input the known minimum and maximum values of both the raw count range and the engineering unit range.
- Enter the engineering unit value you wish to convert to raw counts.
- Apply the formula:
- The calculator will output the raw count value corresponding to the input engineering unit value.
Refer the link for the How a PLC reads the data from field transmitters?
Example: Calculating Raw Value using a 16-Bit PLC
Process parameter Scenario
A temperature sensor gives scaled values from -50°C to +150°C while the raw counts are in the range of 0 to 65,535 in a 16-bit PLC data type as represented in the unsigned integer format. The system gets a signal and it shows 75°C of temperature and raw count values are required to set the programming of the PLC.
Step-by-Step Calculation
Step 1: Gather the Known Parameters
- Scaled Value (Temperature) = 75∘C
- Min Scaled Value = −50∘C
- Max Scaled Value = 150∘C
- Min Raw Value = 0 (PLC raw count minimum)
- Max Raw Value = 65,535 (PLC raw count maximum)
Step 2: Formula for Engineering Units to PLC Raw Counts Conversion Calculator
The formula to calculate the raw value from scaled engineering units is:
Step 3: Substitute the Known Values
Step 4: Round to the Nearest Integer
Since raw counts must be integers, round 40,959.375 to the nearest whole number:
Raw Value=40,959
For a scaled temperature value of 75°C, the corresponding 16-bit raw count value is 40,959.
The sensor’s reading of 75∘C falls within the scaled range of −50∘C to 150∘C, and the calculated raw count of 40,959 represents this value as interpreted by the 16-bit PLC. This make sure that there is the right transfer of information between the sensor and the PLC system.
Click here to access 200+ Online Instrumentation Calculators Collections
Frequently Asked Questions (FAQ) on Raw Value and Engineering Units in PLC Systems
What is a raw value (or native value) in PLC?
The unprocessed value of a variable as it is kept in memory is known as the raw value, or native value. This value is frequently encoded or in a format that is directly connected to the output of the sensor or device.
In memory, a frequency variable of 50.2 Hz could be represented by an integer, like 502, because of scaling.
In a PLC, “counts,” which are integers that represent the electrical output of the sensor within its natural range, are frequently used to convey the raw input
What are engineering units in PLC?
The practical measurement that a sensor is detecting is represented by engineering units (EUs), which are physical values like temperature, pressure, or flow rate. For instance:
The PLC may interpret a temperature sensor’s raw value, which ranges from 0 to 18,000 counts. This range could be equivalent to 0°C to 150°C in engineering terms.
The engineering units in this case offer significant practical values that are based on the raw counts.
What is meant by engineering units?
Standardized measuring units called engineering units are used to quantify physical characteristics like temperature (e.g., degrees Celsius or Fahrenheit).
Pressure (such as psi or Pascals)
Rate of flow (liters per second, for example)
Energy, such as Joules
These units enable uniformity and understanding in a variety of engineering and industrial settings.
What is raw count in a PLC?
The unscaled digital value produced by a sensor or analog input module in a PLC is known as a raw count. This amount:
- is usually an integer that represents the sensor’s electrical signal.
- falls under a predetermined range, for example, 0 to 65,535 for a 16-bit input card or 0 to 8,092 for a 12-bit analog input card.
- For practical purposes, the raw count needs to be adjusted to engineering units.
How is scaling performed in a PLC?
Scaling in a PLC converts raw input values (counts) into meaningful engineering units (e.g., °C, psi).
The formula for scaling is:
Where:
- Raw Input Value = Raw count from the sensor
- ZeroIn = Minimum raw value of the input range
- SpanIn = Maximum raw value of the input range
- ZeroOut = Minimum value of the desired engineering unit range
- SpanOut = Maximum value of the desired engineering unit range
Why are raw values and engineering units important?
- Raw Values: Crucial for calibration, troubleshooting, and communication at the hardware level.
- Units of Engineering: Enable relevant data interpretation and analysis by engineers and operators to improve process control and decision-making.
The smooth integration of sensors, PLCs, and industrial processes is made possible by this differentiation and conversion between raw values and engineering units.