Here we look at, how functional test is done for solenoid valve using instrument air.

Solenoid Valve Testing:

  • Air supply is connected to the Air Filter Regulator (AFR).
  • Set the stress required in the AFR and link the AFR outlet to the Solenoid valve.
  • Connect outlet of Solenoid Valve to a Ball valve.
  • Connect a pressure gauge at the Solenoid Valve outlet.
  • The aim of Test Gauge is to verify the inlet line stress depends on SOV energy.
  • Ball valve used to stop the functional testing

Typical Solenoid valve Test Set-up:

  • Check the nameplate for the manufacturer/instrument datasheet. Confirm the voltage / current scores of the solenoid valve (consider + 24V DC device in our instance)
  • Check the solenoid valve port configuration.
  • Hook-up tool according to the typical sample configuration.
  • Apply air-specified valve port stress and link 24VDC to valve terminals with solenoid.
  • Switch on the 24VDC energy supply, inspect the energy valve by controlling the stress of the sample gage (increasing pressure).
  • Turn off the supply. Confirm the de energized valve, inspect the value of the sample gage again (Diminishing stress)
  • Tabulate all result in Check Sheet.

Sivaranjith

Instrumentation Engineer

Related Articles

Back to top button

Adblock Detected

We Noticed You're Using an Ad Blocker Hi there! We understand that ads can be annoying, but they help support our website and allow us to continue providing you with high-quality content. Please consider whitelisting our site or disabling your ad blocker while you visit. Your support means a lot to us! Thank you for understanding!