Bubble method Interface level measurement calculation with Constant Tank Level and single Bubble Tube

Published on

spot_img

Bubbler method measurement calculation

In this section, examples of typical calculations for determining the liquid interface level in an open tank with constant level and single Bubble tube transmitter Installation are given.

It is important to keep in mind that the upper-range values (URV) and lower-range values (LRV) relate to the highest and minimum measurements that are intended, respectively. The Calibrated Span is equal to the URV minus the LRV. The output at LRV greater than 0% represents the value of the suppression.

Abbreviations

The following acronyms are utilized in this directive.

LRV = Lower-range value (a measurement that’s output is 4 mA).

URV = Upper-range value (a measurement with a 20 mA output).

SG = A liquid’s specific gravity (relative density). Water has a specific gravity of 1.00 in both traditional and SI systems.

HW= Equivalent Headlevel pressure of Water

Formulas for Converting Specific Gravity for All Liquids

Specific gravity = Density [lb/ft3 ] / 62.4

Specific gravity = Density [kg/m3] / 1.00

Interface level measurement Calculations with Constant Tank Level and single Bubble Tube

Bubble method Interface level measurement calculation with Constant Tank Level and single Bubble Tube

SG1 = Specific gravity of upper liquid (lighter liquid)

SG2 = Specific gravity of lower Liquid (Heavier liquid)

H = Height of the bubble tube immersed inside the process liquid

H1 = Interface level need to be measured.(head between LRV and URV)

H2 = Head level below minimum interface level

Calibrated Range of the transmitter = LRV to URV 

Where:

HW = Equivalent Head level pressure of Water 

Span value of the transmitter = (H1)*(SG2 – SG1)

Equivalent Head level pressure of Water (HW) at Lower range value

HW at LRV = (H1*SG1) + (H2*SG2) = Suppression

Equivalent Head level pressure of Water (HW) at Upper range value

HW at URV = (H1 +H2)*SG2

Example calculation – Interface level measurement Calculations With Constant Tank Level and single Bubble Tube

The transmitter is mounted in an open tank with the following specifications to measure interface level.

Process liquid Specific gravity varies between 0.9 and 1.8

Height of the interface level measured between LRV and URV is 

H1= 70 inches 

Head level distance below minimum level(LRV) (suppression)

H2 = 10 inches 

Find the calibration range of the transmitter to measure the interface level?

So, SG1 = 0.9

SG2= 1.8

Span value calculation

Span = (H1)*(SG2 – SG1)

Span = (70)*(1.8 – 0.9) 

Span = (70)*(0.9)

Span value of the transmitter = 63 inchH2O

LRV calculation (4mA)

HW at LRV =(H1*SG1) + (H2*SG2)

HW at LRV = (70 * 0.9) + (10 * 1.8) 

HW at LRV = 63 + 18

Hw at LRV= 81 inch H2O = Suppression 

URV calculation (20mA)

HW at URV = (H1 +H2)*SG2

Hw at URV = (70 + 10) * (1.8) 

Hw at URV =80 * (1.8) 

Hw at URV = 144 inch H2O 

Calibration Range of the transmitter = 81 to 144 inch H2O

Latest articles

How to Safeguard PLCs Against Cyber Attacks in Industrial Networks ?

Table of ContentsUnderstanding Programmable Logic Controllers (PLCs)What are PLCs in cyber security?Importance of PLC...

Equal Percentage Control Valve Flow Calculator

Definition: Equal Percentage Control ValveThe fundamental characteristic of an equal percentage control valve creates...

Wet Leg & Dry Leg DP Measurement Quiz: Top 25 Advanced MCQs

We welcome you to our Knowledge Assessment Quiz about Advanced Dry Leg and Wet...

How to Optimize PLC Scan Time for Better Automation ?

Table of ContentsDefinition of Scan TimeFactors Affecting Scan TimeHow to Measure and Optimize Scan...

More like this

How to Safeguard PLCs Against Cyber Attacks in Industrial Networks ?

Table of ContentsUnderstanding Programmable Logic Controllers (PLCs)What are PLCs in cyber security?Importance of PLC...

Equal Percentage Control Valve Flow Calculator

Definition: Equal Percentage Control ValveThe fundamental characteristic of an equal percentage control valve creates...

Wet Leg & Dry Leg DP Measurement Quiz: Top 25 Advanced MCQs

We welcome you to our Knowledge Assessment Quiz about Advanced Dry Leg and Wet...