Instrumentation Calculators

DP calculator for bubbler method Interface level measurement – Transmitter installed with Constant Tank Level and single Bubble Tube

DP calculator for bubbler method Interface level measurement - Transmitter installed with Constant Tank Level and single Bubble Tube

URV = Upper-range value (a measurement with a 20 mA output).

SG = A liquid’s specific gravity (relative density). Water has a specific gravity of 1.00 in both traditional and SI systems.

HW= Equivalent Headlevel pressure of Water

SG1 = Specific gravity of upper liquid (lighter liquid)

SG2 = Specific gravity of lower Liquid (Heavier liquid)

H = Height of the bubble tube immersed inside the process liquid

H1 = Interface level need to be measured.(head between LRV and URV)

H2 = Head level below minimum interface level

Formula for Span value calculation

Span value of the transmitter  =  (H1)*(SG2 – SG1)

Formula for LRV estimation

Equivalent Head level pressure of Water(HW) at Lower range value

HW at LRV = (H1*SG1) + (H2*SG2) = Suppression

Formula for URV estimation

Equivalent Head level pressure of Water(HW) at Higher range value

Hw at URV =  (H1 +H2)*SG2

DP calculator 

This below calculator used to calculate the Span value, LRV and URV of the transmitter for calibration in interface level measurement

Click here for more Instrumentation Calculators

Sundareswaran Iyalunaidu

With over 24 years of dedicated experience, I am a seasoned professional specializing in the commissioning, maintenance, and installation of Electrical, Instrumentation and Control systems. My expertise extends across a spectrum of industries, including Power stations, Oil and Gas, Aluminium, Utilities, Steel and Continuous process industries. Tweet me @sundareshinfohe