How Conditioning Orifice Plates Improve Flow Measurement in Tight Spaces ?

0
344
How Conditioning Orifice Plates Improve Flow Measurement in Tight Spaces ?

Orifice plates are among the most widely used flow monitoring tools in a variety of industrial applications over the years. Their simplicity, affordability, and compatibility with differential pressure-based flow measurement systems have made them a consistent option in the natural gas industry as well as in liquid and steam flow monitoring.

Among these, the conventional orifice plate usually with a single concentric bore at the center has long been the industry standard. Improved substitutes have been created, thus, in spite of installation limitations, flow disruptions, and the need for lengthy, straight pipe lines. The Conditioning Orifice Plate (COP) is one example of this innovation.

The operation of standard orifice plates is based on Bernoulli’s theory and the differential pressure that is generated across the pipeline restriction. Standards such AGA Report Number 3, ASME MFC 3M, and ISO 5167 control these plates. The quality of the upstream flow profile, therefore, greatly affects the accuracy of conventional orifice plates. Upstream piping components such as elbows, reducers, valves, or tees create flow disturbances that distort the velocity profile and hence compromise measurement accuracy.

Standard orifice plates usually need the following to lessen this:

  • Straight pipe runs: There are typically 5 downstream and 10 to 50 upstream pipe diameters.
  • Flow conditioners are devices that equalize flow, such as perforated plates or tube bundles.

Compact or retrofit installations may find these criteria unfeasible, particularly in skid-mounted systems, offshore platforms, and small industrial facilities.

Refer to This: Orifice Plate Commissioning Checklist

A modernized differential pressure flow element, the Conditioning Orifice Plate, overcomes the drawbacks of the conventional orifice plate. Though it adds important design changes for improved performance in actual applications, it uses the same fundamental concepts of flow monitoring as conventional plates.

Unlike normal plates with one bore, the COP has four equally spaced holes distributed in a circular pattern. By spreading the flow evenly before the differential pressure measurement is recorded, this multi-bore design enables built-in flow conditioning. This means that the COP eliminates the need for external flow conditioners or long straight pipes.

The principle of operation of the Conditioning Orifice Plate is still based on the Bernoulli energy equation. The overall area of the four bores is supposed to correspond to the area of the single bore used in a standard orifice plate for the same pipe size.  A constant pressure drop-to-flow relationship is ensured by maintaining the beta ratio (β = d/D), which is the ratio of bore diameter to pipe diameter.

As the fluid travels through the four holes, the design allows it to “self-condition,” hence generating a more symmetric and stable velocity profile downstream. Even with little straight pipe runs, this significantly improves consistency and accuracy of measurements.

Click to Discover: Why Drain and Vent Holes are Essential for Efficient Orifice Plate Operation?

Though Conditioning Orifice Plates are made to be generally consistent with industry standards like ISO 5167, ASME MFC 3M, and AGA 3, there are intentional variations in four main areas to enhance performance:

  1. Plate Thickness
  2. Orifice Configuration / Beta Ratio
  3. Straight Pipe Requirements
  4. Accuracy and Installation Tolerances

Instead of being infractions, these deviations are improvements that offer useful advantages under field conditions.

Click to Learn: Why RTD Temperature Sensors are Installed Downstream of Orifice Plates?

  1. Better Performance in Limited Areas: The requirement for just two diameters of straight pipe both upstream and downstream lets COPs be installed when space is extremely constrained.
  2. Built-in Flow Conditioning: The four-hole design saves space and money by eliminating the need for extra flow straighteners.
  3. Improved Accuracy in Wet Gas Conditions:  By use of condensate drainage via the bores, COPs stop the accumulation or “damming” usually seen with single-bore conventional orifice plates.
  4. Lowering Installation Cost: Shorter straight pipe lines result in smaller meter runs, a reduced environmental impact, and cheaper labor and material costs.
  5. Consistency in Measurement:  Even when put near flow disturbances, the discharge coefficient for COPs closely matches the typical orifice plate curve..
  6. Simplified Specification and Inventory:  Fixed beta ratios of 0.4 and 0.65 make selection and stocking easier, regardless of pipe scheduling.

Usually, COPs employ thicker plates compared to normal orifice plates. This increases structural durability, reduces plate deflection at high flow rates, and boosts long-term measurement dependability. For example, COPs like as the Rosemount 1595 and 405C offer more resistance to pressure-induced deformation than the AGA 3 thickness standard for 6-inch lines.

  • Standard Orifice Plate: One center bore; beta ratios usually vary from 0.1 to 0.75.
  • Conditioning Orifice Plate: Four bores symmetrically arranged. Two fixed beta ratios are used: 0.4 for low to medium flow and 0.65 for high flow. Pipe schedules show constant maintenance of these values.

Read: Orifice Beta Ratio: Why It Falls Between 0.3 and 0.7 for Optimal Flow Measurement

One of the most transformative aspects of COP technology is its minimal piping requirement:

  • Only 2D upstream and 2D downstream: One of the most revolutionary features of COP technology is its low piping requirements: only 2D upstream and 2D downstream, which drastically reduces the 10D to 50D upstream and 5D downstream that ordinary orifice plates typically require.

For instance, the conventional orifice plate per ISO 5167 would require 16D upstream for a 6-inch line with a single upstream 90° elbow. A COP would only need 2D, signifying an 88% decrease of pipe.

Click to Use: Orifice Plate Flow Rate Calculator

The COP keeps great precision still despite loosened installation criteria. Lab experiments show discharge coefficient (UCd) uncertainty as follows:

Beta RatioReynolds Number < 10,000Reynolds Number > 10,000
0.4±0.5%±0.5%
0.65±1.5%±1.0%

These numbers are better than the uncertainties specified in ISO 5167 and ASME MFC specifications for standard orifice plates.

The graph titled “Discharge coefficient uncertainties for 0.4 beta” compares the uncertainty levels of different flow measurement standards across varying Reynolds numbers. It highlights that the 1595 and 405C Conditioning Orifice Plates maintain a low and consistent uncertainty of around ±0.5%, outperforming ASME MFC 3M, AGA Report Number 3, and ISO 5167 standards, especially at lower Reynolds numbers. Notably, ASME MFC 3M shows high uncertainty (~1.0%) at low Reynolds numbers, which drops significantly after 2000. This graph demonstrates the superior performance and stability of conditioning orifice plates across a broad range of flow conditions.

The graph titled “Discharge coefficient uncertainties for 0.65 beta” illustrates how uncertainty varies with Reynolds number for different standards. It shows that the 1595 and 405C Conditioning Orifice Plates initially have a higher uncertainty (~1.25%) at low Reynolds numbers, but stabilize at around ±0.75% once the Reynolds number exceeds 2000. In comparison, ASME MFC 3M, AGA Report Number 3, and ISO 5167 standards also show higher uncertainties at low Reynolds numbers, which drop significantly after 2000. Despite a slightly higher steady-state uncertainty, the conditioning plates still offer acceptable and consistent performance across a wide Reynolds number range.

FeatureConditioning Orifice Plate (COP)Standard Orifice Plate
Number of BoresFour equally spaced circular holesOne central bore
Beta Ratio OptionsFixed at 0.4 and 0.65 across all pipe schedulesVariable: 0.1 to 0.75 based on pipe size and schedule
Flow ConditioningBuilt-in via multi-hole designRequires separate flow straighteners or long straight runs
Straight Pipe Requirement2D upstream + 2D downstreamTypically 10D to 50D upstream + 5D downstream
Plate ThicknessGenerally thicker than standard (especially for high-pressure lines)Defined by standards (thinner plates may deflect at high flow)
Accuracy in Real InstallationsHigh accuracy maintained even with nearby disturbancesHighly sensitive to upstream disturbances
Installation ToleranceCentering ring ensures proper alignment within the meter runMisalignment risks measurement errors
Condensate HandlingAllows condensate to pass through, avoiding dammingProne to damming in wet gas or multiphase conditions
Compliance with StandardsGenerally complies with ISO 5167, ASME MFC 3M, AGA 3 with minor enhancementsFully adheres to all dimensional standards
Inventory ManagementSimplified due to fixed beta and bore sizesRequires multiple beta and schedule-specific designs
Application SuitabilityIdeal for tight spaces, skid-mounted equipment, offshore platforms, retrofitsBest used in large plants with ample space and long piping
Cost of InstallationLower due to reduced piping and no need for flow conditionersHigher due to extra piping and accessories

Download and Refer: Orifice Plate Flow and Pressure Drop Calculation Excel Tool

The Conditioning Orifice Plate is a major change in technology for measuring differential pressure flow. It provides a contemporary answer to many of the constraints experienced by conventional orifice plates by including flow conditioning into the plate design and reducing the need for long, straight pipe lengths.

COPs not only provide accuracy and dependability but also design flexibility and cost reductions with proven performance in both laboratory and field settings. Conditioning Orifice Plates are especially better than conventional orifice plates in applications where space, installation limits, or multiphase flow conditions occur.