Bubbler method Liquid Density measurement Calculations with Constant Tank Level and Single Bubble Tube

In this section, examples of typical calculations for determining the liquid Density measurement Calculations with Constant Tank Level and single Bubble Tube Installation are given.

It is important to keep in mind that the upper-range values (URV) and lower-range values (LRV) relate to the highest and minimum measurements that are intended, respectively. The Calibrated Span is equal to the URV minus the LRV. The output at LRV greater than 0% represents the value of the suppression.

Abbreviations

The following acronyms are utilized in this directive.

LRV = Lower-range value (a measurement that’s output is 4 mA).

URV = Upper-range value (a measurement with a 20 mA output).

SG = A liquid’s specific gravity (relative density). Water has a specific gravity of 1.00 in both traditional and SI systems.

HW= Equivalent Headlevel pressure of Water

Formulas for Converting Specific Gravity for All Liquids

Specific gravity = Density [lb/ft3 ] / 62.4

Specific gravity = Density [kg/m3] / 1.00

Bubbler method Liquid Density measurement Calculations with Constant Tank Level and Single Bubble Tube

H1 = Height of the bubble tube immersed inside the process liquid

SGL = Specific gravity of the liquid – need to be evaluated

SG1 = Minimum Specific gravity of the liquid

SG2 = Maximum Specific gravity of the liquid

H = Constant level of the tank (Head between LRV and URV)

Calibrated Range of the transmitter = LRV to URV 

Where:

HW = Equivalent Head level pressure of Water 

Span value of the transmitter = (H)*(SG2 – SG1)

Equivalent Head level pressure of Water (HW) at Lower range value

HW at LRV =(H*SG1) = Suppression

Equivalent Head level pressure of Water (HW) at Upper range value

HW at URV = (H*SG2)

Example calculation -Density Calculations with Constant Tank Level and single Bubble Tube

The DP transmitter is mounted in an open tank with single bubble tube and also has the following specifications to determine density of the process liquid.

Process liquid Specific gravity varies between 1.0 and 1.8

 Constant level of the tank is 

H= 60 inches (Head between LRV and URV)

Find the calibration range of the transmitter for measuring the density?

So, SG1 = 1.0

SG2= 1.8

Span value calculation

Span = (H)*(SG2 – SG1)

Span = (60)*(1.8 – 1.0) 

Span = (60)*(0.8) 

Span value of the transmitter = 48 inchH2O 

LRV calculation (4mA)

HW at LRV = (H*SG1) 

HW at LRV = (60 *1.0) 

HW at LRV= 60 inchH2O = Suppression 

URV calculation (20mA)

HW at URV = (H*SG2)

Hw at URV = 60 * (1.8) 

HW at URV = 108 inchH2O 

Calibration range of the transmitter = 60 to 108 inch of H2O

Sundareswaran Iyalunaidu

With over 24 years of dedicated experience, I am a seasoned professional specializing in the commissioning, maintenance, and installation of Electrical, Instrumentation and Control systems. My expertise extends across a spectrum of industries, including Power stations, Oil and Gas, Aluminium, Utilities, Steel and Continuous process industries. Tweet me @sundareshinfohe

Related Articles

Back to top button

Adblock Detected

We Noticed You're Using an Ad Blocker Hi there! We understand that ads can be annoying, but they help support our website and allow us to continue providing you with high-quality content. Please consider whitelisting our site or disabling your ad blocker while you visit. Your support means a lot to us! Thank you for understanding!