Basic troubleshooting of Electrical components in MCC/Electrical Control Panel/Switch Gear

1. SDF (Switch Disconnector Fuse)

Switch Disconnector Fuse
Possible Fault:- Fuse Burning. 
Identification:- Check the fuses continuity with a Multi Meter. 
Cause:- Over Current, Short Circuit
Remedy:-Replace the Fuse with same rated(Current and Voltage) new one 

2.MCCB/MCB (Miniature Circuit Breaker )
MCB / MCCB
Possible Fault:- Tripping
Cause: Short Circuited current.
Remedy:- Rectify the cause produced the tripping current and once rectified the same. Put ON the MCCB/MCB

Rating :- Voltage, Current, Withstanding Fault Current


3.CONTACTOR

CONTACTOR
Possible Fault:- Motor not starting.
Cause:- Contactor Coil faulty, Coil is not getting Power 
Remedy:- Check the Power Supply voltage from Coil point. If coil is faulty replace with new one.     
Rating:- Voltage , Current, Maximum fault withstand Current.

4.OLR (Overload Relay)
Overload Relay

Possible Faults:- Motor not starting/Motor tripping continuously
Cause:- Relay Tripped, Current adjustment is faulty.
Remedy:- Release the tripped OLR switch, Adjust the current rating according to the Name Plate.
Ratings:- Current and Voltage.
5.RELAY
RELAY

Possible Fault:-  Not Working.
Cause: Coil faulty, No power, Contact got damaged
Remedy:- Check the power Supply voltage, Continuity between contacts, wiring faulty.
Ratings:- Coil Voltage, Current Ratings, Type of Contact.

Related Articles

Leave a Reply

Back to top button

Adblock Detected

We Noticed You're Using an Ad Blocker Hi there! We understand that ads can be annoying, but they help support our website and allow us to continue providing you with high-quality content. Please consider whitelisting our site or disabling your ad blocker while you visit. Your support means a lot to us! Thank you for understanding!