How to
Troubleshooting of I to P Convertor (Current to Pneumatic converter)
Table of Contents
- Step by Step procedure for Troubleshooting of I to P Convertor(Current to Pneumatic converter)
- What is I to P Converter?
- Safety Precautions
- Symptom 1: No Output Pressure
- Symptom 2: Maximum Output not available or not reachingÂ
- Symptom 3: Zero adjustment not responding
- Symptom 4: Erratic Operation
- Symptom 5: High Output Signal Air Pressure
- Symptom 6: Irregular Output due to PLC Signal or Faulty Output Cards
- Symptom 7: Problem with Signal Isolator or Analog Junction Box Issues
- Symptom 8: Signal Oscillation due to PID Parameter in Control Loop
- Symptom 9: Environmental Problems
- Step-by-Step procedure for Cleaning of I to P Convertor Orifice:
- Step-by-Step procedure for maintenance of Flapper Nozzle assembly
- Checklist For Troubleshooting Maintenance of I to P Converter
Step by Step procedure for Troubleshooting of I to P Convertor(Current to Pneumatic converter)
What is I to P Converter?
- An I/P converter functions as a current-to-pressure transducer in industrial control systems, translating a 4- 20 mA current analog signal (I) into a 3 to 15 Psi pneumatic output (P).
- This converter is crucial for converting DC current signals into proportional pneumatic pressure, enabling the control of valves, dampeners, actuators, brakes, and clutches in industrial applications.Â
- It is worth noting that there are two main types of converters: I to P converters, which typically handle a 4-20mA signal, and E to P converters, which work with a 0-10V signal. While IP converters operate with current, EP converters function with voltage.
Safety Precautions
- It is critical to ensure that all workers participating in the troubleshooting process have received extensive training and have a solid understanding of the specific I/P converter model and its associated systems.
- Prioritize the use of suitable personal protective equipment (PPE), such as safety glasses and gloves, and ensure that the gear chosen is compatible with the potential hazards in the process area.
- Before beginning any troubleshooting actions, it is critical to isolate the I/P converter via lockout/tagout methods, preventing unintentionally energization or pressure release during the diagnostic process inside the converter.
- Take the hazardous area classifications inside the process environment into careful consideration, and use equipment that conforms with safety requirements related to potentially explosive or dangerous circumstances.
- To reduce the risk of electrical short circuit, always turn off the power to the I/P converter before beginning any troubleshooting actions, and follow all approved safety protocols.
- Release any leftover pneumatic pressure in the system to ensure a safe working environment and prevent unexpected releases during the inspection or disassembly of the I/P converter.
- Conduct a thorough assessment of the I/P converter and its accompanying equipment, looking for apparent damage or signs of wear.
- Follow the manufacturer’s directions and recommended troubleshooting techniques to the letter, consulting the technical documentation given for the specific I/P converter model.
- Create clear and effective communication lines with other staff in the area, such as operators and maintenance teams, to relay information regarding ongoing troubleshooting activities.
- In the event of unanticipated situations or issues during the troubleshooting process, familiarize yourself with and have quick access to emergency procedures, including protocols for emergency shutdowns.
- Maintain proper ventilation in the work space to prevent the accumulation of harmful gasses or fumes, hence contributing to a safe troubleshooting environment.
Symptom 1: No Output Pressure
Problem | Possible Causes | Suggested Action |
Reversed Current Polarity or Faulty Connections in input signal wires | Check wiring and signal continuity with millimeter. | Repair if faulty. |
Broken Internal Wiring | Check instrument resistance with ohmmeter. | Correct as needed. Replace the faulty component. |
No Air Supply | Ensure sufficient air supply.Isolation valve may closed.No air from the Regulator or regulator may be faulty. | Verify air supply and address any issues. Inspectand verify the the isolation valve in the instrument air line. Replace faulty regulator |
Symptom 2: Maximum Output not available or not reachingÂ
Problem | Possible Causes | Suggested Action |
Insufficient instrument supply air pressure | Check and adjust supply pressure to required | Ensure an adequate supply pressure with instrument data sheet |
Damaged Coil or Nozzle / orifice | Replace the damaged component. | Replace the damaged part. |
Oil Contamination | Inspect for oil contamination. | Clean or replace affected parts. |
Clogged Restrictor | Check and clear any blockage. | Verify the air flow or replace the restrictor. |
Actuator or positioner faulty | Investigate if positioner or actuators are stuck open. | Perform maintenance on faulty components. |
Symptom 3: Zero adjustment not responding
Problem | Possible Causes | Suggested Action |
Worm out or Disengaged with Pinion (After Excessive Adjustment) | Re-engage components. | Ensure proper engagement of zero adjustment mechanisms. |
Zero Calibration Error on Initial Turn-On | Repeat the exercise using the instrument multiple times. | Recalibrate if necessary. |
Symptom 4: Erratic Operation
Problem | Possible Causes | Suggested Action |
Electrical Input Signal | Loose wires or connections in input signals, short circuit in the signal connections. | Reconnect and secure wiring. Verify signal stability. |
Liquid in Air Supply | Check air supply for contamination | Clean air supply or replace the filter of regulator |
Output Pressure same as Supply Pressure | Pneumatic connections reversed.Supply and output both connected to input port | Ensure supply is connected to the “IN” port.Verify output is connected to the “OUT” port. |
Transducer generate reverse output | Wires connected in reverse. | Check and correct the wiring connections. |
Sluggish Performance or Reduced Range | Plugged or blocked orifice /nozzleSupply pressure too low | Remove orifice /nozzle screw and clean orifice/nozzle with wire or pin Supply pressure must be at least 5 PSIG above the 100% output |
Symptom 5: High Output Signal Air Pressure
Problem | Possible Causes | Suggested Action |
Excessive Supply Pressure | Check and adjust supply pressure. | Ensure supply pressure within specified range in output of regulator. |
Damaged Diaphragm or Seal in Pneumatic relay | Inspect diaphragm or seals for damage. | Replace damaged diaphragm or seals. |
Calibration Error | Verify calibration settings. | Recalibrate I/P converter if necessary. |
Electrical Signal Error | Check for erratic electrical signals. | Inspect wiring and connections for issues. |
Restricted Exhaust Flow | Check for blockages in exhaust path in the converter. | Clear or replace any obstructed components. |
Click here for Procedure for Calibration of I To P Converter
Symptom 6: Irregular Output due to PLC Signal or Faulty Output Cards
Problem | Possible Causes | Suggested Action |
Fluctuating Output current signal | Inconsistent PLC signal. | Verify and stabilize the signal from the PLC. |
No Output Signal from PLC | PLC signal not reaching the I/P converter. | Check PLC programming and connections. |
Incorrect Output Scaling | Mismatch between PLC output scaling and I/P converter input requirements.(4 – 20mA) | Adjust scaling parameters in the AO card of PLC. |
Faulty analog Output Cards in Control System | Malfunctioning output cards in the control system. | Diagnose and replace faulty output cards. |
Symptom 7: Problem with Signal Isolator or Analog Junction Box Issues
Problem | Possible Causes | Suggested Action |
Inconsistent Signal Transmission | Faulty signal isolator or fault in the connections | Inspect isolator or junction box for issues. |
Signal Interference | External electromagnetic interference. | Shield or relocate the signal cables. |
Broken Wiring Connections | Disconnected or damaged wires in the junction box. | Check and repair wiring connections. |
Voltage Drops or Spikes | Power supply issues affecting the isolator. | Verify the stability the power supply to the isolator. |
Symptom 8: Signal Oscillation due to PID Parameter in Control Loop
Problem | Possible Causes | Suggested Action |
Oscillations in Output | Incorrect PID parameters. | Reevaluate and retune PID parameters. |
Slow Response | Proportional, integral, or derivative values that are not ideal. | Adjust PID parameters for desired response. |
Overreactions or Instability in the output. | Aggressive PID settings. | Fine-tune PID parameters for stability. |
Symptom 9: Environmental Problems
Problem | Possible Causes | Suggested Action |
Temperature Fluctuations | Ambient temperature changes affecting the I/P converter. | Install environmental controls or shielding. |
Humidity or Moisture Issues | High humidity causing condensation or moisture ingress. | Seal or protect equipment against humidity. |
Corrosion | Exposure to corrosive substances. | Implement corrosion-resistant control measures. |
Vibration or Mechanical Stress | Vibrations impacting I/P converter stability. | Install vibration dampening or isolation. Otherwise relocate the i to p converter. |
Step-by-Step procedure for Cleaning of I to P Convertor Orifice:
Cleaning the orifice of an I/P (current-to-pressure) transducer is crucial for maintaining accurate pressure regulation. Here’s a step-by-step guide on how to clean the orifice:
Materials Needed:
- Screwdriver set
- Gauge pin or thin wire
Step-by-Step procedure
- Before starting any maintenance, turn off the supply air to the I/P transducer to ensure safety.
- The orifice screw is typically located on the body of the I/P transducer and it can be found on the face of the unit below one of the calibration screws.
- Use a suitable screwdriver to carefully remove the orifice screw from the unit. Inspect the screw for any visible build-up or dust.
- Remove any present build-up on the screw. It’s essential to have a clear path for air flow.
- You will notice a very small hole on the side of the screw. This is the orifice.
- Use a gauge pin or thin wire to carefully run through the orifice hole. This helps clear any internal blockages that may be affecting the pressure regulation.
- Once the orifice is cleared, carefully reinstall the screw into the side of the unit. Ensure that it fits snugly but avoid over-torquing to prevent damage.
- If air is leaking past the screw when supply air is reconnected, tighten the orifice screw further until the leak stops. Be caution to avoid over-tightening.
- Refer to the instruction manual for troubleshooting instructions if you run into more problems or if erratic functionality persists.
- By following these steps, you may keep your I/P transducer’s orifice clear, allowing for constant and accurate pressure adjustment. This type of regular maintenance will add to the unit’s optimal performance and reliability.
Cleaning an I/P Transducer with Flapper Nozzle
If you’re dealing with a flapper nozzle type I/P (current-to-pressure) converter, the cleaning process involves some additional considerations.
Step-by-Step procedure for maintenance of Flapper Nozzle assembly
- Before starting any maintenance activities, turn off the supply air to the I/P transducer to ensure safety.
- Flapper nozzle type I/P converters have a flapper mechanism instead of a traditional orifice. Locate the flapper nozzle on the unit.
- Depending on the model, you may need to remove the cover of the I/P transducer to access the flapper mechanism. Use a suitable screwdriver to carefully remove the cover.
- Inspect the flapper mechanism for any visible blockage, debris, or obstruction. Use a soft brush or compressed air to gently clean the flapper and surrounding area.
- If the flapper nozzle has any visible blockages, use a gauge pin or thin wire to carefully clear them.Make sure there are no obstructions in the way of the flapper’s movement.
- After cleaning the flapper mechanism and nozzle, carefully reassemble the unit. Ensure that all components are properly aligned and secured.
- If you removed the cover, reinstall it properly using the screwdriver.
- Turn on the supply air to the I/P transducer and check its performance. Check for any signs of improper output or unexpected pressure output(calibration error).
- If the output is not within the expected range, refer to the unit’s manual for instructions on adjusting the flapper mechanism or other calibration settings.
- If you encounter persistent issues or need further guidance, refer to the instruction manual for troubleshooting specifics related to the flapper nozzle type I/P converter.
Checklist For Troubleshooting Maintenance of I to P Converter
Refer below link for the downloadable checklist for troubleshooting maintenance of I to P Converter.
Click here for Procedure for Calibration of I to P ConverterÂ