4 to 20 mA Transmitter Output Process Value Calculator

A 4 to 20 mA transmitter is widely used in industrial applications to transmit analog signals over long distances with high accuracy and minimal noise interference. The 4 to 20 mA current loop is robust against electrical noise and can transmit signals reliably over long distances, making it ideal for use in process control and instrumentation systems.

In a 4 to 20 mA current loop:

4 to 20 mA Transmitter Output Process Value Calculator 1
  • 4 mA represents the minimum value of the measured process variable (e.g., temperature, pressure, level).
  • 20 mA represents the maximum value of the measured process variable.

The below Calculator used to calculate the Process Value (PV) corresponding to a transmitter measured mA output signal.

To calculate the process variable (PV) from the measured current (I) in mA, we use the following linear interpolation formula:

Formula for 4 to 20 mA Transmitter Output Calculation 2

Where:

  • PVmin​(LRV) is the minimum process variable value.
  • PVmax(URV)​ is the maximum process variable value.
  • I is the measured current in mA.

This formula converts the measured current signal back into the corresponding process variable.

Click here for Why not use 0-20mA & 0-15psi instead of 4-20mA & 3-15psi?

Consider a temperature transmitter that uses a 4 to 20 mA current loop to transmit temperature readings. The temperature range that the sensor can measure is from -50°C to 50°C. If the sensor outputs a current of 10 mA, what is the corresponding temperature?

To find the corresponding temperature for a 10 mA signal, follow these steps:

  • PVmin(LRV)​: This is the lowest value the process variable can take. In this example, it is -50°C.
  • PVmax(URV): This is the highest value the process variable can take. In this example, it is 50°C.
  • I: This is the current measured in the loop, which is 10 mA in this scenario.

Apply the values in the formula.

Formula for 4 to 20 mA Transmitter Output Calculation 3

So, the process temperature corresponding to a 10 mA signal is -12.5°C.

This technique allows you to find the value of the process variable for any current in the 4–20 mA range. Any kind of sensor or transmitter operating in this range can use this method, which ensures reliable signal interpretation.

Click here for Calculator for 4-20mA Signal to 1- 5 Volt and PLC 16-bit Raw Count Values

Click here for more instrumentation Calculator

Sundareswaran Iyalunaidu

With over 24 years of dedicated experience, I am a seasoned professional specializing in the commissioning, maintenance, and installation of Electrical, Instrumentation and Control systems. My expertise extends across a spectrum of industries, including Power stations, Oil and Gas, Aluminium, Utilities, Steel and Continuous process industries. Tweet me @sundareshinfohe

Related Articles

Back to top button

Adblock Detected

We Noticed You're Using an Ad Blocker Hi there! We understand that ads can be annoying, but they help support our website and allow us to continue providing you with high-quality content. Please consider whitelisting our site or disabling your ad blocker while you visit. Your support means a lot to us! Thank you for understanding!