Step-by-Step Guide for Troubleshooting Radar Level Transmitters

The advanced technology of radar level gauges provides accurate level measurement for industrial liquids and solid materials. Radar devices send microwave signals through a process that allows them to determine surface-to-transmitter distances for material measurements. These devices serve as the industry choice because their exact measurement capabilities provide benefits beyond hydrostatic and capacitive and ultrasonic methods.

Radar level transmitters provide reliable and accurate measurements but operational difficulties might arise when used under high temperature and pressure conditions or in corrosive environments and when foam forms or when the process includes turbulence and steam interference. These environmental factors result in system breakdowns which require more extensive maintenance along with production disruptions.

The identification and timely resolution of routine faults remains key to achieving maximum performance operation. 

The following sections describe common problems radar level gauges face with accompanying troubleshooting recommendations to decrease measurement downtime and keep accuracy.

SymptomPossible CauseAction
Radar level gauge shows very slow changes or no change at all after liquid level risesEquipment’s fuse may have burned outCheck if the fuse is burned out and replace it if necessary
No current output from the radar level gaugePower supply issue or instrument malfunctionVerify power supply, check fuse condition, and replace or repair instrument if needed
Slow or no change in liquid level measurementIncorrect power supply connection, polarity reversal, or instrument setup issueEnsure proper power supply connection, verify polarity of wire connections, and check instrument parameter settings
Inconsistent readings or operational failuresLack of proper maintenance and managementStrengthen installation and commissioning management, conduct regular maintenance and power cycle checks
Instrument fails to respond after power-onPossible internal fault or incorrect installationInspect the device, confirm correct setup, check polarity of wire connections, and perform necessary repairs or replacements
No power to the level transmitterNo supply voltage, blown fuse in marshalling cabinetCheck supply voltage at terminal; if no voltage, inspect and replace faulty fuse.
No power despite a healthy fuseFaulty barrier/isolatorInspect the barrier/isolator for damage and replace it whenever it is faulty.
Transmitter still does not power onFaulty transmitter power cardThe transmitter power card requires replacement when voltage exists but there is no power output.
SymptomPossible CauseAction
Radar level gauge malfunctions in high-temperature environmentsInternal temperature exceeds 50°CThe system must maintain inner temperatures below 50°C by implementing heat-resistant components.
The radar level gauge fails to operate because the temperature increased.Inadequate cooling method appliedThe radar gauge head requires cool air delivery through a copper tube instead of ice water application.
Erratic readings or system failureElectronic components overheatingPeriodic temperature checks must be followed by appropriate cooling protocols.
Radar level gauges demonstrate failures during operations at elevated temperatures.Inappropriate transmitter selectionChoose a new transmitter that shows compatibility with high-temperature environments based on the supplier-provided specifications.

Must-Read: What is a guided wave radar level transmitter?

Step-by-Step Guide to Troubleshooting Radar Level Transmitters 1
SymptomPossible CauseAction
Communication failure with radar level gaugeFaulty communication unitRun the radar debugging software to verify the proper status of configuration data.
Incorrect or missing signal transmissionRadar sensor misinterpreting echoesThe sensor requires proper configuration to properly differentiate between original reflections and false echoes.
Weak or no signal receptionLow reflected wave intensityVerify the reflected wave intensity matches the established standard requirements.
Persistent communication errorsFaulty electronic componentsPerform inspections on damaged communication components followed by replacements when necessary.
Unstable connectionPoor maintenance of communication equipmentThe radar debugging software enables access to signal lines as well as proper regulator maintenance.

Explained: Level measurement using Radar technique

SymptomPossible CauseAction
Displayed value is incorrectImproper initial settings or incorrect connectionsReview and fix both initial settings procedures and display module wiring connections.
Display is unreadableThe initial settings for contrast ratio function improperly.Users should adjust display contrast settings to make the screen more visible.
Incorrect display despite correct settingsFaulty display moduleTest the display output current and replace the display module when the current reading exceeds 22mA.
Output current less than 3.5mAFaulty electronic moduleThe replacement of the radar level gauge’s electronic module is necessary.
Fluctuating or unstable readingsExternal interference or sensor calibration issueTake the necessary steps to protect the sensor from external interference then perform a calibration check if needed.

Essential Guide: What is a radar level transmitter and how can it be used to do the level measurement?

Step-by-Step Guide to Troubleshooting Radar Level Transmitters 3
SymptomsCausesActions
Measured value fluctuates significantlyMeasurements fluctuate greatly when stirrers create surface turbulence.The system requires improved application parameters that can eliminate rapid changes in measurements.
Temporary interference in readingsAn interfering echo effect occurs when the sensor picks up signals from the feeding process.Enabled usage of near-field suppression prevents the reception of unnecessary signals.
Unstable level measurementInsufficient signal due to improper installationVerify that the installation position is suitable and optimal
Weak or unstable signal receptionA small antenna leads to inadequate signal reception.The installation of a larger antenna will lead to improved signal reception strength.
Measurement variations despite stable processLow output damping settingsRaising output damping levels will help reduce measurement variations.
Step-by-Step Guide to Troubleshooting Radar Level Transmitters 5
SymptomsPossible CausesRecommended Actions
System displays an error messageThe interruption of power supply occurred before the system finished saving data points.Thoroughly check power stability while making sure there are no interruptions during power supply.
Frequent error messages appearThe system shows errors because it needs calibration or the parameters are incorrect.Begin by resetting the system then calibrate it and check all application parameters.
Alarm persists after resetFaulty or damaged electronic moduleInstall a new electronic module inside the radar level gauge system.
Inconsistent error messagesExternal interference or wiring issuesVerify that all electrical connections are secure while checking for electromagnetic interference.
SymptomsPossible CausesRecommended Actions
The liquid measurement shows an empty or low level.Reflection occurs from brackets or pipes installed at the container bottom.Check and readjust the installation process to reduce interference.
Liquid level measurement failureRadar waves experience diffusion because of steam formation within the measured system.Allow steam to vaporize until the system reaches normal temperature.
Unstable or fluctuating readingsRadar waves change direction after reflecting from rough surfaces and blockage obstaclesMaintain a clear measurement path through proper adjustment of mounting position.
Measurement does not recover immediatelySystem error due to previous reflectionsWait for the liquid level to stabilize then start the system to allow automatic recovery functions
Step-by-Step Guide to Troubleshooting Radar Level Transmitters 6
SymptomsPossible CausesRecommended Actions
Measurement failure or inaccuracyAntenna contamination due to oil or residueUsers should first switch off power before they slowly remove the radar and wipe down the antenna with a cleaning rag.
Weak or unstable signalCrystallization on the antennaUse a downward tilt position to remove crystals by lightly wiping the antenna surface with a soft cloth.
Persistent measurement errorsDamage or scratches found on the antenna surfacePay attention to antenna handling while you should not use metal tools during cleaning procedures.
Antenna performance degradationAccumulated dirt affecting signal transmissionThe system requires periodic maintenance together with inspections to stop accumulation from forming.
SymptomsPossible CausesRecommended Actions
A “Wave Loss” error may occur together with system crashes.Low dielectric constant liquid with weak reflectionSet applications to optimal values by analyzing vessel process characteristics.
Weak or no return waveA combination of vortex motion turbulence with thick foam material results in wave diffusion and absorption.Users should modify measurement parameters while possibly switching antenna placement or dimensions.
Frequent wave lossPoor signal due to installation positionThe antenna should be moved to a different position or a larger antenna must be used to enhance signal return quality.
The signal continuously disappears in difficult environmental conditions.The usage of extreme process conditions such as scarring slurry creates problems.Those conditions suitable for waveguides or bypass tubes may implement their use.
Inconsistent readingsExternal interference or improper installationChoose the best positions during installation while ensuring the removal of all possible interference elements.
Step-by-Step Guide to Troubleshooting Radar Level Transmitters 7
SymptomsPossible CausesRecommended Actions
The level sensor maintains steady reading either at 0% or 100% status.Sensor error or power issueExecute a power reboot procedure on the transmitter device.
After a transmitter reboot value remains either at 0% or 100% value.Moisture, vapor, or dirt on sensorUse a soft cloth to clean the sensor before inspecting physical wear and tear.
Inconsistent or stuck readingsThe sensor path encounters blockages stemming from spider webs and rust or bulging structure elements.Check the wave path along with the sensor cone and the flange to ensure cleanliness.

Must-Have: 15+ Collection of Level Measurement Calculators for Industrial Instrumentation

Step-by-Step Guide to Troubleshooting Radar Level Transmitters 8
SymptomsPossible CausesRecommended Actions
There is a difference in value measurements between the field equipment and the PLC/DCS systemConfiguration mismatchCheck all transmitter ranges by comparing them to the Level Coordination Diagram (LCD) and approved design documentation.
Fluctuating readings or operational failuresExcessive turbulence or air bubblesRelocate the level transmitter to a more stable position if possible.
Rapid fluctuations in level valuesLow damping valueIncrease the damping (time constant) by a few seconds for better signal stability.
SymptomsPossible CausesRecommended Actions
Guided wave radar not respondingValves should be opened for extended pipe connections.Check and open the valves to validate their functionality.
The radar system remains unresponsive despite checking all valves.Contaminated probeAfter cleaning the probe tip you should reinstall the transmitter.
Probe contamination persistsMaterial buildup on probeThe probe must undergo complete cleaning before reinstalling to its original spot.
Transmitter stuck at a fixed level readingSevere probe contaminationCombine either hydro jetting or steam jetting to clean away accumulated material from the equipment.
ScenarioAction
The issue remains unresolved after all previous steps failCheck the transmitter’s circuit cards for internal failures then replace them if needed.
If intermittent failures persistRead the OEM (Original Equipment Manufacturer) manual according to the instructions provided for additional troubleshooting assistance.
The transmitter’s operation remains nonfunctional.Contact an experienced field instrumentation expert or a member of the manufacturer support team for help.