- What is a Control Loop?
- What is Loop Checking?
- Understanding Control Loop Commissioning with Practical Example Diagram
- Cold Loop Checking: Ensuring Physical Wiring & Continuity Validation
- Hot Loop Checking: Verifying Functional Integrity(Live Loop Validation with Instruments)
- Cold Loop vs Hot Loop Checking
- Follow-Up and Best Practices for Cold Loop and Hot Loop Checking
- Sign-off Requirements
- Example Pressure Transmitter Loop – Cold and Hot Loop Checking
- Cold Loop Checking (De-energized Testing)
- Hot Loop Checking (Energized Testing)
- Test Your Knowledge on Instrument Loop Diagram
Loop validation is among the most important steps before launch in any industrial automation project. It guarantees that every component of a control loop is wired properly, signals are valid, and the loop acts as intended. Typically, this procedure is split into two primary phases: Cold Loop Checking and Hot Loop Checking. Both are absolutely necessary to verify the reliability and operation of control loops prior to plant commissioning.
With regard to the process diagram displayed above, this guide describes the step-by-step procedures for cold loop and hot loop checks using the attached diagram.
What is a Control Loop?
To regulate a particular process variable (such as temperature, pressure, level, or flow) to a specified setpoint, a control loop is a system of interconnected parts. Its components are:
- Level, Pressure, Temperature Sensors/Transmitters
- Junction Boxes & Signal Cables
- Control Systems (DCS/PLC)
- Final Control Elements or Actuators (e.g., Control Valves)
- Display and control via HMI/SCADA interface
The controller gets feedback from the transmitter, compares it to the setpoint, and sends actuator orders to fix any difference.
What is Loop Checking?
Loop checking confirms that:
- The control loop is wired properly.
- Every device works as planned.
- From field to control room, signal communication is flawless.
- The system reacts appropriately to changes in input.
Loop checking is performed in two phases:
- Cold Loop Checking – Focused on wiring continuity.
- Hot Loop Checking – Focused on functional performance with power ON.
Understanding Control Loop Commissioning with Practical Example Diagram

The given above picture shows a wonderful example of the whole signal route from field to control room::
- Equipped with a Process Tank (3500 mm level) and Process Piping (3.2 BAR, 26.7°C)::
- Level Transmitter (LT) – Range: 0–8000 mm
- Pressure Transmitter (PT) – Range: 0–6 BAR
- Temperature Transmitter (TT) – Range: 10–60°C
- A 12/8/6 multi-pair signal cable from the junction box runs the signal to the Marshalling Panel.
- The marshalling panel is connected to the PLC/DCS Cabinet by ELCO Cables, which does computations and delivers outputs.
- Values are monitored using the PLC/DCS Display Unit in the control room. Data on the PLC/DCS Display Unit (PanelView Plus 700 in the diagram) shows the PID control screen.
Every one of these connections has to be cold tested for continuity and hot checked for signal integrity and process control validation.
Excel PID Loop Simulator: Excel based PID Loop Simulator
Cold Loop Checking: Ensuring Physical Wiring & Continuity Validation
Usually done without power, cold loop testing is the first part of commissioning. It verifies that every cable and signal route runs physically linked from the field instrument to the control room. Check the accuracy and continuity of wiring from field junction boxes to the control system excluding the actual field instruments.
Purpose
- Identify wiring mistakes.
- Verify proper cable termination.
- Verify continuity from transmitter to junction box, marshalling panel, and DCS/PLC.
Tools Used
- Digital Multimeter (DMM)
- Insulation Resistance Tester (if required)
Safety Precautions
- Always ensure circuits are de-energized.
- Use insulated tools to avoid accidental shorts.
- Follow lockout-tagout (LOTO) procedures where applicable.
- Verify isolation from other live circuits
- Use proper electrical safety PPE
Activities Involved
Cable Continuity Testing
- Verifying cable resistance with multimeters.
- Checking from transmitters (e.g., Pressure, Level, Temperature) to the Field AI Junction Box.
- Check that every multi-pair cable core is correctly terminated between the Field Junction Box and Marshalling Panel.
- Measure continuity (end-to-end resistance close to zero) using a multimeter.
- Verify grounding and cable shield continuity.
Check Loop Current Safely: How to Safely Check the mA Current of an Instrument Loop Using a Multimeter
Check Polarity and Terminal Identification
- Verify that signal lines are correctly designated and terminated according to wiring designs.
- Check polarity; this is particularly crucial for loop-powered devices.
Terminations
- Check suitable connections in system cabinets, marshalling panels, and junction boxes.
- The diagram illustrates how the level transmitter (LT) signal flows to the Field AI Junction Box via branch cable, then to the marshalling panel via multi-core signal cable, finally reaching the PLC/DCS cabinet.
- Make that ELCO connectors or terminal blocks are properly linked to analog input (AI) modules in the PLC/DCS cabinet.
Cable Label Verification
- This minimizes troubleshooting time and helps prevent erroneous terminations.
Instrument Loop Diagram Guide: Instrument Loop Diagrams
Simulate 4–20 mA Signal (Optional):
- Sometimes, a dummy transmitter or resistance box is linked to mimic field wiring. To check response at the DCS, replicate 4–20 mA signals using a loop calibrator at the marshalling panel.
- Check the proper signal scale and display in the DCS HMI or SCADA.
Simulate 4-20mA Signal: How to simulate 4-20ma signal with Loop Calibrator ?
Documentation
- Log continuity test findings in loop check sheets.
- For every loop, mark as “Cold Loop Completed.”
- Change as-built drawings if any modifications took place.
Hot Loop Checking: Verifying Functional Integrity(Live Loop Validation with Instruments)
Hot Loop Checking starts when the cold loop is confirmed. This stage verifies the loop’s operation using live power, hence guaranteeing that the system receives and responds to signals accurately. Verify that the loop end-to-end (sensor to control system) is operational and that actual field transmitters are functioning correctly.
Purpose
- Verify that the real 4-20 mA signal is being sent accurately.
- Check system logic and display (HMI/SCADA).
- Make sure the interaction between setpoint and feedback functions.
Tools Used
- HART Communicator or Loop Calibrator
- Handheld Multimeter (for quick diagnostics)
- Portable Pressure/Temperature Sources like Calibrators(if needed)
Safety Precautions
- AWear always PPE (Personal Protective Equipment).
- Watch out for powered machinery or moving actuators.
- Tell operations first before modeling process values.
- When simulating values, be mindful of any process effects.
- For live testing, follow plant safety procedures.
Activities Involved
Power Up the System
- Activate the loop to start real signal flow.
- Transmitters begin sending real process values (PV), such the Pressure Transmitter in the picture, which sends 3.2 BAR.
Verify Live Signals
- At the transmitter, use a clamp-on milliammeter or series multimeter to measure loop current (4–20 mA).
- Verify that the PLC/DCS and display device show the 4-20 mA signal from each transmitter accurately.
- For example, the Level Transmitter on the tank should indicate a live reading in mm on the HMI (in the attached image, the process level is around 3500 mm).
Check Controller Response
- Establish a process setpoint (SP) in the PID controller and watch the feedback.
- For instance, the Temperature Transmitter shows 26.7°C. The system should evaluate this against the SP and modify actuators appropriately.
Functional Loop Test
- Alter process conditions or simulate them with a HART communicator or signal source.
- Verify that the process reacts correctly and that controller output varies.
- Simulate various process values using a HART communicator; for example, set LT to 50% = 12 mA.
- Alternatively, apply physical changes (e.g., introduce pressure to PT or temperature simulation with RTG or TC signal to TT) to produce varying outputs.
Verify Signal at Control System
- Look at the PLC/DCS Display Unit in the control room to see the relevant input signal.
- Make that the shown value matches the transmitter output (e.g., 50% level = 3500 mm).
Test Calibration Scaling
- Verify that the HMI and analog input module are correctly scaled (e.g., 4 mA = 0 mm, 20 mA = 8000 mm for LT).
- If necessary, change range parameters using HART.
Check Alarms & Logic:
- Use simulated values to test interlocks and alarm thresholds set up in the control system.
- Check that control operations, such valve actuation or shutdowns, are properly triggered.
Documentation
- Document observed PV and SP values.
- Observe control response times and contrast with design expectations.
- Once confirmed, tag loop as “Hot Loop Completed”.
Cold Loop vs Hot Loop Checking
Aspect | Cold Loop Checking | Hot Loop Checking |
Power Status | OFF | ON |
Purpose | Verifies wiring and continuity | Verifies function and system behavior |
Signal Type | Simulated or continuity checks | Real 4-20 mA or digital input/output |
Focus Area | Cable paths and terminations | Transmitter output, control logic, system response |
Testing Tools | Multimeter, insulation tester | Calibrator, HART communicator, DCS/PLC software |
Safety Requirement | Basic electrical safety | Full PPE and awareness of live systems |
Documentation | Continuity test results | System response logs, operator interface feedback |
Follow-Up and Best Practices for Cold Loop and Hot Loop Checking
- Keep a loop folder containing recordings of cold and hot loop checks.
- Track maintenance and future troubleshooting using loop folders.
- Make sure control room and field staff members coordinate during loop tests.
- For safe execution, use intercom systems or radios.
- Correct tagging helps to lower the likelihood of wire mix-up.
- Always cross-check with current P&IDs and loop diagrams.
- Revise redlines as required.
- Begin from upstream (sensor side) and progress toward control room.
- Give important loops like pressure safety controls top priority.
- To prevent chasing wire faults during live testing, always do cold loop checks before hot loop checks.
- Clearly label wires and change loop designs to reflect as-built circumstances.
- Keep a Loop Check Log Sheet for every loop detailing tests conducted, tools employed, and outcomes.
- To confirm linearity, test at several setpoints 0%, 25%, 50%, 75%, 100% for important instruments.
Sign-off Requirements
- Instrumentation technician
- Control systems engineer
- QA/QC representative
- Operations representative (for hot loop checks)
Example Pressure Transmitter Loop – Cold and Hot Loop Checking

The step-by-step approach for performing both cold loop and hot loop inspections on the pressure transmitter loop (HTF-PT-7010A/B) seen in the above diagram is described in this technique. The loop comprises a field pressure transmitter, junction box connections, multi-cable routing, marshalling cabinet, PLC analog input module, and DCS display setup.
Cold Loop Checking (De-energized Testing)
Pressure Transmitter Field Verification
Checking Point: Pressure transmitter (HTF-PT-7010A/B)
Activities:
- Check transmitter tag number against records (HTF-PT-7010A/B)
- Verify calibration range (0-3 kg/cm²G as indicated in the diagram)
- Inspect cable links at transmitter terminals (+, -)
- Check instrument cable specs (1P x 1.5mm²)
- Verify that the transmitter is correctly aligned and attached.
Field Junction Box Verification
Checking Point: Junction Box HTF-JB-AP-702A/B
Activities:
- Confirm JB tag number corresponds with records.
- Inspect TB-01 terminal block connections
- Verify signal polarity (+ to +, – to -)
- Check shield ground connection at “S” terminal
- For shorts/opens, measure resistance between terminals
- Examine mechanical integrity and terminal tightness
Multi-Cable Path Verification
Checking Point: Multi-cable HTF-MC-AP-702A/B
Activities:
- Check cable tag and specs (12P x 0.5mm²)
- Verify cable tray routing for cables.
- Verify cable shield continuity
- Make sure there is appropriate strain relief at both ends.
Marshalling Cabinet Connections
Checking Point: Terminal board TB52
Activities:
- Check terminal numbers (3641, 3642)
- Verify wire termination and labeling
- Check polarity across marshalling panel (+/-).
- Check shield termination at “S” terminal
- Check continuity from field JB to marshalling cabinet
PLC Analog Input Module Connections
Checking Point: PLC Module HCU2
Activities:
- Check module type (AI)
- Verify channel numbers (Ch11+, Ch11-)
- Inspect ELCO cable links to terminals 343 and 344
- Check PLC rack and slot numbers (I/O Z-1, PRI.SLOT 7)
- Verify channel setup (Channel 10)
DCS Configuration Verification
Checking Point: DCS tag HTF-PT-7010A4/B
Activities:
- Check engineering unit configuration (kg/cm²G)
- Verify scale range (L: 0, H: 3)
- Review alarm limit configurations (if relevant)
- Examine control system tag handling
Pressure Transmitter Loop Check: Method Statement for Loop Checking of Pressure Transmitter Loop
Hot Loop Checking (Energized Testing)
Pressure Transmitter Functionality
Checking Point: Pressure transmitter HTF-PT-7010A/B
Activities:
- Power up the transmitter
- Connect HART communicator to check transmitter setup.
- Check transmitter zero (4mA at 0 kg/cm²G)
- Measure voltage of power supply at transmitter terminals
- At transmitter terminals, measure live 4-20mA signal
- Use a calibrator to simulate pressure.
Troubleshoot 4-20mA Loop: How to do troubleshooting of a 4-20mA loop?
Junction Box Signal Verification
Checking Point: Junction Box HTF-JB-AP-702A/B
Activities:
- At terminal block TB-01, measure loop current.
- Check transmitter to JB signal continuity.
- Ensure signal readings correspond to anticipated process values
- Test signal over several simulated pressure levels: 0%, 25%, 50%, 75%, and 100%.
Marshalling Cabinet Signal Testing
Checking Point: Terminal board TB52
Activities:
- At terminals 3641, 3642, measure loop current.
- Check that the signal value corresponds to field transmitter output.
- Verify signal quality over the multi-cable route.
- Look for signal loss or noise.
PLC Analog Input Verification
Checking Point: PLC Module HCU2
Activities:
- Check analog input reading in PLC diagnostic tool
- Validate signal scaling (4mA = 0 kg/cm²G, 20mA = 3 kg/cm²G)
- Verify A/D conversion accuracy
- Check engineering unit conversion
DCS Display and Logic Verification
Checking Point: DCS interface
Activities:
- Check HMI/SCADA screen pressure value display
- Verify engineering units are right (kg/cm²G)
- Simulate high/low pressure situations to test alarm operation.
- Check that control logic reacts properly to pressure fluctuations.
- Check every interlock condition pertaining to this pressure transmitter.
Successful commissioning in automation projects is based on cold loop and hot loop checks. Skipping or hurrying through these inspections could cause significant starting delays or process risks. Dedicated execution guarantees that:
- Wiring is accurate and complete.
- Process instruments communicate reliably.
- Controllers and operators can trust what they see.
Test Your Knowledge on Instrument Loop Diagram
Refer the below link to test your understanding in Instrument Loop Diagrams(ILD)