HomeInstrumentation CalculatorsPV to 4-20mA scaling calculator

PV to 4-20mA scaling calculator

Published on

spot_img

4-20 mA signals are used to transmit physical process values, such as temperature, pressure, liquid level, or other physical quantities. The current in the loop represents the equivalent physical process value.

Example:

A temperature transmitter with a temperature range of 0 to 1000 degrees Celsius produces 7.2 mA in an analogue loop, which is equal to the degree temperature being measured at 200 degrees.

The following “PV into 4-20mA scaling calculator” transforms the measured value to the current:

The following calculations provide the basis for the PV into 4-20mA scaling calculator:

Formula for changing a physical value (Pv) to a current (I):

Formula for changing a physical value (Pv) to a current (I):

 I=[(I high – I low)/(Pv high – Pv low)]*(Pv-Pv low)+I low

In this article, scaling is used to establish the relationship between a field value (in this case, mA) and a process value (e.g. Temperature, Pressure, Level).

The electrical current loop signal is converted into a physical value using a linear characteristic. This feature is used to describe the relationship between the current signal and physical value.

It is important to take extra precautions when converting from a physical value with a starting value other than zero. a pressure indication with a range of -1 to 1 bar, for example. 12 mA of current are flowing at a pressure of 0 bar. In this situation, it is advised that you utilise a scaling calculator because the 4 mA starting current makes the relationship between the physical value and current irrational.

It could be necessary to test instruments using a  simulator when working with real – life conditions. Because the simulator allows manual control of the process value in the loop, scaling can be evaluated and checked relatively easily.

Click here for more Instrumentation Calculators

Latest articles

Control Valve Stroke Length Calculator

Control valves function through modifications to the flow passage diameter which directs signal-controlled flow...

Essential Control Valve Performance Parameters

Table of ContentsDead Band & BacklashActuator-Positioner DesignResponse TimeValve TrimDead TimeGainHysteresisInherent CharacteristicShaft Wind-UpValve Capacity (Cv...

Cause-and-Effect Diagrams in Process Industries: Test Your Knowledge

The Cause-and-Effect Diagram in Instrumentation and Control Engineering quiz welcomes you to its examination....

Easy Pull-Up Resistor Calculator for PLC Inputs in Discrete Sensor Applications

Table of ContentsWhat is a PLC?What is a Pull-Up Resistor in PLC Applications?PLC Input...

More like this

Control Valve Stroke Length Calculator

Control valves function through modifications to the flow passage diameter which directs signal-controlled flow...

Essential Control Valve Performance Parameters

Table of ContentsDead Band & BacklashActuator-Positioner DesignResponse TimeValve TrimDead TimeGainHysteresisInherent CharacteristicShaft Wind-UpValve Capacity (Cv...

Cause-and-Effect Diagrams in Process Industries: Test Your Knowledge

The Cause-and-Effect Diagram in Instrumentation and Control Engineering quiz welcomes you to its examination....