- Abbreviations
- Formulas for Converting Specific Gravity for All Liquids
- Interface level measurement Calculations with varying Tank Level and two Bubble Tubes
- Example calculation – Interface level Calculations With Varying Tank Level and two Bubble Tubes
- Span value calculation
- LRV calculation (4mA)
- URV calculation (20mA)
In this section, examples of typical calculations for determining the liquid interface level in an open tank with with varying tank level and two bubble tubes transmitter installation are given.
It is important to keep in mind that the upper-range values (URV) and lower-range values (LRV) relate to the highest and minimum measurements that are intended, respectively. The Calibrated Span is equal to the URV minus the LRV. The output at LRV greater than 0% represents the value of the suppression.
Abbreviations
The following acronyms are utilized in this directive.
LRV = Lower-range value (a measurement that’s output is 4 mA).
URV = Upper-range value (a measurement with a 20 mA output).
SG = A liquid’s specific gravity (relative density). Water has a specific gravity of 1.00 in both traditional and SI systems.
HW= Equivalent Headlevel pressure of Water
Specific gravity = Density [lb/ft3 ] / 62.4
Specific gravity = Density [kg/m3] / 1.00
SG1 = Specific gravity of upper liquid (lighter liquid)
SG2 = Specific gravity of lower Liquid (Heavier liquid)
H = Interface level need to be measured.(Head between LRV and URV)
Calibrated Range of the transmitter = LRV to URV
Where:
HW = Equivalent Head level pressure of Water
Span value of the transmitter = (H)*(SG2 – SG1)
Equivalent Head level pressure of Water (HW) at Lower range value
HW at LRV = (H*SG1) = Suppression
Equivalent Head level pressure of Water (HW) at Upper range value
HW at URV = (H*SG2)
The DP transmitter is mounted in an open tank with two bubble tubes and also has the following specifications to determine interface level.
Process liquid Specific gravity varies between 1.0 and 1.7
Height of the interface level measured between LRV and URV is
H= 50 inches
Find the calibration range of the transmitter for measuring the interface level?
So, SG1 = 1.0
SG2= 1.7
Span = (H)*(SG2 – SG1)
Span = (50)*(1.7 – 1.0)
Span = (50)*(0.7)
Span value of the transmitter = 35 inches of H2O
HW at LRV = (H*SG1)
HW at LRV = (50 *1.0)
HW at LRV= 50 inches of H2O = Suppression
HW at URV = (H*SG2)
Hw at URV = 50 * (1.7)
HW at URV = 85 inches of H2O
Calibration Range of the transmitter = 50 to 85 inches of H2O