What is the interface liquid level measurement?
Measurement of the interface level is used to keep track of the level of two liquids with different specific gravities. When two liquids are in the same tank but can’t mix, they are separated by an emulsion layer. When two materials that don’t mix well together are put together, the liquid with the heavier molecules will sink to the bottom and the liquid with the lighter molecules will stay on top. Oil and water is a perfect example of this.
If two liquids in the same vessel or tank have different densities, or specific gravities, the denser liquid will sink to the bottom and the less dense liquid will float on top. The Interface is the place where these two liquids meet.
How is interface level calculated?
To figure out the transmitter’s calibrated range, you should remember the following:
- The total level should be at least as high as the upper (low pressure) tap or higher.
- Either a remote seal system or a wet leg can be used to measure this.
- The height and density (SG3) of the reference level must be constant.
- At the lower range value (LRV), 4 mA, the tank is filled with lighter fluid (SG2).
- At the upper range value (URV), 20 mA, the tank is filled with the heavier fluid (SG1).
A calibrated range of 4 to 20 mA is produced by a DP transmitter, which essentially measures the difference in pressure applied to H.P. and L.P. tap.
Figure: Interface Level Measurement using DP Transmitter with Remote Seals
- HP tapping connected to bottom of tank
- LP tapping connected to side/top with seal fluid
- Two immiscible liquids: light fluid (top), heavy fluid (bottom)
Interface Level Calculation Formula and Variables
L = Level height of the heavier liquid need to be measured
LI = Lighter liquid level need to be measured
L2 = Heavier liquid level need to be measured
x = Height distance between the DP transmitter remote sealed diaphragm flange locations (HP & LP) in tank
SG2 = Specific gravity of the heavier process liquid
SG1 = Specific gravity of the lighter process liquid
SG3= Specific gravity of the sealing liquid inside capillary of remote sealed transmitter
h1 = height between transmitter location from the minimum level of the tank
IL = Interface level
Pressure on HP side of the DP transmitter = P.HP
Pressure on the DP transmitter’s LP side = P.LP
DP = P.HP – P.LP
LRV Calculation
For the purpose of interface level calculation, the condition in which to calculate the LRV of the differential pressure (DP) transmitter occurs when the tank must be filled with lighter liquid (SG1)
P.HP = Pgas+L*SG1+h1*SG3
P.LP = Pgas+x*SG3+h1*SG3
DP = P.HP – P.LP
LRV(4mA) = (Pgas+L*SG1+h1*SG3) – (Pgas+x*SG3+h1*SG3)
LRV(4mA) = (L*SG1) – (x*SG3)
URV Calculation
For the purpose of interface level calculation, the condition in which to calculate the LRV of the differential pressure (DP) transmitter occurs when the tank must be filled with heavier liquid (SG2)
P.HP = Pgas+L*SG2+h1*SG3
P.LP = Pgas+x*SG3+h1*SG3
DP = P.HP – P.LP
URV(20mA) = (Pgas+L*SG2+h1*SG3) – (Pgas+x*SG3+h1*SG3)
URV(20mA) = (L*SG2) – (x*SG3)
Range of the transmitter = (L*SG1) – (x*SG3) to (L*SG2) – (x*SG3)
Variable – Definitions
| Symbol | Meaning |
| L | Total liquid height in the tank (mm or m) |
| SG1 | Specific Gravity of the lighter fluid |
| SG2 | Specific Gravity of the heavier fluid |
| SG3 | Specific Gravity of seal fluid (if used) |
| % Level | Percentage of interface level from 0 to 100% |
| DP | Differential Pressure (mmWC or mbar) |
Step-by-Step Example Calculation
- Total Tank Height (L): 2000 mm
- SG of Light Liquid (SG1): 0.8
- SG of Heavy Liquid (SG2): 1.2
- SG of Seal Fluid (SG3): 1.1
LRV and URV Calculation
LRV = L × SG1 = 2000 × 0.8 = 1600 mmWC
URV = L × SG2 = 2000 × 1.2 = 2400 mmWC
Assume transmitter reads 2000 mmWC
% Interface Level = ((DP – LRV) / (URV – LRV)) × 100
= ((2000 – 1600) / (2400 – 1600)) × 100 = 50%
DP calculator for interface Level measurement – calculate the level of the heavier liquid in the closed tank
The below calculator used to calculate LRV and URV of the transmitter
Practical Considerations and Best Practices
- Always calibrate with actual process SG values for accuracy.
- Ensure the entire liquid column always covers the lower tap.
- Avoid emulsions or foaming – can affect accuracy.
- Use remote seals when fluids are corrosive or tank pressure is high.
Click here for more Instrumentation Calculators