Level Measurement Errors
INTRODUCTION
There are many methods to measure level of a system or a tank (Direct and indirect). Let us discuss about the differential pressure level measurement technique. The indication of fluid level is based on the pressure exerted on a differential pressure (DP) cell by the height of the liquid in the vessel. Level Measurement Errors occur in such technique is what we are going to discuss now
Connections
Many avoidable errors occur because the DP cell had the sensing line connections reversed. In systems that have high operating pressure but low hydrostatic pressure due to weight of the fluid, this is easy to occur. This is particularly important for closed tank systems.
With an incorrectly connected DP cell the indicated level would go down while the true tank level increases.
Over-Pressuring
Three valve manifolds are provided on DP cells to prevent over-pressuring and aid in the removal of cells for maintenance. Incorrect procedures can inadvertently over-pressure the differential pressure cell. If the cell does not fail immediately the internal diaphragm may become distorted. The measurements could read either high or low depending on the mode of failure.
Note that if the equalizing valve on the three-valve manifold is inadvertently opened, the level indication will of course drop to a very low level as the pressure across the DP cell equalizes.
to known more about Three way Manifold valve.
Sensing lines
The sensing lines are the umbilical cord to the DP cell and must be functioning correctly. Some of the errors that can occur are:
1.Obstructed sensing lines
The small diameter lines can become clogged with particulate, with resulting inaccurate readings. Sometimes the problem is first noted as an unusually sluggish response to a predicted change in level. Periodic draining and flushing of sensing lines is a must.
2.Draining sensing lines
As mentioned previously, the lines must be drained to remove any debris or particulate that may settle to the bottom of the tank and in the line. Also, in closed tank dry leg systems, condensate must be removed regularly to prevent fluid pressure building up on the low-pressure impulse line.
Failure to do so will of course give a low tank level reading. Procedural care must be exercised to ensure the DP cell is not over-ranged inadvertently during draining. Such could happen if the block valves are not closed and equalizing valve opened beforehand.