Control Valve

Modes of Split-Range Control in Control Valve Applications

For most control applications in process industries, it is required to have more than one control valve to respond to the single controller output.  The control valves must be configured to follow the control instructions issued by a particular controller.

Control valves are said to be split ranged or sequenced and configured to follow the command of a single controller.

The various modes of sequencing are employed in Split-ranged control valves.

What are the common modes of control valve sequencing?

In the process industry, this involves some modes of control valve sequencing are

1. Complementary Split-Range control:

Complementary Split-Range control
COMPLEMENTARY SPLIT-RANGE CONTROL

In complementary split-ranging control mode for a particular controller output range both the control valve cannot be in a single state at a time. These control valves must be in complement with each other which means if one control valve is in an open state and the other must be in a close state and vice versa.

This split range control can be observed in a standby situation, where the primary valve halts operation due to some problems the same operation is carried by the other valve called the secondary valve.

A complementary split-range control is observed in the case of an agitator tank where the mixing of two different fluids is carried out.

Let us consider an example of mixing base and pigment liquids together to form coloured paint.

The single controller output signal is sent to both the base valve and pigment valve. While the pigment valve is of Air-To-Open type.  And the base valve is of Air-To-Close type.

The below table represents the relationship between base and pigment valve opening for a particular task issued by the single controller output.

Controller O/P (%)I/P Converter Output
(PSI)
Pigment Valve (Stem position)Base Valve
(Stem position)
03Fully ClosedFully Open
25625% Open75% Open
509Half-OpenHalf-Open
751275% Open25% Open
10015Fully OpenFully Closed

2. Exclusive Split-Range Control:

Exclusive Split-Range Control
EXCLUSIVE SPLIT RANGE CONTROL

The behavior of valve sequencing in exclusive split-range control is to have an “EITHER OR” throttled path for process fluid. Here the process fluid will flow through only one valve at a particular instant of time but not through both valves simultaneously.

In this type of split-range control when the output signal of the controller is 50%, both the acid valve and caustic valve remain fully closed.

When the output signal of the controller is 100% only one valve will open and another valve will close fully. And vice versa.

Let us consider an example of a neutralization process in which the reagent is fed to bring the pH of the process liquid close to neutral by the addition of either acid or caustic.

The working of Exclusive split range control is as follows.

  1. A pH analyzer monitors the pH value of the mixture, and a single pH controller commands two reagent valves to get open when needed.
  2. If the pH value of the mixture rises above the desired set point, then the controller output signal will increase and the controller directs the acid valve to get open to maintain the desired pH value. The addition of acid to the mixture will have the effect of lowering the pH value of the mixture.
  3. If the pH value of the mixture drops below the desired set point, then the controller output signal will decrease and the controller directs the caustic valve to get open to maintain the desired pH value. The addition of base (caustic) to the mixture will have the effect of raising the pH value of the mixture.
  4. The pH value of the mixture in the tank is maintained by closing and opening either of the valves as directed by the controller.

The operating range of the acid valve and the caustic valve is as follows.

  1. The acid valve called the Air-To-Open valve has an operating range of 9 to 15 PSI,
  2. The caustic valve called the Air-To-Close valve has an operating range of 3 to 9 PSI.

The relationship between valve openings for each control valve and the controller’s output is shown in the below table.

Controller O/P (%)I/P Output (PSI)Acid Valve (Stem position)Caustic Valve (Stem position)
03Fully ClosedFully Open
256Fully ClosedFully Open
509Fully ClosedFully Closed
7512Fully OpenFully Closed
10015Fully OpenFully Closed

3. Progressive Split-Range Control:

Progressive Split-Range Control
PROGRESSIVE SPLIT-RANGE CONTROL

To expand the operating range of flow control of some kind of fluid above the range that a single control valve will deliver.

This type of control technique uses two valves one is the small acid valve and another one is a large acid valve.

For the controller output of 50%, the small acid valve opens gradually and becomes fully opened, during this time the large acid valve will remain closed until the controller output rises above 50%.

As the controller output rises above 50% the large acid valve will start opening and when the controller output reaches 100% both the small acid valve and large acid valve are opened fully.

Let us consider an example of controlling the pH of the incoming fluid.

When the pH of the incoming fluid is high this must be neutralized with the proper mixing of acid to control the pH to the desired set point. The pH analyzer AT is used to measure the pH of the inlet water.

When the controller output increases the small acid valve will start to open gradually and becomes fully open at 50% of the controller output. During this time the large acid valve will remain closed until the controller output rises above 50%.

When the controller output reaches 100% the large acid valve opens and small acid valve is fully closed to ensure that the pH of the incoming water is neutralized.

The below table represents the controller output and valve status for the proper sequencing of small and large acid control valves

Controller O/P (%)I/P Output (PSI)Small Acid Valve (Stem position)Large Acid Valve (Stem position)
03Fully ClosedFully Open
256Fully ClosedFully Open
509Fully ClosedFully Closed
7512Fully OpenFully Closed
10015Fully OpenFully Closed

What is pH?

 The pH of an aqueous solution is defined as the negative logarithm of its hydrogen ion concentration.

pH = – log {H+}

What are acid, neutral, and base?

  • Acid: The solution where the pH value lies between pH 0.0 to pH 6.7
  • Neutral: The solution where the pH value lies between pH 6.8 to pH 7.4
  • Base: The solution where the pH value lies between pH 7.5 to pH 14.0
0ACIDIC
(Acidity)
1
2
3
4
5
6
7NEUTRAL
8BASE
(Alkalinity)
9
10
11
12
13
14
ACID, NEUTRAL AND BASE TABULATION

Rabert T

As an electrical engineer with 5 years of experience, I focus on transformer and circuit breaker reliability in 110/33-11kV and 33/11kV substations. I am a professional electrical engineer with experience in transformer service and maintenance. I understand electrical principles and have expertise troubleshooting, repairing, and maintaining transformers, circuit breakers, and testing them. Tweet me @Rabert_infohe