How to calibrate flow transmitter for pitot tube

How to calibrate flow transmitter for pitot tube

Material

Data sheet
Pressure calibrator (std)
Multimeter (std)
Hart communicator

Step

*Ask panel man to put the controller in manual mode for control loop and to put it on MOS for ESD loop.
*Hook up HART Communicator and verify some parameters by refer to data sheet. Typical parameters are, tag number, PV, LRV and URV.
*Isolate the instrument from the process.
*Remove connection at manifold to the process after release the process pressure
*Connect pressure calibrator to high side of manifold
*Expose the low side to atmosphere
*Hook up a multimeter in series with the signal to the DCS to measure current signal.
*Apply pressure as per data sheet LRV
Multimeter should show 4mA
If not, do zero adjustment at transmitter using HART Communicator
*Apply pressure as per data sheet URV
Multimeter should show 20mA
If not, do span adjustment at transmitter using HART Communicator
*Verify the linearity by increasing and decreasing the pressure (0%,25%,50%,75%,100%,75%,50%,25% and 0%of range)
*After completion of the job ask panel operator to put loops back in normal mode or normalize the MOS
*Fill the calibration form and file it for future reference.

Example calculation

Instrument calibrated range: 0 – 5000 mmH2O
Process calibrated range: 0 – 22900 kg/h
Q =K  P
0%  0 mmH2O = ( 0/5000) x 22900
= 0 kg/h
50%  2500 mmH2O = ( 2500/5000) x 22900
= 16192.7 kg/h
100%  5000 mmH2O = ( 5000/5000) x 22900
= 22900 kg/h

Related post:

Related Articles

Leave a Reply

Back to top button

Adblock Detected

We Noticed You're Using an Ad Blocker Hi there! We understand that ads can be annoying, but they help support our website and allow us to continue providing you with high-quality content. Please consider whitelisting our site or disabling your ad blocker while you visit. Your support means a lot to us! Thank you for understanding!