- What is an Earth Fault?
- What is earth fault relay and how is it different from RCCB?
- How does an earth fault relay work?
- What is the function of the earth relay?
- What is the function of the earth fault?
- What is a ground fault relay?
- How to check an earth fault relay?
- Earth Fault Protection Devices
- Earth Leakage Circuit Breaker (ELCB)
- Ground Fault Circuit Interrupter (GFCI)
- Restricted Earth Fault Protection (REFP) – explained
- Example – Restricted Earth Fault Protection (REFP) Scheme
- Common Earth Fault Protection Devices (overview)
What is an Earth Fault?
An earth fault occurs when there is an unintentional connection between a live conductor and the earth. This fault results in a short circuit within the electrical system, causing fault current to flow through the system. The fault current returns via the earth or through electrical equipment, potentially damaging the equipment, disrupting the power supply, and posing a risk of electric shock to users. To safeguard equipment and ensure the safety of individuals, earth fault protection devices are implemented.
What is earth fault relay and how is it different from RCCB?
The earth fault relay is a type of relay that can sense the faults between the phase and earth. The major function of an earth fault relay is to operate for the leakage currents to the earth. This relay can detect the earth’s fault, so we can say that RCCB does the same function. The earth fault relay is an advanced device, RCCB is used to prevent electric shock and thus it can provide human protection but the EFR is not used for human protection it is used to protect the equipment.

How does an earth fault relay work?
Principle of operation
- CTs (usually one or more) monitor current in the protected zone.
- Under balanced conditions, the vector sum of currents through a neutral CT (or CT array) is zero.
- If part of the current leaks to earth, the imbalance produces a residual current or induced EMF in the CT secondary.
- The EFR measures this residual current and, when it exceeds a set pickup and time delay, energizes its output contact to trip a breaker.
Key functional elements
- Sensing input: CT(s) arranged as a summation/neutral CT, or dedicated residual CT.
- Measurement stage: Electronic detection of residual current magnitude and waveform.
- Logic & timing: Settings for instantaneous, time-delayed, definite time or inverse time operation.
- Output/trip: Relay contact(s) that drive a circuit breaker trip coil or a tripping interface in a protection system.
- Auxiliary features: Alarms, event logging, adjustable thresholds, and sometimes overcurrent/inrush suppression.
Engineer note
EFRs are programmable to avoid nuisance tripping from magnetizing inrush or transient disturbances by using start/blocked ranges, restraint, or blocking during inrush windows.
What is the function of the earth relay?
An earth relay, also known as an earth fault relay, is designed to detect faults where a live conductor comes into contact with the earth or ground. Its primary function is to sense abnormal earth fault currents and provide a tripping signal to circuit breakers, which then isolate the faulty section of the electrical system. This prevents potential hazards such as electrical shock, fire, and equipment damage, and ensures the safety of both personnel and the electrical system.
What is the function of the earth fault?
The function of the earth fault is to serve as a protective mechanism by detecting any unintended connection between a live conductor and the earth. When an earth fault occurs, it creates a low-resistance path for current to flow to the ground. This abnormal current flow can cause damage to electrical equipment, disrupt the continuity of power supply, and pose a significant safety hazard. Earth fault detection systems are crucial for quickly identifying and isolating these faults to minimize risks and damage.
What is a ground fault relay?
A ground fault relay is a protective device used to detect ground faults (also known as earth faults) in an electrical system. It monitors the current flow in a circuit and compares the current entering and leaving a protected zone. If there is an imbalance, indicating that some current is leaking to the ground, the relay trips the circuit breaker to disconnect the faulty section from the power supply. Ground fault relays are essential for preventing equipment damage, electrical fires, and ensuring the safety of personnel by quickly isolating ground faults.
How to check an earth fault relay?
By following these steps, you can verify that the earth fault relay is operating correctly and is able to provide effective protection against earth faults.
Visual Inspection
- Ensure that the relay is properly installed and all connections are secure.
- Check for any visible signs of damage or wear on the relay.
Functional Testing
- Primary Injection Test: Apply a simulated earth fault current to the relay using a primary injection test set. This tests the relay’s response to actual fault conditions by injecting current through the system’s primary conductors.
- Secondary Injection Test: Use a secondary injection test set to inject a known current directly into the relay’s input terminals, bypassing the system’s primary conductors. This allows you to test the relay’s settings and tripping accuracy.
Operational Test
- Simulate an earth fault condition by applying a small test current to the relay and observing if it correctly trips the associated circuit breaker.
- Reset the relay and repeat the test to ensure consistent performance.
Inspection of Relay Settings
- Verify that the relay’s settings, such as current sensitivity and time delay, are correctly configured according to the system’s protection scheme.
Testing Documentation:
- Record the test results, including trip times and current levels, and compare them with the relay’s specifications and manufacturer guidelines.
Calibration Check:
- If necessary, perform a calibration check to ensure the relay operates within its specified parameters. Calibration should be done by a qualified technician using appropriate testing equipment.
Earth Fault Protection Devices
These devices are designed to trip the circuit when an earth fault occurs, thereby limiting the fault current and mitigating damage through a Restricted Earth Fault Protection (REFP) scheme. Common devices used for this purpose include earth fault relays, earth leakage circuit breakers, and ground fault circuit interrupters.
Earth Leakage Circuit Breaker (ELCB)
An Earth Leakage Circuit Breaker detects leakage current directly and is primarily used to prevent electric shocks to humans and animals. It operates as a voltage-sensing device. In recent years, it has been largely replaced by the Residual Current Circuit Breaker (RCCB), a current-sensing device. The ELCB is a specialized latching relay connected to the main power supply. When a fault current flows from the live wire to the earth wire, the ELCB senses the voltage difference and cuts off the power supply. To restore power, the ELCB requires a manual reset. On the other hand, the RCCB detects the leakage current and automatically trips the system to prevent further damage or injury.
Ground Fault Circuit Interrupter (GFCI)
The Ground Fault Circuit Interrupter is a safety device designed to prevent electrical accidents when a faulty tool or appliance is plugged in. It is a fast-acting circuit breaker that disconnects the power supply within 1/40th of a second when an earth fault is detected. The GFCI continuously compares the incoming and outgoing currents in the circuit. If there is any discrepancy, even as small as 5 mA, the GFCI quickly restricts the current and trips the circuit. Although GFCIs do not offer protection against line contact hazards, they are effective in preventing fires, overheating, and damage to wire insulation.
Restricted Earth Fault Protection (REFP) – explained
Purpose: Provide high sensitivity and selectivity for internal earth faults inside a defined zone of a transformer or generator winding.
How REFP works
- CTs are placed on each phase of the transformer secondary and their secondaries summed (vectorially).
- For external faults, phase currents cancel out and resultant is near zero — no trip.
- For internal earth fault inside the protected zone, current from one or more phases produces a net residual current that flows through the REFP relay.
- The relay trips rapidly to isolate the faulted winding portion before severe damage occurs.
Design considerations:
- Proper CT ratio, polarity and wiring to ensure correct summation.
- Stabilizing networks or restraint to avoid tripping for magnetizing inrush.
- Sensitivity set low enough to detect incipient faults but high enough to reject noise.
Example – Restricted Earth Fault Protection (REFP) Scheme
Consider a star-wound transformer protected by a Restricted Earth Fault Protection scheme using an Earth Fault Relay (EFR).

In this setup, when an external fault (F1) occurs in the network, currents I1 and I2 flow through the secondary side of the current transformers (CTs). The resultant of I1 and I2 is zero, so no action is taken. However, if an internal fault (F2) occurs within the protected zone, only I2 flows, with I1 being negligible. The resultant current I2 passes through the earth fault relay, which detects the fault and protects the restricted portion of the winding. The fault current in this case is typically around 15% higher than the rated winding current. To prevent the relay from tripping due to magnetizing inrush current, a stabilizing current is placed in series with the relay.
Common Earth Fault Protection Devices (overview)
| Device | Purpose | Typical Pickup | Typical Use |
| Earth Fault Relay (EFR) | Detects residual/earth currents using CTs | Adjustable (A to hundreds of A) | Transformers, substations, plant distribution |
| RCCB / RCD / GFCI | Detects small leakage currents for human safety | 10 mA to 300 mA typical | Consumer circuits, plant sockets, local personnel protection |
| ELCB (Voltage sensing) | Older voltage-sensing earth leakage device | Voltage threshold | Largely obsolete; replaced by RCCB |
| Restricted Earth Fault Protection (REFP) | Fast sensitive protection for transformer winding zones | Low pickup, fast | Transformer differential/secondary winding protection |