- What is Calibration?
- What is Re-ranging?
- Calibration vs. Re-ranging: Key Differences
- Practical Understanding Through a Field Scenario for Industrial Automation Technicians
- Relationship Between Calibration and Re-ranging in Analog vs. Digital Instruments
- When to Choose Calibration vs. Re-ranging
- Importance of Understanding the Difference
- What is the difference between calibration and recalibration?
- What is the difference between calibration range and instrument range?
- What is the difference between calibration and validation?
- What is the difference between calibration and repair?
- What is the difference between zeroing and spanning?
- What is called calibration?
- How to calculate calibration range?
In process control and industrial automation systems, it’s very important to make sure that measurements are correct and that control actions are always the same. To get accurate and useful data from instrumentation instruments, they need to be set up and cared for properly. This is especially true for analog and digital transmitters. Calibration and re-ranging are two words that come up a lot in this context. Both entail setting up equipment, but they have different goals and use different methods to do so. Understanding the distinction is essential for instrumentation professionals involved in commissioning, preventive maintenance, performance audits, troubleshooting, or preparing systems for regulatory inspection.
What is Calibration?
In real life, calibration means employing precise sources to give the instrument known reference inputs, including pressure, temperature, flow, or voltage. We write down the output answer and compare it to what we expected. If there are differences (such measurement errors), internal zero and span modifications are made to make the output match the real numbers.
Example
Let’s say you’re calibrating a pressure transmitter that can read between 0 and 100 PSI. You use a certified pressure calibrator to apply pressures at different times, such as 0, 25, 50, 75, and 100 PSI. If the output for 40 PSI is 12 mA instead of the required 10.4 mA, the transmitter needs to be calibrated to fix the problem. This calibration makes sure that the transmitter accurately shows how things are really going on in the process and that the 4-20 mA signal stays dependable for PLC or DCS systems downstream.
Key Points about Calibration
- Includes checking the numbers with real, known input values.
- Fixes zero, span, and sometimes linearity or non-linearity errors.
- Makes ensuring that things can be traced back to national and international standards.
- Done during commissioning, regular maintenance, or after repairs or failures.
- Confirms that the instrument works correctly over its whole range of use.
- Needs documentation for reviews, especially in places where regulations are strict.
Refer the below link for the Basic Safety and General Consideration While Executing Calibration Process in process industries
What is Re-ranging?
Re-ranging is the process of changing an instrument’s measuring range such that it sends out a signal (usually 4-20 mA) that is proportional to a new set of input values. Re-ranging does not check or fix the instrument’s accuracy, unlike calibration. This is a configuration activity that makes sure the instrument’s output scale is in line with the new process circumstances.
When process parameters change or when an instrument is given a new job to monitor a different area of the process with a different operating range, it is usually time to re-range. This adjustment helps make the resolution better and keeps the output signal from getting too strong.
Example
For example, a differential pressure transmitter that was originally set to 0–200 PSI. You can change the transmitter’s range to output 4 mA at 0 PSI and 20 mA at 150 PSI if the process operates between 0 and 150 PSI later. This change makes the resolution and signal sensitivity better in the updated process window, but it doesn’t change the calibration itself. Re-ranging is quite helpful when you want to match the signal resolution with the expected usual operating zone to get better loop tuning and more accurate trends.
Field communicators (like HART), configuration software, or a DCS/PLC interface are typically used to re-range modern digital smart transmitters. Typically, this process doesn’t require physically adding process inputs, therefore it can be done quickly in the field or from a distance.
Key Points about Re-ranging
- It changes the range of the measurement, but not the accuracy or the sensor’s properties.
- Done when the conditions of the process or the needs of the application change.
- If the transmitter stays accurate, it doesn’t need to be recalibrated.
- Usually done with HART communicators, DCS configuration tools, or PLC interfaces.
- Helps get the best measurement resolution for the spectrum of expected use.
- If done within the device’s specifications, it can be done again without affecting the accuracy of the sensor.
Refer the below link for the DP Flow Transmitter Re-Ranging Calculator
https://automationforum.co/dp-flow-transmitter-re-ranging-calculator/
Calibration vs. Re-ranging: Key Differences
Aspect | Calibration | Re-ranging |
Definition | Verification and adjustment to ensure accuracy against known standards | Adjustment of input range corresponding to 4-20 mA output |
Purpose | Ensure the instrument gives accurate readings across its entire range | Change the measurement span to suit process needs |
Input Requirement | Requires known, traceable input stimuli | May not require applying physical inputs |
Affects Accuracy? | Yes, improves or confirms accuracy | No, unless the transmitter was already inaccurate |
Tools Required | Calibrated reference devices (e.g., pressure, temperature, electrical sources) | Configuration tools (e.g., HART communicator, DCS/PLC software) |
Common Scenarios | Commissioning, audits, post-repair checks, annual QA | Process redesign, range optimization, changing service conditions |
Applies To | Both analog and digital instruments | Mostly digital or smart instruments |
Regulatory Requirement | Often mandated by quality or safety standards | Usually an internal engineering decision |
Practical Understanding Through a Field Scenario for Industrial Automation Technicians
Let’s say we have a flow transmitter on a natural gas line. At first, the process runs at a speed of 0 to 100 m³/h. The transmitter has been set up and the range has been adjusted.
Situation 1: Re-ranging Needed
The operating flow goes up to 150 m³/h after the pipeline is upgraded. The technician changes the range of the transmitter so that 4 mA = 0 m³/h and 20 mA = 150 m³/h. This re-ranging enhances resolution without needing to be recalibrated because calibration stays the same.
Situation 2: Calibration Needed
During a routine check, the transmitter sends out 12.5 mA when the flow is 75 m³/h (it should be 12 mA). This difference shows that there is a defect or drift in the calibration. You need to do a full recalibration with a flow calibrator or simulator.
This difference helps save people from making mistakes whether they are doing maintenance or trying to figure out if an instrument’s behavior is due to drift or just an incorrect range setup.
Calibration Guidelines Every Engineer Should Follow: Calibration Guidelines
Relationship Between Calibration and Re-ranging in Analog vs. Digital Instruments
In Analog Instruments:
In Digital Instruments:
These instruments isolate the calibration of the sensor from the scaling of the output. Users can change the output mapping (for example, scale 4-20 mA to a new span) without affecting factory calibration. This modular method divides down on the need for field recalibration until errors are found.
Some smart transmitters have internal sensor diagnostics that can even tell users if calibration is drifting, which makes it even easier to separate configuration from accuracy control.
When to Choose Calibration vs. Re-ranging
Scenario | Recommended Action |
Installing a new instrument | Perform calibration to verify compliance |
Process operating range has changed | Perform re-ranging for optimal measurement resolution |
Conducting scheduled QA/QC checks | Perform full calibration |
Output signal deviates from expected value | Perform calibration to identify and correct error |
Reassigning the instrument to a new application/service | Re-range, followed by calibration if required |
Importance of Understanding the Difference
If you confuse re-ranging with calibration, you might think your instrument is working better than it really is. If a transmitter has drifted or is broken, re-ranging it won’t fix problems like zero shift, span shift, or nonlinearity. In the same way, doing a full calibration when all you need to do is re-range takes up extra time and resources.
Calibration must be adequately recorded in regulated industries like pharmaceuticals, oil and gas, or food processing in order to meet standards like ISO 9001, FDA 21 CFR Part 11, or IEC 61511. It’s very important for technicians and engineers to know the difference between these jobs and use them correctly so that they don’t break the rules, put people in danger, or have data quality problems in important applications.
Calibration and re-ranging are both important steps in keeping high-quality instruments, but they are not the same thing. Calibration makes assurance that the instrument’s output shows true values with traceable precision. Re-ranging, on the other hand, changes the meaning of the instrument’s signal in the context of a new process.
In today’s digital systems, these two roles are separate, which makes it possible to make changes faster, be more flexible, and manage the lifespan better as long as technicians use the right technique for the right situation. In any industrial context, having a comprehensive knowledge of both principles makes sure that the data is reliable, the processes are as efficient as possible, and the rules are followed.
Free Instrument Calibration Report Templates (Editable): Downloadable Instrumentation Calibration Report Preparation Templates
What is the difference between calibration and recalibration?
The first step in which an instrument is adjusted to guarantee its output accurately reflects a known reference standard is calibration. It brings the performance of the instrument into line with stated tolerance and accuracy requirements.
On the other hand, recalibration is the periodic or corrective repeating of this process. Instruments could drift over time via mechanical wear, aging components, or environmental influences. By means of verification and readjusting to either the original or revised standard, recalibration helps the instrument to be accurate. This is true for many measuring instruments, from barometers and industrial flow meters to lab balances and pressure transmitters.
Top 15 Calibration Mistakes Engineers Still Make: Top 15 Common Calibration Mistakes in Industrial Instruments
What is the difference between calibration range and instrument range?
- The particular span of values over which an instrument has been examined and confirmed for accuracy is known as its calibration range. A pressure transmitter might be tuned, for instance, from 0 to 100 PSI.
- Sometimes known as the turndown capability or functional range, the instrument range specifies the larger operational limits the device is intended to manage. Although a device can operate from 0 to 300 PSI, its certified accuracy is only guaranteed within the calibration range if it is calibrated just from 0 to 100 PSI.
In summary:
Calibration range = verified working span
Instrument range = total operable span
What is the difference between calibration and validation?
Calibration is the process of confirming that, by means of a recognized reference standard, the output of one instrument faithfully matches a known input. It is device level focusing on measuring precision.
Validation is a more general process whereby a system or process regularly generates outputs satisfying preset criteria. While validation guarantees that the complete system e.g., a production batch or analytical technique performs correctly and consistently, calibration guarantees a sensor is accurate.
- Calibration = Device-level accuracy check
- Validation = System-level performance assurance
In controlled sectors including food processing, biotechnology, and pharmaceuticals, both are very vital.
Validation vs Calibration Explained Clearly: Differences Between Validation and Calibration
What is the difference between calibration and repair?
Calibration is a preventive quality assurance process used to confirm and preserve the accuracy and dependability of an instrument even if it is running as expected.
Repair is a corrective activity used when an instrument breaks, fails, or produces false data.
In short:
Calibration basically maintains the accuracy of a healthy instrument.
Repair gives a broken or malfunctioning instrument functionality once more.
Sometimes calibration comes after repair to guarantee the fixed gadget is once more operating within specification.
What is the difference between zeroing and spanning?
- Zeroing: Usually corresponding with the 4 mA signal in analog transmitters, zeroing sets the bottom limit of measurement for the instrument.
- Spanning: Spanning defines the whole measurement span (e.g., 0–100 °C or 0–50 PSI) by varying the difference between the bottom and upper range values.
For example, if a pressure transmitter is ranged from 0 PSI (zero) to 150 PSI (span), then:
- Zero = 0 PSI
- Span = 150 PSI – 0 PSI = 150 PSI
The calibration process consists in appropriate zero and span adjustments to guarantee linear and accurate response over the designated range.
What is called calibration?
Calibration is the act of calibrating and confirming an instrument such that, within a reasonable tolerance, it generates accurate output matching known input values. It entails determining deviations by matching the readings of the gadget to a known reference standard and, should corrections be needed, making them.
Minimizing or eliminating measurement errors brought on by environmental circumstances, sensor drift, or manufacturing tolerances can help to guarantee traceability and industry standards compliance.
How to calculate calibration range?
Find the calibration range of an instrument by first noting the:
- Lower Range Value (LRV): In analog systems, Lower Range Value (LRV) is the lowest input value for which an expected output is 4 mA.
- Upper Range Value (URV): The highest input value matching 20 mA is known as the upper range value (URV).
Formula:
Calibration Range = URV – LRV
Example:
Should a temperature transmitter span 50 °C (LRV) to 250 °C (URV), the calibration range is:
250 – 50 = 200 °C
This span specifies the area the instrument has been tested to produce precise and linear readings within.
Instrument Calibration Procedures You Can Trust: 40+Instrument Calibration Procedures